/ just one meter.
Thanks for this and all the other great info.
Eric R. Andrews
NABCEP Certified PV Installer
Klamath Falls, OR 97601
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
Thanks to all the input on this topic... SolarPro Magazine (proving to be a
great info source to installers!) pg. 22 does outline the process nicely.
One production meter per leg, so two necessary for 2 stack GVFX system.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc
Our AHJ has a list of reasons that shoot down even the thought of using
Enphase... including, his requirement for AC and DC discos on each
inverter...
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
Klamath Falls, OR 97601
Hi Gang,
For the number of ads I've seen for the pr
Fellow PV Techies -
When designing an AC coupled PV system using Outback: Am I correct that the
battery bank can be minimally small, as they are just there to power the
GVFX Output and mimic the grid for the grid-tied inverter of choice?
Thanks,
Eric R. Andrews
NABCEP Certified PV Installer
Hey all -
Just wondering what your favoring inverter combo is for a 25 kW job.
Building has 4:12 pitch, 135 deg. az. We get a significant amount of snow,
as well. Looking for gear pros & cons.
Eric R. Andrews
NABCEP Certified PV Installer
Klamath Falls, OR 9
Evergreen 195's probably... service is 3p 208.
Eric
>>
Eric,
What are you using for modules? I'm a big fan of the SMA inverters--very
reliable, easy install, excellent support.
There's a good article in the new journal Solar Pro deals with this
issue of multiple sm
r.
Heck, I should be selling these things.
My felt bottom fishing boots are way stiff. can't imagine a day in those
things.
Eric R. Andrews
NABCEP Certified PV Installer
Klamath Falls, OR 97601
>>
Any thoughts on the best type of shoe for working on comp shingle roof?
Good tra
il Jan. 1. You
may want your customer to ok that w/ their CPA.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273-3200 office
<mailto:[EMAIL PROTECTED]> mailto:[EMAIL PROTECTED]
Saving th
-grid installs that use the AGS function. Just wondering if one method
is better or not.
Cheers,
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
Klamath Falls, OR 97601
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Does anyone have any experience using Helical screw pier footing for ground
mount racks?
Eric
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options
I believe these guys are the patent holders. yes Canandian.
http://helicalpiersystems.com/
Eric
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches
Is anyone else dealing w/ a general contractor who wants to sell solar?
I'm curious of the work arrangement, as we are being propositioned by a
high-end custom home builder who is normally quite busy and says he "can
sell a lot of solar".would be tricky w/ all the incentives.
Gro solar.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273-3200 office
<mailto:e...@ecosolarnow.com> mailto:e...@ecosolarnow.com
Saving the World... One Solar Panel at a Time!
Fr
y... Sometimes
customers are not privy to how crystalline technology works and a discussion
of efficiency is necessary. A customer will get more "bang for their buck"
if they make efficiency their first priority.
http://us.sanyo.com/HIT-Power/HIT-Power-HIT-Photovoltaic-Module
Eric R.
Hi Wrenches,
I'm shopping for a 72 panel, fixed, ground mount. What are your
favorites for arrays in the 10 KW+ range?
Thanks in advance,
~ Eric
--
---
Eric Hansen, RE System Designer & Installer
Electron Connection, Inc.
O
We have similar curiosity but using Tigo. We also would like to use APS QS1
micro-inverters and the MLPE mounts that Ecolibrium has don't really fit
the bill.
Eric Smiley, P.Eng.
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-60
You may be thinking of the change to not requiring overcurrent protection
on both conductors.
Eric Smiley, MASc
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca <http://www.viridianenergy.ca>
yone else has had this problem and/or solution.
Eric Smiley, MASc
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca <http://www.viridianenergy.ca>
<http://www.v
o their circuit board.
Eric Smiley, MASc
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca <http://www.viridianenergy.ca>
<http://www.viridianenergy.ca/>
RENEWABLE POWER NOW
On Mon, 1 Feb 2021 at 1
I have a client whose Trace DR 1524 inverter (yes, it's an old system) fan
is running constantly.
I haven't been to the site (3 hour drive, 1 hour boat ride) but I am
guessing that it's a failure of a temperature sensor.
Does anyone have experience with something like this?
Er
I've done 3phase with 6 Schneider Conext XW. It worked well but when you
convert to 3-phase you lose surge capacity because you are turning the
inverters into 120V inverters from 240.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 &l
Just remember to turn off the AC coupled solar when manually starting the
generator!
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>
with Discover
Magnum doesn't appear to have any UL9540 battery partners
Sol-Ark has a long list on their website.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
The spec sheet indicates it is rated as Service Equipment in the US but not
in Canada. :-(
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianener
itial savings with SokArk disappear. I can't recall the last time I had
to repair/service a Magnum system unless it was user error.
Keep it simple!
Eric Smiley
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca
On Thu., Ja
Usually I wouldn't chime in with a single example but we have a single
customer with a Kohler 12RES on propane and a Connext XW+.
It's worked well for three years and was easy to connect.
Eric Smiley
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll fre
I looked up the CSA record for the XW PDP and it shows:
- Maximum System Voltage (DC) 150V dc
- Maximum Battery System Voltage 62 V dc (48V nominal)
- Maximum System Voltage (AC) 140/280V ac
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004
right now.
Does anyone know if there's a way to reduce the transfer time? The
transition to charging is smooth. I don't understand why it's so clunky
transitioning back to inverting.
Eric Smiley
Project Manager, North Island
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll
YES. We get ours from PLATT Electric. Most electric supply houses should
have this wire. It is definitely nice for your DC source circuits.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
Electrical Contractor #C623
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
inverter that does the neutral isolation/grd
switching, but it's not a Grid tie inverter.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273-3200 office
<mailto:e...@ecosolarnow.com&g
inspectors.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
www.ecosolarnow.com
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cg
asily remove from the separate disconnect box like the fronius IG+ does
if future service is required.
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
Electrical Contractor #C623
www.ecosolarnow.com
PO Box 5194
Klamath Falls, OR 97601
541-281-8252 cell
541-273-3200 office
mai
or if we are having poor luck.
Our other string inverter systems are not displaying this problem, which
leads us to believe it isn't due to installer error.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIA
Also check bonding and ground loops (e.g. genny neutral bonded and also
bonded at main panel). This can cause voltage to bounce around and the
inverter won't sync.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*
Skybox is discontinued and tech support is limited. There are still
significant software issues with them that make them unreliable for battery
back-up. We are in the process of replacing the 3 Skyboxes we wish we had
never installed.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004
I am having the same problem - same situation. I am going to tweak the
efficiency value and see if it helps.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <http
n the CAT5 cable anyway?
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>*
___
List spons
inverters configured for
3-phase, I would recommend an external transfer. The relays have a habit of
welding.
Once they were configured properly, there was no problem starting large
HVAC loads and even large single phase loads were OK.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 25
stry keeps evolving and improving, which is great for keeping us
on our toes and I find it very exciting.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://v
resonance with the inverter enclosure. But it's
the first time we have encountered this.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <
recommission the
system.
*Eric Smiley,* Project Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>*
On Tue, 6 Dec 2022 at 11:45, Tump via RE-wrenche
nly a very thin
coating is sufficient. I use it on all connections that I don't solder.
Eric Stevens
Vermont Made Energy
Grafton VT___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address:
Keep in mind the Fortress eVault is a 500 lb beast. Our installers
complained about it and we've moved to smaller, rack-mount units and are
currently testing the HomeGrid Stack'd in various configurations.
*Eric Smiley,* Design Manager
e...@vecoop.ca
T: 250.703.6004 <+1
Last time I had an AC relay go, I ordered a board from Mark Snyder.
mseproje...@marksnyderelectric.com
Eric Smiley
Design Manager
E: e...@vecoop.ca
T: 1-888-386-0116 ext 702 (toll free)
C: 250-703-6004
W: viridianenergy.ca
On Tue., Aug. 1, 2023, 16:00 Andrew Perkins via RE-wrenches, <
e and good service in Australia and Europe. Not sure why the US gets
short shrift.
*Eric Smiley,* Design Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>*
t get much snow so a shallow tilt is OK.
*Eric Smiley,* Design Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
* <https://viridianenergy.ca/>*
On Wed, 25 Oct 2023 at 17:42, integrity
We were called to repair a system where this happened.
All the micro inverters were fried and so was the generator. It caused a
voltage rise that the monitoring system recorded at 348 V before it went
down, when the PV ran the generator as a motor.
*Eric Smiley,* Design Manager
e...@vecoop.ca
T
.
IMHO relying on firmware and circuit boards to keep your system running and
protect it from catastrophic failure is not sustainable.
*Eric Smiley,* Design Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENERGY.CA <https://viridianenergy.
We have a client with a Huawei 9KTL-USL0 who recently contacted us about
his system.
Does anyone know how to obtain tech support in NA for these products?
*Eric Smiley,* Design Manager
e...@vecoop.ca
T: 250.703.6004 <+12507036004>
T: 888.386.0116 <+18883860116>
*VIRIDIANENER
unded, and none of the DC conductors
should be white or grey, they can both be hot with respect to ground.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridianso
If you want UL9540, the AES rackmount has to be in the Slimline enclosure.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-h
Install stand-alone charge controllers. That is the only way to get
redundancy.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-h
ks like the DR is so dumb it, it works just fine with the BMS keeping an
eye on things.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmai
electronic noise. The customer decided to live with it rather
than try to fix it. My recommendation would be some L-C line filtering
tuned to 60 Hz to reduce electronic noise. Try your system in bypass.
Eric Stevens
Vermont Made Energy
Grafton VT
(802) 289-2280
On Oct 21, 2024, at 9:12?AM
tions.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702155901939000&usg=AOvVaw3SHpXB-WRSlzWmjpz4htqG>
Vir
. We are crossing our fingers we don't have any failures.
Eric Smiley (he/him) - Design Manager
250.703.6004
e...@vecoop.ca
888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702
program the logic on the phone app. Once you
have the hub and phone app installed there are a ton of other "smart"
sensors and devices that work with the system.My off-grid home has
gotten a lot smarter in the past couple of years!
https://shop.yosmart.com/ <https://shop.yosmart.