Is there a Code information sheet from the architect? Check to see what 
allowances have been taken.  
 

 
Is the separation enough for this to be treated as two buildings or is it a 
single building?
 

 
My gut answer says no to 13R but the differences in construction could make a 
difference.  
 
 
 
   
 

 
 
>  
> On Nov 9, 2021 at 3:42 PM,  <tstone52--- via Sprinklerforum 
> (mailto:[email protected])>  wrote:
>  
>  
>  
>  Am I reading the Scope of 13R correctly? I am designing a Sprinkler system 
> for a building which is five stories in height. Each floor is about 5,500 SF. 
> The Ground floor is a parking garage of concrete  &  steel (Type 1a 
> construction) with 4 stories of Residential above which constructed of wood 
> (Type 3B Construction). The parking garage shall be protected by a Dry Pipe 
> System designed in accordance with NFPA 13. There is a 2 hour Occupancy 
> Separation between Garage  &  The Second Floor. The Second thru Fifth levels 
> are to be protected by a NFPA 13R Sprinkler System. The overall building 
> height measures less than 60' above grade. NFPA 13R Scope: states this 
> standard shall cover ____ "residential occupancies up to and including four 
> stories in height in buildings not exceeding 60 ft. in height above grade 
> plane." Due to the phrase "in Buildings" am I interpreting this correctly? 
> Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III 
> Engineering Technician Fire Protectio
n Sprinkler Design and Consulting Services  117 Old Stage Rd. - Essex Jct 
(x-apple-data-detectors://3).,  VT. 05452 (x-apple-data-detectors://4/0)  CELL: 
 (802) 373-0638 (tel:(802)%20373-0638)  TEL:  (802) 434-2968 
(tel:(802)%20434-2968)   <mailto:[email protected]>   [email protected] 
(mailto:[email protected])  _______________________________________________ 
Sprinklerforum mailing list  [email protected] 
(mailto:[email protected])   
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>
>  
 
 
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to