Eric-
Thank you. I have an EOR that called for a K14.0 CMDA on a specific job. Since 
I can't find one, I was wondering if I could use a K11.2 instead.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Eric Rieve <[email protected]>
Sent: Monday, September 11, 2023 11:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

To expand on this slightly, it's not that "general storage applications" 
directly means class I-IV commodities, but that chapter 12 applies to all the 
following storage criteria chapters. So, "general storage applications" is how 
they show that 12.6.3 applies to chapters 14 and 15 for solid-piled 
commodities, and then "rack storage" is there to reference chapters 16 and 17. 
The rest of the sentence containing "rubber tire storage, roll paper storage, 
and baled cotton storage" is how they reference chapters 18, 19, and 20 
respectively to round out the rest of chapters.

[A close up of text]

Hope this helps!

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Eric-
Thank you. I didn't want to assume class I-IV fit into "general". Much 
appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,0GPrjmr1UnUZUD1dC2S_0zPb18z5RsmivEapMbxWxXZh0Z8xeW_wo38ttJ26ezgjT88xjZeUN-zIwYtZW3LVrX02vu1_1ePrf-JdHuJVtMUmNiCMD84,&typo=1>


From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:27 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

Yes, it does per the "general storage applications" segment of the code section.

Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, September 11, 2023 11:19 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] CLASS I-IV / CMDA

Would 12.6.3 (NFPA-13 2013) apply for class I-IV? My remote area is .36/2000.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,Fz_3mU2H_Ojb1YY6oijGOLnnNaRa7hDR_0xsbgsJ7z6pCBxHT1MEGLQdRZPurT2UN0kMjjHnC-ulMsxAg9BZ1lIW3A4QFGpu82oXRLmyd4G-kzjUnLn2Yg,,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to