William
We have found fire raptor better suited for our roof mounted off grid or
back up systems what modules are you specing and what inverter Solark or
Outback. I have seen arc fault shut down the CC on the OB and inverter on
the Solark, none of the faulted systems had Fire Raptor used but beware
I have seen repeat melting and freezing rip the frames from the modules,
granted these modules were not sealed or glued in. But just consider if
water can get in a rail and freeze then any extruded frames with inclosed
channels can be effected. Option is to drill the boxed channel to promote
drain
Jason
The programming is different with a battery vs no battery so if he is
removing the battery this may create an issue, I have not tried myself to
disconnect a battery once in place
Jerry
On Fri, Apr 1, 2022 at 11:52 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote
Fortress 5.4 can be but the 18.5 is better but not wall mounted, simplify
same as the fortress 5.4, lots of cabling, does not look good
On Wed, Apr 6, 2022, 7:36 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I'm trying to find out what wall-mounted outdoor rate
Need more than this, we have amperage, we need distance, temp, # of wires
per conduit, also at 480 you may want to verify cold temp for over the top
voltage @ VOC, any RSD device(s) being used? Help to have total module
count, as an example use a combiner to make 4 strings, 2 of equal voltage
per i
Wrenches
In the am it will latch up but in the hotter days the inverter may not
reconnect in the event of corrected outage resulting in no production
through the rest of the day, if the VMPPT falls below minimum tracking you
might not get much production due to fixed power settings. I have seen thi
You must meet all expected source output potentials within the design and
operating limits, as long as the distribution panel and connected wiring is
rated for the max output of the protected source then you are good. A 200
ATS connected to a 10 kW genny does not require 2/0 as it will never meet
t
You may want to look at fire raptor as a RSD option.
Jerry
On Tue, Apr 19, 2022, 9:42 AM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> HI All
>
> I’ve got a project coming up that has specified a Schneider XW 80/600
> controller.
>
> Its going to need RS.
>
> Is the only produ
I have only seen this if you have spotty signal strength to the inverter,
are you hard lined out or a bridge
Jerry
On Fri, Apr 22, 2022, 10:31 AM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Friends:
>
>
>
> I installed a Radian AC coupled system a few months ago.
Sure if the peak voltage is not getting to the battery then low SOC will
result. Programming may be a result of comms issues poor or due to old
firmware.
Jerry
On Fri, Apr 22, 2022, 10:31 AM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Friends:
>
>
>
> We are setti
Just get an empty GSLC, at least it has the breakers
Jerry
On Sat, May 7, 2022, 1:44 PM Kirk Herander via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Ok, time to break wrenches radio silence over the last week.
>
> My question concerns the Radian battery terminal connections. I don'
;>>>> example,
>>>>>>> load output conductors run to a 100A main breaker panel board.
>>>>>>> Obviously
>>>>>>> depending on circumstances, a #4 copper could fit the bill.
>>>>>>>
>>>>&
Wrenches
The new solark 15 has a 200 amp rated contactor this is so if you want to
have whole home pass through you can but if you only have an inverter then
use that as your starting point and if the genny is contributing then add
that is, you do not need 2/0 for a single 15 k off grid but you may
Are your solark install with arcfaults have RSD, as not all RSD devices
work well and can call faults.
On Tue, May 10, 2022, 10:17 AM Eric Smiley via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> A general question for those who have installed Sol-Ark.
> We have a handful of systems t
Just so it is abundantly clear to all that wish to modify or cut open an
inverter, SMA will not do any advanced replacements of any inverters that
have been modified, Outback is not a problem as they are field serviceable,
SolArk is a all in one unit and any modification to the cabinet will
prevent
If you have a pv combiner box, you may be able to restring from there and
use a 48 vdc charger
Jerry
On Thu, May 12, 2022, 9:47 AM Kirk Herander via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Looking to charge a 48 V battery bank from a 24 V old PV array. I guess I
> could use a DC
What are you using for the RSD, I have found they all fault out except for
fire raptor, dont go with any features, keep it simple
Jerry
Jerry
On Tue, May 10, 2022, 10:17 AM Eric Smiley via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> A general question for those who have installed So
Regarding the tape on the back sheet
I have seen Novis installers keep the tape to secure the modules and I have
also seen it with the tape stll attached to the wires laying on the roof so
in my humble opinion the tape is for shipping only and is not to be used as
a wire management system.
Jerry
NA
When it comes to what manufacturers will have in the future,
guaranteeing or stating that a product will have a feature in the future is
mostly doomed to failure, enphase, LG Chem, Ford and so many
obsolete inverter manufacturers that have come and gone. You might as well
be selling snake oil, you
oor
>promptly?
>
>
>
> I really try to support manufacturers, wholesalers, & companies that meet
> these criteria.
>
>
>
>
>
>
>
> Dana Orzel - E - d...@solarwork.com - C - 208.721.7003
>
>
>
> *From:* RE-wrenches *On
> Beha
Matt
Look at the fortress Evault Max 18.5 BMS, display, battery enclosure all
together and they work well better than the simplify parts and pieces,
Jerry
On Fri, Jun 10, 2022 at 4:08 AM Matt Sherald via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> I've got cust
Jeremy
I have and used a second PS1 and added a transformer to connect the two,
worked fine was just parts that all needed to connected
Jerry
On Tue, Jun 14, 2022, 4:08 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello
> Does anyone have a solution for adding
Jay
https://www.fuelminder.biz/waterminder%20collection/gallagher.html
these guys have a variety of monitors, I am getting one myself
Jerry
On Fri, Jun 17, 2022 at 2:31 PM William Bryce via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi Jay
>
> Don’t think anyone else chimed in on t
PM Dana Orzel via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Tape is not approved as a wire retaining device as far as I can find in
>>> the NEC :-]
>>>
>>>
>>>
>>>
>>>
>>> Dana Orzel
ave
>
>
> On Thu, Jun 30, 2022, 7:00 PM Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>>
>> Dave
>> Nothing should be attached to the back sheet as it can be an issue down
>> the road, I might want to look at looping the co
We used sun bandit years ago and it was a regular accurance to go out
trouble shoot then go back with the part. No more of that! Just get an
electric Rheem marathon and put it on a off peak timer, less parts from
companies that don't respond.
Jerry
On Mon, Jul 4, 2022, 6:48 PM Chris Sparadeo via
Is there any other power sources on this building, does the leak go away at
night, what is the voltage of this tingle?
Fun times!
On Sun, Jul 10, 2022, 2:10 PM Ron Young via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I have a customer that has self installed an array on a metal roo
Fortress Evault max, good form factor, simple
Jerry
On Wed, Jul 13, 2022, 3:05 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Any suggestions for LiPO batteries that play nice with the SW5548? This
> system also has an Outback CC for a pretty small PV array (rat
Most AGM's don't like voltage that high and it swells the battery and
destroys its storage capability alot of the time
Jerry
On Fri, Jul 22, 2022, 7:50 PM Steve Higgins via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> William,
>
> If the battery cases swelled, they saw over 52 degree
Its not clear to me if you will actually have a DC side coupled connection
in talking about the pole mount. If so then it does work but if not then
no, the big question is how would you restart the inverter to restart the
SE to start the charging process on the AC side, answer, you can't in most
ca
to AC vs. DC coupling, as someone said.
>
> On Sat, Jul 30, 2022 at 3:58 PM Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Its not clear to me if you will actually have a DC side coupled
>> connection in talking about the pole mount. If
Jason
Is the installation designed for 208 as you have greater limitations then
240, so now replace the buss and all the breakers, after that run currents
tests and see what you have. I had a 3 phase that the tin cam off the buss
and looked like a plazma cutter due to the exposed aluminum
Fun times
Drake
This is an interesting topic, Q, do bi-facials really work? A, it depends,
Solution, low profile on a roof may not so much its all about reflectivity
so higher off the ground(roof) the better. A parking lot canopy might see a
measurable improvement if the parking lot is a light reflective col
You also might want to look at the solark 12 and 15
On Thu, Aug 18, 2022, 6:06 AM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> I have several Enphase system customers looking to add battery storage.
> The Enphase system, which I got certified in, comes across t
The cycle life sounds good the warranty cycle for off grid is far less than
blue planet and fortress. If you compare the fortress x 2, 18.5's with a
better warranty it comes out cheaper. I do see a display but l only see
volts. Pretty low surge, is there US warranty administration? Good luck,
On
I did some infrared tests years ago on metal vs comp,vs TPO this along with
color, attic temps. As an example regular comp roof (Dark color non
reflective) in clear sun, gable end vented rafters and plywood temps were
135 degrees and under the modules a foot away was 85 Degrees, so in short
it will
This has been an issue with me, these batteries all have a basic BMS and
then why does Simplify not support their own with a readable BMS, Fortress
has a monitor, Blue planet has a BMS.
Jerry
On Fri, Sep 2, 2022 at 11:32 AM Matt Sherald via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
Outback FX R can be built to be 3 phase and solark also works, for 30 k l
would look at solark, 3 12's or 15's.
Jerry
On Thu, Sep 8, 2022, 4:42 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> What inverter options are there for 3 phase, UL listed, of
Wrenches
The 15 is not that similar to the 12, there is no OCP on most of the AC
inputs, this means you need to add that in, connection to the grid will
require a OPD maybe a traditional AC disco we used for years, you may need
a 200 amp with fuses as required by your meter max. Off grid you would
Wrenches
We have used the midnight box, both with and without OCP breakers, I dont
think they are large enough for what you want, we have up to 80 kWhrs
connected going to 5 Radians.
Fun times
On Thu, Sep 8, 2022, 8:47 PM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> He
Wrenches
Solark issues, I have them living off grid, 3 phase and grid tied back up,
both AC and DC coupled with only one intermittent comms issue, does not
seem to have any more issues than OB and less than Schnieder, all are
connected to Fortress 18.5's or Blue Planet BMS interface seems hardy,
Wo
Hilton
With all the inverters out there SMA has been far ahead of all the rest,
which inverter are you looking for, Fronius has been an issue, power one
has been problematic,
Jerry
On Thu, Sep 29, 2022 at 11:53 AM Hilton Dier via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Esteemed
ailures. I
> suggest that your friend gets a fresh set of eyes on the system and look
> for that oversite we have all made and just can’t seem to see it on our own.
>
> Pieter Huebner
>
> Off Grid Enterprises
>
>
>
> *From:* RE-wrenches
> *On Behalf Of *
Wrenches
It might sound cheap but I have incandescent lamps, also used reptile tank
heaters, watered heaters work too.
Funtimes
On Fri, Sep 30, 2022, 12:34 PM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello all you brilliant people:
>
>
>
> Does anyone have somethin
Wrenches, William
I have installed quite a few memory saver kits in the old SW Inverters, ask
around if there are any kits still around. This is a viable solution to the
Li batteries. Here is something else, the BMS's should protect the
batteries anyway, in part of my testing we did this using chea
On the system size of batteries We have had several issues with resi and
80kWhr limitations, I dont know if this is an issue for you or not just
want to through it out there.
Jerry
On Fri, Oct 21, 2022 at 11:14 AM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi f
Wrenches and Ray
So did you properly configuer the master slave battery config, I have
several set up with no issues SOC is within1 to 2% and volatge is the same,
what inverter/chargers are you using are you still connnected to bat temp
sensors I assume there is no connection to the inverter(s)
Jer
Wrenches, Christopher
I have done quite a few and per solark have always connected in the
inverter with no issues, Now with that connecting to the output side it
would do much the same work until it did not then shut off the modules.
Fun times
On Wed, Nov 16, 2022 at 6:33 AM Christopher Warfel via
Wrenches, Howie
As SOC climbs the rate of current will reduce current flow, what was the
SOC when you had both connected and configured master slave with in the
batteries
Fun times
On Wed, Nov 16, 2022 at 9:59 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Good
This is great to hear even as l have used fortress with no tech support
issues but rather than a phone conversation a zoom might be better as you
can hear and see from the horses mouth. Add in all the notes of all of the
questions and get an answer back one time not a dozen.
Just a thought
Jerry
O
Wrenches, William
I did a few back up systems for data hubs, we had 250+ kWhr systems. We had
to have a firewall between the batteries and everything else. We used
copper stock 1/2 x 2" and 20' long, each bank connected to the buss with
its own 250 a breaker, the buss was above the batteries mounte
This is interesting, set all aside temps, how its constructed, the power
cycle is what changed it. Sounds like the inverter(s) were stuck in a
finish charge, this may be a programming issue, is it available on line to
watch remotely, has it done that again, next day?
Fun times programming
On Sun,
Wrenches
First of all confirm as it might well be the inverter, SMA is a great
solution for a replacement however like much we deal with are in short
supply, if it is a battery inverter then the Solark or Outback are good
solutions.
On Thu, Dec 8, 2022 at 1:14 PM Sam Haraldson via RE-wrenches <
re
The xantrex had one fused line on some of the GT lines,as l recall its a 15
or 20, no this is not the GFI Fuse, old SMA's also had just one.
On Thu, Dec 8, 2022, 1:14 PM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Howdy Wrenches,
>
> Any "old timers" here care to c
Wrenches, Jay
You may want to remove the battery temp sensor and see what it does, an
open/short in the sensor will send it all over to compensate for the range
issue, the issue may also be in the temp compensation board inside the
inverter.
Jerry
On Tue, Jan 3, 2023 at 6:16 AM Jay via RE-wrenche
Wrenches, Glen
I have installed fortress Evaults on both the older and newer SMA SI
inverter/chargers, you will need to make some changes to the charger config
with the temp sensor. It is somewhat wild in the current state and must be
locked down, it is not very difficult to do and makes a big diff
Wrenches, Chris
I would only look at outback, Date available and easy to access, can be
easily connected to additional components in the future.
Fun Times
Tue, Jan 3, 2023 at 6:43 AM Chris Sparadeo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hey there,
>
> I have a client with
Kirk, wrenches,
There are several gravity storage systems out there in the renewable energy
industry. I did water lift and drain back through lift pumps and
hydro-electric. No different than all storage systems, it's all about
capacity. Great talks
Jerry
On Wed, Jan 4, 2023, 7:23 AM Kirk Herander
Wrenches and Bruce
I have sent some people there that are not practical and want want want,
they are a DYI shop and what l get from customers is there in house design
and engineering is not what l would use myself. As a last ditch l tell the
prospective buyers to get what they want and l can do an
William
We have done 80 kwh Blue planet resi installs in the past (at the time this
was as large as we could go in resi) anyway the BMS has a push to start and
on/off buttons we just connected into them and we compliant, rotory switch
at 24 volts 10 mA is all that is needed, Now not all BMS.s can d
Wrenches.
You might want to consider turning off the inverter as a solution to
turning off the batteries, we have this feature as part of our installs
with outback real simple then no chance of AC anywhere, Not going to pop a
CC, no chance of run on and it has passed every time. Just a thought that
Hey wrenches
I have been to the Sacramento facility, they are 48 vdc nom. We ran some
tests on site pushing pretty hard and the battery did well, no volt drop,
was well over 250 amps for an extended period of time. It might be good to
reach out to them and do a visit to see how it works, bring you
Carl
Wrenches, E Guage make a great energy monitoring platform
Jerry
On Mon, Jan 30, 2023, 5:43 PM Carl Adams via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello wrenches,
> I have a client that is installing solar on a commercial building where he
> has four points of connection
Pet heater have worked for me, I air gap a sealed heater box under the
battery, thermostat inside the top of the battery. It's slow and low power
but does the trick
Fun times
On Wed, Feb 8, 2023, 3:05 PM Ray Walters via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi All;
>
> I have
Any plumbing supply shop has these, soft copper comes in 50 feet and up,you
can use 1t2",5/8" or 3/4" I use double 1/2" and "T" it on top of the tank,
Funtimes
On Wed, Feb 22, 2023, 4:16 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Thermal Wrenches,
> can some
Wrenches, Dave
I have had this issue, first turn off everything, check static voltage,
this will drive everything else. If the static is 240 L-L look at the
utility side you might have small conductors, you might also have a
transformer size issue bottlenecking the current. Next turn loads more th
Wrenches
It might be easier to use the wire cabinet for the radian, but hey thats
just me
On Thu, Mar 2, 2023, 9:47 AM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi All,
>
> I have a stand alone system that was upgraded from an FX inverter to a
> Radian WITHOU
Wrenches/Hilton
Home run connections, confirm brand, had issue where it needed more volts
to overcome the poor connections. You will need to be on site with at least
two techs and check each homerun first but l have had module to module
issues. I have also had internal issues at the Jbox some brand
Wrenches
Sounds like a SIP's type product, there are quite a few multi hole
attachment bases that are designed for SIP's. Most will have a larger base,
lots of holes for screws to attach that do not require rafters underneath
to attach.
Fun times
On Wed, Mar 29, 2023, 8:30 AM frenergy via RE-wrenc
Wrenches, Mac
You might want to find out what size battery you currently have so you can
build from there, this way you can know the current values under sized Li
on will make for an unhappy customer service.
Fun times
On Tue, Mar 28, 2023, 8:07 PM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-
Wrenches, Corey
Yes it was a thing in California but soon fell off the radar, They were
based or had a shop in Sacramento CA. It was mainly designed for BIPV but
was adopted to framed panels, grounding is an issue, mounting of the
electrical another. l have had bolted modules rip out of unirac in H
Jeremy
I got a bunch of sharp 185's
Jerry
On Mon, May 1, 2023, 1:35 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> If anyone has a model # NE170-U1 Or similar size / wattage 72 cell
> modules laying around in good condition please contact me off the list
>
Lary do you want analog or digital, egauge is great for remote monitoring
or just your basis utility meter and socket is a inexpensive solution a
simple results.
Jerry
On Thu, May 11, 2023, 1:21 PM Larry Brown via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
> Does anyone have a reco
Wrenches
Bottom line package price, all inclusive one number, I list all the major
components inverter, modules ect. and all of what is included permits
engineering thats it system cost, tax incentive, rebate (if any) no a la
carte here sorry.
But thats just me!
On Tue, May 16, 2023 at 8:11 AM Jay
Bill
You do need to verify that you also have No current, l see this quite a few
times where modules have failed just to find a shorted inverter or damaged
conduit where one wire overheats cause unknown and the cascade is they all
melt together and it's such a great short that voltage is near zero.
Kirk
Personally I would go with solark that's what they do, make inverters not
other stuff just like I would use Fortress for the battery because that's
what they do, is it similar sure but why? If it's the same then go with a
known product and track record, we are seeing this mre and more and that
Wrenches
I have used Verizon cellular modems, looks the same works the same just pay
for data mine was 25 per month 2 year contract, very simple, I plugged in
both the blueplanet battery's and outback mate and there we had it. I'm
sure all the carriers have the same thing.
Fun times
On Mon, Jun 5,
Kirk
As the batteries come up to charge does the vibration subside. Are the
battery cables spun together "corkscrew like" l have seen this correct DC
noise. I have an 8 on 8 just like your 10 and l have no noise at all, mine
come in from each side of the battery combiner, how is your install
config
are the ramifications down the road?
> Loosening of connections I suppose would be one.
>
>
>
> On Fri, Jun 30, 2023 at 12:40 AM Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Kirk
>> As the batteries come up to charge does the vi
issues.
>>>
>>> I used cable tray because the CT-rated cable is in free air, no derating
>>> of current required. But merely pairing the leads may be the issue.
>>>
>>> I could rearrange the inverter cables and twist the sets, but doing it
>>> from co
Jay
Fortress is a good solution, blueplanet is a great battery also, both have
been around long enough. So many manufacturers talk the big warranty but
don't have time in the field to support what they say. I ran a lab testing
batteries and saw some impossible warranties.
Fun times
On Thu, Jul 13,
03.6004 <+12507036004>
> T: 888.386.0116 <+18883860116>
> *VIRIDIANENERGY.CA <https://viridianenergy.ca/>*
>
> * <https://viridianenergy.ca/>*
>
>
> On Thu, 13 Jul 2023 at 19:34, Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wr
Kent
I can assume there is no backsheet external damage, These look cell
fractures, more common on poly, they may be cause of manufacturing or a
result of overheating traces or both. Run an IR Curve test and see if this
is resulting in decreased output. Sharp had a similar issue when they
stepped u
Jay
I don't seem to have an issue set the inverter to shut down befor the
battery and the CCwill begin to charge again untill voltage rises enough to
start the inverter back up. Also set the genny to come on even above the
inverter voltage so a shut down does not even accure. If you use lithium
don
Jason
In plenty of applications l will use couplers with chase nipples, height is
one issue but installed working height is very important. I use a 8"x8"x X
gutter and sometimes even off set that from the wall, l have had AHJ not
want to see mixed cables LVDC and AC in the same conduit so pass thro
Does the utility allow line side tie in and then you should not need to be
concerned about the 100 amp main as long as you have the wire size correct.
Many utilities are not allowing line side tap however.
Fun times
On Tue, Aug 8, 2023, 8:11 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wr
Wrenches
I'm sure you did all your due diligence on this location, wind rated output
is generally at 25 mph and needs 5 to 7 just to produce a watt. The math is
a cube root calculation. Small wind never really produced what people
expected. You also need to be higher than anything around the unit a
Dana, wrenches
Grunfus makes 120 vac booster pumps, MX Series as l recall they are a
variable speed tech
Fun times
On Sun, Aug 20, 2023, 9:56 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hey all you wise ones!
>
>
>
> I am looking for a recommendation on a 1/2HP ECM
Mick, Wrenches
You may have dodged a bullet with fronius, personally l have not had a good
experience with them, yes going back to the beginning with the IG's, put
the word out for SMA -41's they are not easy to get but are programable.
Just have to ask is there a particular reason why you are goin
Jeremy, wrenches
It's been some time since as they don't pencil very well, where are you
seeing the leakage, case top or elsewhere
Fun times
On Tue, Aug 29, 2023, 6:53 AM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> If anyone has had issues with the Iron Edison l
> Solar Installation / Design
> All Solar, Inc.
> 1453 M St.
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
>
> On Aug 29, 2023, at 10:30, Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
&g
I must agree with Ray, that inverter was never intended to run the slew of
electronics we have now. There are gadgets out on the market that may do
what you want but the reliability is in question. Does this site have a
genny? Using the that may get you past the issue but not solving the
problem.
Jay, wrenches
ASCO makes multiple ATS controls that can manage delays latching up and for
cool down. Most of the gensets have are programmed cool down after relay
opens so its not an issue. Generally on start up the genny connects as soon
as it's voltage and freq are within range.
fun times
On
Jason, Wrenches
I am familiar with Franklin and when I asked them about the battery they
had all the answers but when I asked about the AC coupled inverter inside,
mainly who made it is it field serviceable I got deer in the headlights and
a few weeks later I asked them the same thing and again no
William, Wrenches
Yes I do and it does require some basic electronics to make it work
correctly, you will need to remove the ttemp sender and make a
resistor pack to simulate the 77 degree reading otherwise it will not
charge properly, for the first one I used a breadboard to set the temp for
what
ation). One weakness of the
> ext BMS setting is that it won't fall back on Voltage settings if battery
> communication goes down, but this is a weakness throughout closed loop
> communication for many manufacturers.
>
> Let us know if there is a Fortress to SMA communication so
gt; <%3cre-wrenc...@lists.re-wrenches.org>
> *Cc:* Kirk Herander > <%3Ckirkh@vermont.solar>
> *Subject:* Re: [RE-wrenches] Sunny Island/Fortress E-vault
>
> Jerry,
>
> Who is the maker of the Blue Planet/Outback SOC box interface you mention?
>
> On Sat, S
We had wind lift issues so that will effect your installation. I have used
the current Nuance product and prior to that the same manufacturer under a
different name. Its more than just driving the rods down we had to do a
pull out test. We used hydrolic drivers attacked to the rack due to the
neces
Chris, wrenches
I have a few off grid or very close to off grid, I run well pumps, booster
pumps, septic system pumps, no issues
Fun times
On Wed, Oct 11, 2023, 7:12 AM frenergy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
>
> I'm looking for opinions and/or real world experience o
Wrenches
I have always used 50 miles per hr as this works well, sure the 3600 rpm
unit runs faster but 2000 hrs is 10 miles and unless you have a prime
mover that's about right. I see many with well over 10,000 hrs. Had one
last week do 1000 hrs in a month.
On Tue, Oct 24, 2023, 4:50 AM Dana O