Steve,
That is exactly what the Architect that I am working for told me. The two
hour Horizontal separation between the floors make this 2 separate
buildings.

Thank you.

Regards,
G. Tim Stone
 
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
 
   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]

-----Original Message-----
From: Steve Leyton <[email protected]> 
Sent: Tuesday, November 9, 2021 3:51 PM
To: [email protected]
Cc: [email protected]
Subject: RE: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies

Assuming the building code that's applicable to this project classifies this
as two separate buildings (a four-story Type 3 on a single-story Type 1
podium), NFPA 13R can be used as a basis of design in many (most?)
jurisdictions.   It is up to the building official to clarify whether a two-
or three-hour separation is required between the podium and upper floors,
but this is commonly viewed as two separate buildings.

I have served as member of the NFPA Technical Committee for Residential
Sprinklers, but this is MY opinion only.


Steve Leyton, President
Protection Design and Consulting
T  |  619.255.8964 x 102  |  www.protectiondesign.com
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108 Fire
Protection System Design | Consulting | Planning | Training




-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of tstone52--- via Sprinklerforum
Sent: Tuesday, November 09, 2021 12:42 PM
To: [email protected]
Cc: [email protected]
Subject: 13R Installation of Sprinkler Systems in Low-Rise Residential
Occupancies

Am I reading the Scope of 13R correctly?

 

I am designing a Sprinkler system for a building which is five stories in
height. Each floor is about 5,500 SF. The Ground floor is a parking garage
of concrete & steel (Type 1a construction) with 4 stories of Residential
above which constructed of wood (Type 3B Construction). The parking garage
shall be protected by a Dry Pipe System designed in accordance with NFPA 13.
There is a 2 hour Occupancy Separation between Garage & The Second Floor.
The Second thru Fifth levels are to be protected by a NFPA 13R Sprinkler
System. The overall building height measures less than 60' above grade.

 

NFPA 13R Scope:  states this standard shall cover ____ "residential
occupancies up to and including four stories in height in buildings not
exceeding 60 ft. in height above grade plane."

 

Due to the phrase "in Buildings" am I interpreting this correctly?

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968

              <mailto:[email protected]> [email protected]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to