There is no requirement to separate occupancy/storage design areas other
than the more demanding space has to extend 15 ft when no draft curtain or
similar barrier is provided to contain the heat and smoke to one design
area. In this case, it would seem that the space above the storage
occupancy is a concealed space -- either combustible concealed or an unused
attic as suggested. Either way, those are examples of light hazard areas
with the caveat that it is ultimately the responsibility of a registered
design professional to make that determination. Additionally, maximum
spacing and areas of coverage would vary in the space above. Combustible
concealed spaces require 120 max sq. ft per sprinkler and unused attics
would need to be spaced based on construction, combustibility and pitch
based on Table 10.2.4.2.1.

Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
*Coordinator, Engineering and Technical Services*

*American Fire Sprinkler Association*
p: 214-349-5971
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>


*Don’t miss another issue!*

Sign-up to get your exclusive copy of the industry’s leading membership
magazine *Sprinkler Age* <https://sprinklerage.com/subscribe/> delivered
straight to your mailbox, inbox, or both! Subscribe now to get the latest
information you need to know and never miss another issue.


On Wed, Oct 6, 2021 at 1:57 PM Scott Futrell via Sprinklerforum <
[email protected]> wrote:

> Mike,
> That is an interesting situation and thought.
> I would defer to Messer's Hall and Denhardt.
> For CMDA sprinklers there are requirements in light and ordinary hazard,
> but I don't see specific reference to combustible roof materials for
> storage and CMDA.
> The are limitations for spacing of CMSA sprinklers with combustible
> construction 13.2.6.1, but I don't see differences between combustible and
> non-combustible in the ESFR chapter.
> Storage sprinkler tests are conducted with non-combustible roof
> construction to the best of my knowledge. I don't see a requirement for
> non-combustible roof materials in the 2022 edition, storage section.  It
> seems that if the sprinklers are operating as intended the combustible roof
> material would not ignite before sprinkler operation, but...
> I didn't spend a lot of time on this research, so I hope I didn't miss
> something.
>
> Scott
>
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 11:43 AM
> To: [email protected]
> Cc: Mike Morey <[email protected]>
> Subject: RE: Attic protection over a storage occupancy
>
> Maybe I wasn't clear, this is an existing unsprinklered building attached
> to a sprinklered building at a firewall.  I presume when constructed it was
> per code.  The intent is to add fire protection at the request of an
> insurance company.  All areas would be protected as stated, my concern is
> whether or not a traditional light hazard attic design is appropriate for
> the space above the plywood ceiling given that it's a plastic storage
> warehouse below.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /
> cell 260.417.0625 /  fax 260.487.7991 email [email protected]
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Art Tiroly via Sprinklerforum
> Sent: Wednesday, October 6, 2021 11:36 AM
> To: [email protected]
> Cc: Art Tiroly <[email protected]>
> Subject: RE: Attic protection over a storage occupancy
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> No building size is indicated. Does the building code require protection?
> Plastic storage may be considered a high hazard.
> If protection is a code requirement then the attic requires protection.
> Without protection a fire in the attic will likely cause a total loss of
> the building and contents.
>
> Art Tiroly
>
> ATCO Fire Protection
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 10:59 AM
> To: [email protected]
> Cc: Mike Morey <[email protected]>
> Subject: Attic protection over a storage occupancy
>
> Applicable code/standards would be IBC 2012 and its references (NFPA 13
> 2010
> mainly) I'm not coming up with a "why not" for this, but it doesn't give
> me a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
> storage in racks.  The building is a standard 4:12 wood truss building with
> plywood sheathing at the bottom of the trusses (with a layer of fiberglass
> batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
> 2x construction with fiberglass batts.  I can't come up with a reason I
> can't protect the space below the plywood according to the storage
> requirements (looking at .6/2600 dry system, rack storage of Gp A plastic
> to 20' max <5' clear, doing CMDA both because they barely have 18" clear
> and they want a dry system) and the space above as an unused light hazard
> attic, potentially with "back to back" style attic heads.  Anyone see a
> flaw with this logic, or any other pitfalls to watch for due to this
> construction scenario?  I don't love this scenario but the customer went
> out of their way to avoid sprinklering the building
>   origina  lly and built it to the bottom dollar, but now a new insurance
> carrier may require it to be protected.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
> 260.417.0625 /  fax 260.487.7991 email [email protected]
>
>
>
> This message is for the named person's use only.  It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission.  If
> you receive this message in error, please  immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender.  You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to