I need a sanity check. I have a micro-electronics clean room area. H-5 occupancy. The interstitial space above is above 15 ft high and has catwalks which are above the cleanroom ceiling. Architects have deemed the interstitial space as “Equipment Platforms”, unoccupied space.
Referencing IBC/IFC 2021, NFPA 13, 2019 Both the clean room and the interstitial space require full sprinkler protection per the building code, typically OH-2. Based on NFPA 13, the maximum area for the OH system is 52,000 sq. ft. Per 2019 NFPA 13, 4.5.2 if the area is considered a mezzanine there is no requirement to include the sq. footage of the interstitial space as part of the system area. However, the interstitial space has a substantial ceiling assembly between it and the occupied clean room below so it’s closer in definition to an attic space or non-combustible concealed space with no provision for storage. Access is restricted and limited. Overall the clean room is around 700,000 sq. ft. total so I’ve got a LOT of systems and am trying to determine size and quantity of riser rooms. So, does it make sense to not include the area of the interstitial space in determining the number of risers. Basically one OH system can cover 52,000 sf of clean room and 52,000 sq. ft. of interstitial space? Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | [email protected]<mailto:[email protected]> | www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$> 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]