Just make the main drain 2½.  A 2” may even suffice depending on how the water 
supply is.

Thomas R. Worley
  Estimator/Design Manager
  Fire Foe Corp.
  999 Trumbull Ave.
  Girard, OH 44420
  P: 330-759-9834 x112
  F: 330-759-8949
  E: [email protected]<mailto:[email protected]>
[cid:[email protected]]<http://www.firefoe.com/>

From: Fpdcdesign <[email protected]>
Sent: Thursday, March 28, 2024 9:38 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] BFP Forward flow test design

I am working on a re-design of a system where I need to include a provision for 
doing a forward flow test for the backflow preventer (4”). Due to space issues, 
I would like to do a by-pass around the check valve to the FDC. Is there a 
problem with this due to the clappers in the FDC?

Also, the building is Residential or Light Hazard and the maximum demand flow 
is around 250 gpm. If I have to add another outlet for the test, would a single 
2-1/2” FDC be acceptable? Unfortunately, I am not aware of any way to predict 
what would be required. Is there any rule of thumb for the design of these 
things?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to