What is the height of the top floor?  What is the occupancy classification?  Go 
through 905 in the fire code and see what it says about standpipes.  From 
similar projects I have done over the years, I have not seen them required.  
But, your local fire code will dictate.


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: James Litvak <[email protected]>
Sent: Tuesday, January 23, 2024 6:55 AM
To: AFSA Sprinkler Forum <[email protected]>
Subject: [Sprinklerforum] Hose Valves in Townhome Apartments

I am designing an NFPA 13 mid-rise apartment building that includes three 
townhome-style two-floor apartments. The EOR put a note on the FP plans to 
locate a hose valve on each floor of those units "AS REQUIRED." I didn't put 
them on my plans because I have never seen them required in similar units in 
other buildings. The EOR's review comments came back saying "Fire Protection 
permit review indicated hose valves required in 2-story units." I have 
requested the fire protection permit review comments and was told by the GC it 
is unlikely we'll receive them, and that I should just include those valves. My 
plans were approved by the AHJ without those valves. It is the EOR now refusing 
to accept my plans without the valves.

Are those valves required?