Or mech-tee the riser and add a hose valve.


Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Worley, Tom <[email protected]>
Sent: Thursday, March 28, 2024 8:46 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: BFP Forward flow test design

Just make the main drain 2½.  A 2” may even suffice depending on how the water 
supply is.

Thomas R. Worley
  Estimator/Design Manager
  Fire Foe Corp.
  999 Trumbull Ave.
  Girard, OH 44420
  P: 330-759-9834 x112
  F: 330-759-8949
  E: [email protected]<mailto:[email protected]>
[cid:[email protected]]<https://urldefense.com/v3/__http:/www.firefoe.com/__;!!O7jEn5k3aH8!cuaHibCXwaAnFLnXeA8jgIgRYiCstZyaNyhuRwNqS9wUz4M2_B9zJ2Ydo3BqWcyCz06VI8GRM1Ln$>

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Thursday, March 28, 2024 9:38 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] BFP Forward flow test design

I am working on a re-design of a system where I need to include a provision for 
doing a forward flow test for the backflow preventer (4”). Due to space issues, 
I would like to do a by-pass around the check valve to the FDC. Is there a 
problem with this due to the clappers in the FDC?

Also, the building is Residential or Light Hazard and the maximum demand flow 
is around 250 gpm. If I have to add another outlet for the test, would a single 
2-1/2” FDC be acceptable? Unfortunately, I am not aware of any way to predict 
what would be required. Is there any rule of thumb for the design of these 
things?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)