Baffle or elevation change of at least 2’-0

On Tue, Aug 9, 2022 at 11:51 AM <[email protected]> wrote:

> Can I assume that this elevation change would serve the same purpose as a
> draft curtain or would one still be needed?
>
> Bruce
>
>
>
> *From:* Brett Peters <[email protected]>
> *Sent:* Tuesday, August 9, 2022 1:33 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: ESFR Question
>
>
>
> NFPA 13 12.3 - elevation change of at least 2'-0 and above an aisle with a
> minimum of 2'-0 of clearance to each side of the center of the aisle.
>
>
>
> Thanks
>
>
>
> Brett Peters
>
> General Manager Installation & Design
>
> Proudline Fire Protection Services Ltd.
>
> [email protected]
>
> 780 490 7602 office ext 202
>
> 780 490 7605 fax
>
> 780 777 0568 cell
>
> 780 718 2676 24h
>
> Visit us at www.proudline.ca
>
>
>
> Proudline now offers ULc listed monitoring services, please contact
> [email protected] for more information
>
>
>
>
>
>
>
> [image: Image removed by sender.] [image: Image removed by sender.] [image:
> Image removed by sender.] [image: Image removed by sender.] [image: Image
> removed by sender.] [image: Image removed by sender.] [image: Image
> removed by sender.] [image: Image removed by sender.]
>
>
>
>
>
> On Tue, Aug 9, 2022 at 11:12 AM <[email protected]> wrote:
>
> We have a building where there is a roof height that changes elevation by
> 10’-0”.
>
> The higher roof will have ESFR protection. The lower roof will be ordinary
> hazard.
>
> I would like to utilize extended coverage sprinkler heads at the lower
> roof on a spacing of 20’-0” x 20’-0”
>
> This spacing voids the QR rating of the extended coverage sprinkler.
>
> I thought that there was something in the code that I cannot find where it
> talks of change in roof height.
>
> So my question is would the change in roof height serve at a draft curtain
> between the 2 systems.
>
>
>
> Bruce Hermanson
>
> President TSFP Holdings Inc.
>
> (734) 454-1350
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]

-- 
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone