Gentlemen,
The way we would interpret this in Florida per the "Florida Fire Prevention
Code" would be based on the height of the top "Floor Level". I think at the
least you are looking at 13 for the garage level, 13R for the Residential
Levels, and an "Manual Wet" Standpipe System, using Fire Department Flows with
Hydrant Supply for your Standpipe Demand. Hopefully you have a decent enough
water supply to run .05/sq ft. demand for your top floor.
We are doing 4: Story Apartment buildings here with 13 on the ground floor for
parking and 13R for the top 3: floors with no "True" Standpipe because our top
residential "Floor" is under 34' above the Fire Apparatus Staging Area. As an
accommodation, we gave the AHJ 3" "Hose Risers" with 2 1/2" hose valves.
It all depends on how high that top floor is.
John W. Farabee
561-707-5150
On Tuesday, November 9, 2021, 03:59:21 PM EST, Dane Long via Sprinklerforum
<[email protected]> wrote:
Tim,
If you have the handbook the next page actually talks about this with a
"Closer Look" at the height limitations. (2016 - Pg201)
Thanks,
Dane Long, AET
Engineering Technician | Bamford Fire Sprinkler Co., Inc.
P: 785.825.7710
F: 785.825.0667
A: 1383 W. North Street Salina, KS 67401
-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of tstone52--- via Sprinklerforum
Sent: Tuesday, November 9, 2021 2:42 PM
To: [email protected]
Cc: [email protected]
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies
Am I reading the Scope of 13R correctly?
I am designing a Sprinkler system for a building which is five stories in
height. Each floor is about 5,500 SF. The Ground floor is a parking garage
of concrete & steel (Type 1a construction) with 4 stories of Residential
above which constructed of wood (Type 3B Construction). The parking garage
shall be protected by a Dry Pipe System designed in accordance with NFPA 13.
There is a 2 hour Occupancy Separation between Garage & The Second Floor.
The Second thru Fifth levels are to be protected by a NFPA 13R Sprinkler
System. The overall building height measures less than 60' above grade.
NFPA 13R Scope: states this standard shall cover ____ "residential
occupancies up to and including four stories in height in buildings not
exceeding 60 ft. in height above grade plane."
Due to the phrase "in Buildings" am I interpreting this correctly?
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968
<mailto:[email protected]> [email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org