Steve,
What I've done on other projects such as Dick's Sporting Goods is Class I-IV
commodities, unexpended, cartooned or exposed Group A plastics.  This was
with a maximum storage height of 8'.  It required a .425/2000 & .5/4 most
demanding sprinklers.  This was based on their spec and NFPA 13 (16 ed.)
20.3.3, hope it helps a little bit.


Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, November 16, 2021 1:52 PM
To: [email protected]
Cc: Steve Leyton
Subject: RE: Shoe store complications

Whatever the fire official wants.

SL

-----Original Message-----
From: Kyle.Montgomery <[email protected]> 
Sent: Tuesday, November 16, 2021 12:50 PM
To: [email protected]
Cc: Spencer Tomlinson <[email protected]>; Steve Leyton
<[email protected]>
Subject: RE: Shoe store complications

I would assume that there are tons of these that exist with OH2 sprinkler
designs. Are there any examples of fires in any of those and information
about whether the fire was controlled or overwhelmed the sprinklers? If the
theory says it should be protected like Group A plastics, but the history
shows that OH2 has proven sufficient, then what do you do?

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Spencer Tomlinson via Sprinklerforum
Sent: Monday, November 15, 2021 2:04 PM
To: [email protected]
Cc: Spencer Tomlinson <[email protected]>; Steve Leyton
<[email protected]>
Subject: [EXTERNAL] RE: Shoe store complications

I have worked with a very large insurer of mall properties that treats the
commodity class of any shoe store as storage of Group A unexpanded plastics,
at whatever height, etc., that applies.

Spencer Tomlinson, PE
Owner, Fire Protection Engineer


Ph:  316-202-6412
Fax: 316-202-2346
Cell: 620-955-7293

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Steve Leyton via Sprinklerforum
Sent: Monday, November 15, 2021 2:59 PM
To: [email protected]
Cc: Steve Leyton <[email protected]>
Subject: Shoe store complications

Has anyone got any experience with design or classification of a discount
shoe store that displays shoes in 8' shelving units?   These are particle
board, storage to 10', with shoes on attachments to the front of  the
shelving units and densely packed boxes with stock in the shelving.
Today's shoes can be made of textile or leather uppers, but more and more
the inventory is characterized by synthetic materials, often nylon and
polyester materials.   Except for traditional dress shoes that may still
have wood or leather soles, most shoes have various densities of foam layers
for inner and middle soles, with rubber outer soles.

Classifying the mix is challenging because of fast inventory turn-over,
especially the discount chains.   Not all are using the taller fixtures, but
many do and we've got fire officials asking for protection of stored
plastics.  I can't really impeach that finding since the stores aren't able
to state equivocally what shoes will be in stock at any time.   We're
assessing a format that's moving into a retail shell that was a Walgreen's
store and will now be discount shoes with the aforementioned 10' of storage
and a 25' deck height (an existing mezzanine is being demolished so roof is
high  for a standalone retail pad).    Seems to me that Chapter 20 is the
way to go and I'd value feedback or additional info it anyone's got
something to offer.

Thanks,

Steve Leyton, President
Protection Design and Consulting
T  |  619.255.8964 x 102  |
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.protectiondesign.com
&d=DwIFAw&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJw
Qd9A&m=cKGNzEOqtLu9spkm42kD9eVGA5WtFI8oARrHH0m-SyCbn0kCX7pIFhAk_zydkGeB&s=UC
RVIIqu4Op0eXLcV4o2_0u-dFnahjOclK5zGCvxS0w&e=
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.protectiondesign.co
m_&d=DwIFAw&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OB
JwQd9A&m=cKGNzEOqtLu9spkm42kD9eVGA5WtFI8oARrHH0m-SyCbn0kCX7pIFhAk_zydkGeB&s=
4aJnC4OJpc1QrHQX2HNNcig86dGV5INX7yYj7HDAJCU&e= >
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108 Fire
Protection System Design | Consulting | Planning | Training



_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZQLIuInh2ClcJ
0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=cKGNzEOqtLu9spkm42kD9e
VGA5WtFI8oARrHH0m-SyCbn0kCX7pIFhAk_zydkGeB&s=Uph4KkSswfWfRZn_CTml0WdAGdoOAhI
1M1WR_kudugI&e= 
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIFAw&c=wn3mZQLIuInh2ClcJ
0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=cKGNzEOqtLu9spkm42kD9e
VGA5WtFI8oARrHH0m-SyCbn0kCX7pIFhAk_zydkGeB&s=Uph4KkSswfWfRZn_CTml0WdAGdoOAhI
1M1WR_kudugI&e= 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to