Hey Ken-
Good to hear from you as always.
I was given the design criteria from the EOR. Since he spec’d out a K14.0 CMDA 
head, and I can’t find one, I was curious if Class I-IV fell under the “General 
Storage” so I could use a K11.2 instead.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Ken Wagoner <[email protected]>
Sent: Monday, September 11, 2023 11:45 AM
To: [email protected]
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA

Brian,

Please remember that when you're looking for the required protection method for 
storage, before you begin selecting any protection method, you must first 
identify these five things, at least.

  *   Commodity class
  *   Storage method (rack, shelf, etc)
  *   Packaging (cartoned, exposed)
  *   Intended storage height
  *   Ceiling height above the storage

Once those are established, then you can develop a protection strategy.  And, 
where 12.6.3 comes into play is if a required criteria for one 
commodity/method/packaging/height/ceiling height are adjacent to an area with a 
different set of criteria, then the separation or extension of the design for 
the more demanding (Say Class IV, Racks, 20' high, cartoned, 25' ceiling) must 
extend at least 15' into the lower demanding (e.g Class II, Floor, 20' high, 
cartoned, 25' ceiling).

Now if the separation does meet the criteria of 12.3 (1)-(2)-(3) then extending 
the protection is not required.  Remember that such a requirement does not 
impact the size/selection of the remote area, merely the spacing and density 
required.  Yes, it may impact the most remote area selection, however it makes 
no requirement for the size to be adjusted.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

On 9/11/2023 10:18 AM, Brian Harris wrote:
Would 12.6.3 (NFPA-13 2013) apply for class I-IV? My remote area is .36/2000.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935







_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to