Applicable code/standards would be IBC 2012 and its references (NFPA 13 2010 
mainly)
I'm not coming up with a "why not" for this, but it doesn't give me a warm 
fuzzy.  I have a wood framed "pole barn" being used for plastic storage in 
racks.  The building is a standard 4:12 wood truss building with plywood 
sheathing at the bottom of the trusses (with a layer of fiberglass batts on 
them above) creating a flat ceiling at 18' AFF, walls are exposed 2x 
construction with fiberglass batts.  I can't come up with a reason I can't 
protect the space below the plywood according to the storage requirements 
(looking at .6/2600 dry system, rack storage of Gp A plastic to 20' max <5' 
clear, doing CMDA both because they barely have 18" clear and they want a dry 
system) and the space above as an unused light hazard attic, potentially with 
"back to back" style attic heads.  Anyone see a flaw with this logic, or any 
other pitfalls to watch for due to this construction scenario?  I don't love 
this scenario but the customer went out of their way to avoid sprinklering the 
building origina
 lly and built it to the bottom dollar, but now a new insurance carrier may 
require it to be protected.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to