Brian,

Please remember that when you're looking for the required protection method for storage, before you begin selecting any protection method, you must first identify these five things, at least.

 * Commodity class
 * Storage method (rack, shelf, etc)
 * Packaging (cartoned, exposed)
 * Intended storage height
 * Ceiling height above the storage

Once those are established, then you can develop a protection strategy.  And, where 12.6.3 comes into play is if a required criteria for one commodity/method/packaging/height/ceiling height are adjacent to an area with a different set of criteria, then the separation or extension of the design for the more demanding (Say Class IV, Racks, 20' high, cartoned, 25' ceiling) must extend at least 15' into the lower demanding (e.g Class II, Floor, 20' high, cartoned, 25' ceiling).

Now if the separation does meet the criteria of 12.3 (1)-(2)-(3) then extending the protection is not required.  Remember that such a requirement does not impact the size/selection of the remote area, merely the spacing and density required.  Yes, it may impact the most remote area selection, however it makes no requirement for the size to be adjusted.

sincerely,

*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>


*
On 9/11/2023 10:18 AM, Brian Harris wrote:

Would 12.6.3 (NFPA-13 2013) apply for class I-IV? My remote area is .36/2000.

*Brian Harris, CET*

BVS Systems Inc.

bvssystemsinc.com <http://bvssystemsinc.com/>

Phone: 704.896.9989

Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to