Assuming the building code that's applicable to this project classifies this as 
two separate buildings (a four-story Type 3 on a single-story Type 1 podium), 
NFPA 13R can be used as a basis of design in many (most?) jurisdictions.   It 
is up to the building official to clarify whether a two- or three-hour 
separation is required between the podium and upper floors, but this is 
commonly viewed as two separate buildings.

I have served as member of the NFPA Technical Committee for Residential 
Sprinklers, but this is MY opinion only.


Steve Leyton, President
Protection Design and Consulting
T  |  619.255.8964 x 102  |  www.protectiondesign.com 
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training




-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of tstone52--- via Sprinklerforum
Sent: Tuesday, November 09, 2021 12:42 PM
To: [email protected]
Cc: [email protected]
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential 
Occupancies

Am I reading the Scope of 13R correctly?

 

I am designing a Sprinkler system for a building which is five stories in 
height. Each floor is about 5,500 SF. The Ground floor is a parking garage of 
concrete & steel (Type 1a construction) with 4 stories of Residential above 
which constructed of wood (Type 3B Construction). The parking garage shall be 
protected by a Dry Pipe System designed in accordance with NFPA 13.
There is a 2 hour Occupancy Separation between Garage & The Second Floor.
The Second thru Fifth levels are to be protected by a NFPA 13R Sprinkler 
System. The overall building height measures less than 60' above grade.

 

NFPA 13R Scope:  states this standard shall cover ____ "residential occupancies 
up to and including four stories in height in buildings not exceeding 60 ft. in 
height above grade plane."

 

Due to the phrase "in Buildings" am I interpreting this correctly?

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968

              <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to