FYI, if it is a retrofit, you are not specifically tied to 12.6.2 and 12.6.3 
with sprinklers of K-11.2 or greater. The following Subsection 12.6.4 is an 
"exception" to those provisions:

12.6.4*   Unless the requirements of 12.6.5 are met, the requirements of 12.6.2 
and 12.6.3 shall not apply to modifications to existing storage application 
systems, using sprinklers with K-factors of K-8.0 (115) or less.

A.12.6.4   Modification of an existing system includes extending sprinkler 
protection into adjacent areas.

With this, EOR call ups not-with-standing, NFPA 13-2013 allows you to utilize 
any K sprinkler that works for you hydraulically.

The foregoing is my opinion only and does not represent NFPA or the NFPA 13 
Technical Committees.

Best regards,

Larry Keeping

From: Brian Harris <[email protected]>
Sent: Monday, September 11, 2023 1:46 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Warning! This email came from outside your company.
Travis-
Thanks. I should have mentioned I need it to be an upright. It's a retro-fit 
job.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 1:40 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

https://www.reliablesprinkler.com/files/bulletins/146.pdf?x76626


Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]<mailto:[email protected]>

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 10:34 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Eric-
Thank you. I have an EOR that called for a K14.0 CMDA on a specific job. Since 
I can't find one, I was wondering if I could use a K11.2 instead.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

To expand on this slightly, it's not that "general storage applications" 
directly means class I-IV commodities, but that chapter 12 applies to all the 
following storage criteria chapters. So, "general storage applications" is how 
they show that 12.6.3 applies to chapters 14 and 15 for solid-piled 
commodities, and then "rack storage" is there to reference chapters 16 and 17. 
The rest of the sentence containing "rubber tire storage, roll paper storage, 
and baled cotton storage" is how they reference chapters 18, 19, and 20 
respectively to round out the rest of chapters.

[A close up of text]

Hope this helps!

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Eric-
Thank you. I didn't want to assume class I-IV fit into "general". Much 
appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,0GPrjmr1UnUZUD1dC2S_0zPb18z5RsmivEapMbxWxXZh0Z8xeW_wo38ttJ26ezgjT88xjZeUN-zIwYtZW3LVrX02vu1_1ePrf-JdHuJVtMUmNiCMD84,&typo=1>


From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:27 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

Yes, it does per the "general storage applications" segment of the code section.

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:19 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] CLASS I-IV / CMDA

Would 12.6.3 (NFPA-13 2013) apply for class I-IV? My remote area is .36/2000.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,Fz_3mU2H_Ojb1YY6oijGOLnnNaRa7hDR_0xsbgsJ7z6pCBxHT1MEGLQdRZPurT2UN0kMjjHnC-ulMsxAg9BZ1lIW3A4QFGpu82oXRLmyd4G-kzjUnLn2Yg,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to