What size are the equipment platforms? You might also need to look at 4.5.2.2 
and 4.5.2.3.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Dec 19, 2023 at 3:05 PM,  <Craig Prahl (mailto:[email protected])>  
> wrote:
>   
>   
>         
>   
>
> I need a sanity check.   
>
>   
>
>   
>
>   
>
> I have a micro-electronics clean room area.    H-5 occupancy. The 
> interstitial space above is above 15 ft high and has catwalks which are above 
> the cleanroom ceiling.    Architects have deemed the interstitial space as 
> “Equipment Platforms”, unoccupied space.
>
>   
>
>   
>
>   
>
> Referencing IBC/IFC 2021, NFPA 13, 2019
>
>   
>
>   
>
>   
>
> Both the clean room and the interstitial space require full sprinkler 
> protection per the building code, typically OH-2.   
>
>   
>
>   
>
>   
>
> Based on NFPA 13, the maximum area for the OH system is 52,000 sq. ft.
>
>   
>
>   
>
>   
>
> Per 2019 NFPA 13, 4.5.2 if the area is considered a mezzanine there is no 
> requirement to include the sq. footage of the interstitial space as part of 
> the system area.    However, the interstitial space has a substantial ceiling 
> assembly between it and the occupied clean room below so it’s closer in 
> definition to an attic space or non-combustible concealed space with no 
> provision for storage.    Access is restricted and limited.
>
>   
>
>   
>
>   
>
> Overall the clean room is around 700,000 sq. ft. total so I’ve got a LOT of 
> systems and am trying to determine size and quantity of riser rooms.   
>
>   
>
>   
>
>   
>
> So, does it make sense to not include the area of the interstitial space in 
> determining the number of risers.    Basically one OH system can cover 52,000 
> sf of clean room and 52,000 sq. ft. of interstitial space?   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>
>  Craig Prahl   |Jacobs     | Fire Protection SME – Special Hazards |    
> [email protected] (mailto:[email protected])|www.jacobs.com 
> (https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$)
>
>   
>
> 1041 East Butler Road      Greenville, South Carolina    29606
>
>   
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>   
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to