A-okay - Absolutely two different design criteria: attic above is light
hazard and your system below is group 'a' plastics storage commodity. I
would do it the same way. There's no need to design the attic to the lower
area storage density in your case because they're not storing group 'a'
plastics up there.

JH

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Wed, Oct 6, 2021 at 9:42 AM Mike Morey via Sprinklerforum <
[email protected]> wrote:

> Maybe I wasn't clear, this is an existing unsprinklered building attached
> to a sprinklered building at a firewall.  I presume when constructed it was
> per code.  The intent is to add fire protection at the request of an
> insurance company.  All areas would be protected as stated, my concern is
> whether or not a traditional light hazard attic design is appropriate for
> the space above the plywood ceiling given that it's a plastic storage
> warehouse below.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825
> direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
> email [email protected]
>
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Art Tiroly via Sprinklerforum
> Sent: Wednesday, October 6, 2021 11:36 AM
> To: [email protected]
> Cc: Art Tiroly <[email protected]>
> Subject: RE: Attic protection over a storage occupancy
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> No building size is indicated. Does the building code require protection?
> Plastic storage may be considered a high hazard.
> If protection is a code requirement then the attic requires protection.
> Without protection a fire in the attic will likely cause a total loss of
> the building and contents.
>
> Art Tiroly
>
> ATCO Fire Protection
>
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of Mike Morey via Sprinklerforum
> Sent: Wednesday, October 06, 2021 10:59 AM
> To: [email protected]
> Cc: Mike Morey <[email protected]>
> Subject: Attic protection over a storage occupancy
>
> Applicable code/standards would be IBC 2012 and its references (NFPA 13
> 2010
> mainly) I'm not coming up with a "why not" for this, but it doesn't give
> me a warm fuzzy.  I have a wood framed "pole barn" being used for plastic
> storage in racks.  The building is a standard 4:12 wood truss building with
> plywood sheathing at the bottom of the trusses (with a layer of fiberglass
> batts on them above) creating a flat ceiling at 18' AFF, walls are exposed
> 2x construction with fiberglass batts.  I can't come up with a reason I
> can't protect the space below the plywood according to the storage
> requirements (looking at .6/2600 dry system, rack storage of Gp A plastic
> to 20' max <5' clear, doing CMDA both because they barely have 18" clear
> and they want a dry system) and the space above as an unused light hazard
> attic, potentially with "back to back" style attic heads.  Anyone see a
> flaw with this logic, or any other pitfalls to watch for due to this
> construction scenario?  I don't love this scenario but the customer went
> out of their way to avoid sprinklering the building
>   origina  lly and built it to the bottom dollar, but now a new insurance
> carrier may require it to be protected.
>
> Mike Morey
> CFPS 3229 * NICET S.E.T. 123677
> Project Manager * Fire Protection Group
> Shambaugh & Son, LP an EMCOR Company
> 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell
> 260.417.0625 /  fax 260.487.7991 email [email protected]
>
>
>
> This message is for the named person's use only.  It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission.  If
> you receive this message in error, please  immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender.  You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!PEy36P2Ree2IDKHDssMLwq70UBvwk5gX32aU8NcgXc8x_JP_Pkqr3gfirY-jNCeY$
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to