Yes. The EOR said so after the fact.. Price the change, add the valves.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: James Litvak <[email protected]>
Sent: Tuesday, January 23, 2024 7:55 AM
To: AFSA Sprinkler Forum <[email protected]>
Subject: [Sprinklerforum] Hose Valves in Townhome Apartments

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
I am designing an NFPA 13 mid-rise apartment building that includes three 
townhome-style two-floor apartments. The EOR put a note on the FP plans to 
locate a hose valve on each floor of those units "AS REQUIRED." I didn't put 
them on my plans because I have never seen them required in similar units in 
other buildings. The EOR's review comments came back saying "Fire Protection 
permit review indicated hose valves required in 2-story units." I have 
requested the fire protection permit review comments and was told by the GC it 
is unlikely we'll receive them, and that I should just include those valves. My 
plans were approved by the AHJ without those valves. It is the EOR now refusing 
to accept my plans without the valves.

Are those valves required?