inverters are likely to have current on the
neutral.
Peter, since it sounds like you have battery backup in your example it
sounds like you will need to count the neutrals between your inverter(s)
and critical loads as current carrying.
Best,
August
*From:* August Goers [mailto:aug
Hi Wrenches,
We have a particular plan checker who wants us to provide a *lockable* AC
disconnect for our inverter output circuit. His particular issue is that he
wants the locking mechanism to be installed and on site. Here is a little
NEC background info:
2014 NEC 705.22 Disconnect Device
pr 28, 2016, at 5:58 PM, jay wrote:
HI August,
I guess my question is.
Are they asking for a lockout AC disconnect on a AC circuit IE from the AC
panel?
or
are they asking for a lockout from the inverter AC at the inverter?
thanks
jay
peltz power
On Apr 28, 2016, at 3:11 PM, August
Hi Bill,
It sounds like you’re talking about a purlin type setup – 4’ sounds a
little far apart but I guess that’s what you have to deal with. If you have
a corrugated metal roof, we’ve used S-5 CurruBrackets screwed through the
metal and into the purlins and then either run the solar rail up an
ket. The name of it escapes me at the moment. Maybe FixT?
We are attaching to purlins which are 2"x6". I wouldn't think 1"x anything
would provide enough pull-out?
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
On Apr 29, 2016, at 9:09 AM, August Goers wrote:
Hi Bill,
feedback/good ideas.
Bill
Feather River Solar Electric
On 4/29/2016 3:28 PM, August Goers wrote:
Benn,
We’ve done it several ways including putting four 14 x 1.5” TYPE 17 screws
per attachment point through the metal and into the 1” x wood purlin. The
key is that the load path all the
I don’t know about other parts of the country.
If we have a self contained revenue meter – ie the type that cuts off power
to the building when it is pulled, then we just pull it for any type of
supply side connection or service upgrade. Sometimes we have to cut the
utility locking mechanism (we
Hi Wrenches,
We have a 125 A meter/main combo with space for up to 6 breakers (or three
two-pole breakers). Here is a Google photos link:
https://goo.gl/photos/kftDerEESg3giLrB9
The configuration is such that the busing is unprotected and connected
directly to the utility feeds through the
panel since the connection would qualify as a supply
side connection. However, I’m still curious about main breaker limitations
for these types of panels.
Best, August
*From:* August Goers [mailto:aug...@luminalt.com]
*Sent:* Wednesday, May 25, 2016 2:39 PM
*To:* 'RE-wrenches'
*Subje
All –
Just to cheer you up, this reminds me of client of ours who had 12/3 NM
Romex run between the utility service-drop conductors and weatherhead:
https://goo.gl/photos/m5kDypbXmyPSftnU7
This was a 200 A service and the client had been running his entire house
this way for years!
I wo
Hi Adam,
Check out “NEC 240.24(D) Not in Vicinity of Easily Ignitible Material.
Overcurrent devices shall not be located in the vicinity of easily
ignitable material, such as in clothes closets.”
-August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
B
Hi Dave,
We’re used Midnite’s battery enclosures with good success:
http://www.midnitesolar.com/products.php?productCat_ID=12&productCat_ID=12&productCatName=Battery
See the MNBE-CL16
Best,
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
0.318.7646
On Thu, Feb 7, 2013 at 10:44 AM, August Goers wrote:
Hi Wrenches,
I imagine that all of us working in rooftop PV have put some good hard
thought on the best way to get the modules up to the roof. There are
various lifts on the market, you can hoist them with ropes manually, or
walk t
Kirk,
It sounds like you might have a bonafide ground fault somewhere, possibly
at a location other than the module lead connections. I’ve seen current
leakage cause all kinds of strange corrosion problems. Maybe there is a
pinched or cracked module lead or homerun? It might even be possible tha
Hi Jason,
The mandatory switch to a TOU rate along with NEM 2.0 forces all of us
working with grid tied systems in CA to thoroughly rethink our game plan!
We have been using Energy Toolbase (as Mac mentioned) to model proposals to
accurately estimate post-solar bills under one of these new rates
? Please enlighten me.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 6/27/2016 6:57 AM, August Goers wrote:
Hi Jason,
The mandatory switch to a TOU rate along with NEM 2.0 forces all of u
Dan,
I went through what sounds like a similar situation with a XW+ recently.
Ours had the Schneider charge controllers, not Outback, so I’m not sure how
the two would interface in your situation.
You should be able to update firmware through the SCP, call Schneider
support for help. You basi
:* August Goers [mailto:aug...@luminalt.com]
*Sent:* Tuesday, July 19, 2016 6:43 AM
*To:* RE-wrenches
*Subject:* RE: [RE-wrenches] Conext XW+ always feeding critical loads
subpanel from battery bank
Dan,
I went through what sounds like a similar situation with a XW+ recently.
Ours had the
Hi Bruce,
We haven't run into multiple jurisdictions in the Bay using the same
application forms, although there is a slow convergence of similarities in
what jurisdictions are requiring. More and more jurisdictions are allowing
us to email in plans, however.
I believe Grid Alternatives is a CALS
This topic came up on the list previously. Since isolated transformer based
inverters are going the way of the dodo, the only reasonable inverter
upgrade choice is to replace old inverters with new transformerless models.
As was previously pointed out here, these modern inverters have much more
rob
Jay,
Current NEM 1.0 customers are not required to go TOU. NEM 2.0 will require
mandatory TOU.
E-6 is closed for new applicants - if your client is already on E-6, I
highly suggest that they stay on it as it is an excellent solar rate unless
they have low afternoon production or very high afterno
Glen,
It’s interesting you mention that you’re having AFCI issues with new TL
inverters and old modules. We are too. We have a particular system with BP
modules where we’re trying to figure out if we have a warranty claim
situation. We’ve cleaned up all the DC-side wiring and still the Sunny Boy
*jay
*Sent:* Friday, July 22, 2016 7:32 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Replacing grounded inverters
Oh boy.
Which BP models.
I mean those things have had lots of trouble.
jay
peltz power
On Jul 22, 2016, at 8:23 AM, August Goers wrote:
Glen,
It’s interesting you
Hi Jason,
We’re in a territory where we can’t run Romex (NM) directly into Soladecks
because of the wet location issue. I actually think inspectors are easing
up on enforcing this particular code grey area, but nonetheless we haven’t
run NM directly into Soladecks. I imagine that using a regular
Here are a couple of products that come to mind:
http://www.ecofastensolar.com/store/pc/viewPrd.asp?idproduct=4&idcategory=
2#.V5jb0TsrJaQ
http://www.anchorp.com/ (I believe IronRidge resells these as well)
-August
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.r
Bill,
I don't know about Samlex. We have a small offgrid system with an Outback
GFX1424 1.4 kW inverter and FM80-150VDC charge controller. There were some
issues early on with incompatible LED dimmer switches that apparently fried
the Outback inverter board, so that was replaced under warranty.
Hi James,
Great topic! Minimizing roof wear and tear during installation is a big
deal. We have Yellow Spaghetti mat (
http://www.bestmaterials.com/PDF_Files/yellow-spaghetti-datasheet.pdf) and
carpet scraps. Each has pros and cons. Spaghetti mat is durable and we use
it over and over. It does g
Hopefully manufacturers will steer away from supplying fine stranded wires
with their trunk cables – it’s been a joke trying to fine the proper listed
reasonably priced parts to make these connections. I bet that a huge
percentage of the installs out there are not meeting the listing for fine
stran
Hi Stephen,
My most recent experience has been with SMA Tripower and Fronius Symo
inverters. Previously, we installed dozens of Power-One (ABB) PVI 10.0 and
12.0 inverters in the < 2015 time period. Although I’ve heard lots of bad
stories about those inverters, ours have been quite reliable over
John,
I’m assuming that you’ve got a mix of household voltages (120 or 240 volts)
and low voltage cat-5 cable. You can’t do that, here is the code:
*NEC 300.3(C)(1) Conductors of Different Systems. 1000 Volts, Nominal, or
Less.* Conductors of ac and dc circuits, rated 1000 volts, nominal, or
whole lot of benefit to ballast that I can think of.
Is anyone on this list successfully installing small ballast systems?
Best,
August
August Goers
Luminalt Energy Corporation
m: 415.559.1525
o:415.641.4000
aug...@luminalt.com
*From:* RE-wrenches [mailto:re-wrenches-boun
Hi Daryl,
You might check out S-5 VersaBrackets and RibBrackets:
http://www.s-5.com/clamps/index_71.cfm
http://www.s-5.com/clamps/ribbracket/index_5336.cfm
-August
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of penobscotso...@midmain
?
Best,
August
August Goers
Luminalt Energy Corporation
m: 415.559.1525
o:415.641.4000
aug...@luminalt.com
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
trings is leading to false arc fault trips.
>
> Matt
>
>
> On Mon, August 29, 2016 3:42 pm, August Goers wrote:
>> Hi Wrenches,
>>
>>
>>
>>
>> I’m preparing for 2014 NEC 690.12 Rapid Shutdown to hit in California
>> January 2017. Spec
I checked the math and it indeed seems like a rounding issue – 20,000 W /
480 V / √3 = 24.05626122 A
I wonder if the SMA tech support agent that Brian spoke with was just
reading the manual when they said it was 24.1 A. Regardless, it seems like
we would need to rely on the manufacturer to clari
Are those wire nuts listed for wet locations? Most ideal outdoor (damp/wet)
rated wire nuts are blue or grey in my experience.
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Benn Kilburn
*Sent:* Tuesday, September 06, 2016 12:02 PM
*To:*
ction/transition boxes.
Jason Szumlanski
On Tue, Sep 6, 2016 at 3:19 PM, August Goers wrote:
Are those wire nuts listed for wet locations? Most ideal outdoor (damp/wet)
rated wire nuts are blue or grey in my experience.
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches
, August Goers wrote:
We’re using ideal/Buchanan splice cap crimp connectors as I’ve posted here
a couple of times:
http://www.idealind.com/ideal-electrical/us/en/products/wire-termination/60-crimp-connectors/copper-splice-cap-crimp-connectors.aspx
We really like these in nearly every way. I just
Definitely check polarity on each string. Could be positives and negatives
are mixed up and the wire colors are adding to the confusion.
August
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Roy Rakobitsch
*Sent:* Wednesday, September 07, 2016 3:35 PM
Certainly seems like a stumper so far! I'd still check voltage and
polarity with the strings through the conduit but not landed in the
inverter. We've seen all kinds of mistakes where the negatives were
mixed-up between strings, etc, causing strange behavior. Voltages can test
fine when landed in i
Ray,
I’m intrigued by this. We’ve always gone off NEC 300.3(B):
(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
Here’s a pic of an M210:
[image: burned enphase m210.jpg]
I guess a picture is worth a thousand words.
August
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *frank -bz products
*Sent:* Wednesday, September 14, 2016 12:25 PM
*To:* RE-wrenches
*Subj
My gut is that MC4 can’t handle the kind of current that you need for #6
wire. Why such large PV wire?
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Corey Shalanski
*Sent:* Thursday, October 06, 2016 3:23 PM
*To:* RE-wrenches@lists.re-w
We run PVC underground but typically transition to RMC starting at the 90
bend underground, up out of the ground, and to a box or conduit body where
we then transition to EMT.
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *AE Solar
*Sent
Dave,
It is particularly interesting that you have two inverters with
intermittent arc faults. I’ve been following this thread, and agree that
looking for noise on the AC side makes sense. Definitely update firmware
too!
That said, I thought I’d share a recent arc-fault story to this list. We
I was at Home Depot a week or so ago and a sales rep was pointing me to
DeWalts new 60v system!
http://www.dewalt.com/products/power-tools/shop-by-cordless-platform/60v-120v
Luckily, it is backwards compatible with the 20v stuff. Our crews are still
using the DeWalt 18v system but sooner or l
Hi Adam –
Can you elaborate a bit on what you are trying to accomplish and perhaps
give a description of the single line setup?
August
Luminalt
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *AE Solar
*Sent:* Tuesday, November 29, 2016 7:15 PM
*To:* R
Hi Adam,
Most load center panels list backfed breaker requirements on the inside of
the cover or inside the can. Some panels do no require breaker hold down
kits at all, even when backfeeding as a main breaker.
As you mention below, utility-interactive inverter breakers don’t need to
be fast
Hi Wrenches,
We are adopting the 2014 NEC in just a few weeks and will be installing NEC
690.12 rapid shutdown compliant systems for all permits pulled on or after
Jan 1 2017. I thought I’d take a quick poll to see what equipment you are
all planning on using to comply with rapid shutdown for yo
Hi Mark,
The current issue of IAEI magazine has an article writing by Bill Brooks
called "Hot Topics for PV System Installations." In the article, he
directly addresses 2014 NEC 690.47(D).
Unfortunately I don't see this article posted online, but you might want
to check it out if you can find it.
I don’t know if this will meet your goals, but we’ve been using Sunmodo’s
deck mount with good results:
*K10068-020 EZ Roof Mount Kit w/ L-Foot, Clear, Decking*
http://sunmodo.com/product/ez-roof-mount-kit-w-l-foot/
-August
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrench
We have a couple of Fluke 381 meters. I recommend them although battery life
has been a problem. Now we always keep spare batteries in the case.
I like having the iFlex option for measuring amperage where the standard
clamp jaws can't reach. The removable display is nice but not a must have
for me
Larry –
My immediate thought is that you would need a listed grid tied inverter
designed for the purpose of connecting to this type of battery and
inverting to the grid. A regular PV inverter won’t cut it since it is
designed to MPT PV modules.
The SolarEdge StorEdge product sounds like the c
, at 1:04 PM, August Goers wrote:
Larry –
My immediate thought is that you would need a listed grid tied inverter
designed for the purpose of connecting to this type of battery and
inverting to the grid. A regular PV inverter won’t cut it since it is
designed to MPT PV modules.
The SolarEdge
fitting.
August
August Goers
Principal
Luminalt
m: 415.559.1525
o: 415.640.4000
aug...@luminalt.com
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Kirk Herander
*Sent:* Tuesday, March 07, 2017 10:58 AM
*To:* 'RE-wrenches'
*Subject
All –
Yea, it’s amazing how much buzz Tesla was able to generate with their
Powerwall without even having a product ready for sale. I’ve been keeping
track of these next generation lithium-ion batteries so that we can keep up
with the demand of all the tech savvy early adopters here in the Bay A
Strange one. I would be surprised if the PV system has anything to do with
this. We’ve experienced strange electrical intermittent problems and they
have almost always been related to grounding or neutral problems. I realize
that two different electricians have checked out the site, but maybe they
Hi Eric,
Regarding the supply side connection, check out this article:
http://iaeimagazine.org/magazine/2013/11/16/supply-side-pv-connections-a-closer-look/
Check out 2014 NEC 230.50 – I don’t think NM is allowed. In our neck of the
woods we need to use RMC or IMC.
Secondly, I’d recommend
Hi Chris,
I’ve contacted Ideal about the suitability for their copper crimp
connectors to be used in outdoor locations in approved junction boxes.
Their response was that they are listed to UL 486C and are designed to be
used in approved outdoor boxes. I’ll forward the email to you off list.
As a related note, the 2014 NEC has an addition that allows field-installed
drainage holes in junction boxes:
We’ve found that installing drain or weep holes is a very good idea to keep
water from accumulating in outdoor boxes and conduit bodies.
August
*From:* August Goers
Hi William,
Check out NEC 314.16(C)(2):
I don’t know per se about putting fuses in conduit bodies, but the code
allows for some limited splices, taps, or devices in conduit bodies.
August
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *William Mi
We have done many high-leg delta installations with both single phase and
three phase inverters here in the Bay Area.
Besides the normal stinger-leg type issues of trying to install a single
phase 120 volt load across the high leg, I’m not aware of any particular
problems. Certainly we see many
transformer manufacturer, seems to hit the nail on the head:
https://ctlsys.com/support/inverter-power-factor/
😊
August
Luminalt
*From:* August Goers [mailto:aug...@luminalt.com]
*Sent:* Monday, June 12, 2017 12:37 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Ginlong inverter current
Hi Wrenches, especially those of you who work on off-grid projects,
We have an upcoming off-grid project where we will be powering a storage
container with electronics in it. The loads are mostly 120 volt but there
is a 240 volt heat pump that might occasionally run. We’re AC coupling the
Sunny
:* Thursday, June 15, 2017 12:03 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Generator choice for Sunny Island
Sho you want diesel, propane or natgas?
Nathan is more reliable as it does not require a refuel.
On Jun 15, 2017 12:02, "August Goers" wrote:
Hi Wrenches, especiall
1227
Greenfield, MA 01302-1227 USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com
Original Message Below
[RE-wrenches] Generator choice for Sunny Island
August Goers august at luminalt.com
Thu Jun 15 09:02:41 PDT 2017
Hi Wrenches, especially those of you who work on of
Hi Jay -
We don't do a whole lot of tile, but when we do we've switched to using a
tile replacement mount product. Quickmount and EcoFasten both make similar
products:
http://www.quickmountpv.com/downloads/datasheet/QMPV-datasheet-QMTRM-TileReplacement-web.pdf
http://www.ecofastensolar.com/store
issues and
stay away from self-waterproofing tile roofs that are older than 10 years or
that show signs that they weren't installed properly in the first place.
August
-Original Message-
From: August Goers [mailto:aug...@luminalt.com]
Sent: Thursday, June 22, 2017 8:07 AM
To: RE-wrench
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
] *On Behalf Of *August Goers
*Sent:* June-16-17 7:22 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Generator choice for Sunny Island
Thanks for the good feedback folks!
We are using a Sunny Island setup because
27;ll be up and running next week and I'll keep you posted.
http://www.kohlergenerators.com/home-generators/products/14RESA
-August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
m: 415.559.1525
www.luminalt.com
On Fri, Jun 23, 2017 at 3:46 PM, Dave Angelini Off
The 14RESA unit we have has an integrated battery charger. We just need to
wire a 15 A circuit from our backup panel to the terminals to keep the
starter battery charged. I confirmed that the warranty is 18 months or 1000
hours of operation for offgrid use.
August
*August Goers*
Luminalt Energy
ldn't find any literature from US battery
on recommendations for their AGM.
August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
m: 415.559.1525
www.luminalt.com
On Mon, Jul 24, 2017 at 5:36 AM, Drake wrote:
> Are you getting a good taper charge with this system?
27;ve
been installing Sunny Islands in grid tied battery backup applications
(with AGM batteries) for over 10 years now and they have been very solid.
August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
m: 415.559.1525
www.luminalt.com
On Tue, Jul 25, 2017 at 3:16 AM, Drake
lieve both a Chem Link M1 and Geocel 4500 can be used with primed TPO,
but there may be more TPO-specific sealants available.
August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
www.luminalt.com
On Wed, Aug 30, 2017 at 11:00 PM, William Miller
wrote:
> Friends:
>
>
ugust
*August Goers*
Luminalt
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http:/
ot;magic code " and walk me through
>> the programming. Once the Sunny Boy was reset to operate on the lower hertz
>> range everything worked great. You may have a similar situation, not sure
>> if the ABB folks will help with the hertz adjustment but you should give it
>>
rstand the diagram correctly on the spec sheet, it
looks like SMA is going the same route as Tesla where there will be a sort
of automatic transfer switch (aka the Gateway with the Powerwall) at the
hub of the system.
Best,
August
*August Goers*
Luminalt Energy C
Hi Sam - Yes, I believe SMA is planning on being compatible withe LG Chem
battery. However, I'm referring to the transfer switch unit highlighted
here in yellow, not the battery:
[image: Inline image 1]
*August Goers*
On Tue, Oct 3, 2017 at 2:48 PM, Sam Haraldson
wrote:
>
> Does
eutility/electrictransmission/handbook/060559.pdf
-August
*August Goers*
On Tue, Oct 3, 2017 at 7:25 PM, Jerry Shafer
wrote:
> Jerry
> Historically the utilities require a bladed disco, we had one on a military
> base which required a breaker by the base but we also were requir
meant to only include PV source and PV output circuits:
[image: Inline image 1]
[image: Inline image 2]
Best,
August
*August Goers*
Luminalt Energy Corporation
o: 415.641.4000
www.luminalt.com
___
List sponsored by Redwood Alliance
List Address: RE
Hi Chad -
We've been using Solar Census which has some very nice features for sales
reps. It is fast and easy to use - a layout can typically be created in
about 15 minutes. It uses LIDAR data to calculate the pitch of the roof and
estimate shade and we've found it to be generally quite accurate.
Chris - I agree with Carl that aluminum "cut and roll" jacketing is the
only way to go for longevity. It is a pain to install but once it's done it
will last the duration of the system. There is a video on this website
showing the idea:
http://www.buyinsulationproductstore.com/aluminum-jacket-for-
Hi Wrenches,
Please see question below forwarded from one of my fellow engineers.
Thanks, August
*From:* Eric Schoonbaert [mailto:e...@luminalt.com]
*Sent:* Monday, May 07, 2012 9:38 AM
*To:* August Goers
*Subject:* 120% Rule
The 120% rule, and how it is applied to panel board bus size
ission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!"
~William McDonough
On Mon, May 7, 2012 at 10:55 AM, August Goers wrote:
Hi Wrenche
type
busbars) seems to be more prevalent on the common trip models. Anyone a
breaker guru who can explain why one might one or the other?
Thanks,
August
August Goers
Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
o: 415.641.4000
aug...@luminal
Jeff,
Yea, sounds like a pain. We've been through this before with several high
profile projects in the Bay Area. Luckily, we have a lawyer on staff and
have gone through the waiver process in order to obtain marketing approval.
It might be possible to obtain a waiver that blankets the future us
Hi All Wind Wrenches,
We have 5 turbines recently installed in the Golden Gate National park
land in San Francisco. They are small 1 kW vertical axis units - I was not
happy about installing vertical axis but that was what the client wanted.
The good news is that each turbine is being monitored fo
(and installers) to see.
Thank you,
Jason Lerner
Waldron Power and Light Co.
On Jun 22, 2012, at 8:01 AM, August Goers wrote:
> Hi All Wind Wrenches,
>
> We have 5 turbines recently installed in the Golden Gate National park
> land in San Francisco. They are small 1 kW vertical axi
Hi Eric,
We've used TTi, EcoFasten, and Quick Mount. I like Quick Mount the best but
they are a bit pricy so we've been using Eco Fasten for the majority of our
work over the last year. If anything, I've found that TTi requires more
labor and is more likely to require shingle cutting plus I'm gu
All -
We attempted a couple of jobs with the S5! kit and no rails and lining
everything up was tough. Pro Solar rail directly to the S5! clamps works
great or Unirac with L feet even gives more installation flexibility.
Sounds like almost all of the responses are along these same lines.
-A
Wrenches,
I'm still on the hunt for a good label supplier or method of making them
ourselves. We install several projects each week and the label expense is
not insignificant. We're currently using a mix of the Tyco labels, custom
engraved labels, custom reflective labels required by some fire
j
William,
You might try calling Enphase again. I was discussing a similar issue with
them recently and they said that they have a noise filter option for
handling noisy lines. As with all tech support, some representatives are
better than others.
-August
August Goers
Luminalt Energy
galvanized nipple to
corrode so quickly. I wonder if there is a grounding issue with the tank or
maybe it's just the nature of galvanized fittings.
Best,
August
August Goers
Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
m: 415.559.1525
o: 41
Hi Wrenches,
Do any of you know the reason why we might use an independent trip versus a
common trip two pole breaker for a solar inverter? My understanding is that
the independent trip will only trip the individual line effected by the
overcurrent condition compared to the common trip which wil
William,
Good points. Keep in mind that both of these breakers have handle ties
(both are two pole), it's just that one can trip independently and the
other forces both to trip. What is the correct solution for 240 V solar
inverters? It seems like common trip is the best way to go but I've not
bee
I'm looking forward to checking out the SMA Smartformer. We're sending one
of our guys to SMA training later this month to learn more about it is
depth. Up to date, we used the Outback PSX-240 like the one found here to
120/240 step up:
http://www.altestore.com/store/Enclosures-Electrical-Safety/M
Hi David and Rebecca -
We're still in the 2008 code cycle here in California so AFCI hasn't become
an issue yet. I just listened to a webinar by SMA last week and I believe
that their AFCI Sunny Boys wont' be shipping for at least a couple of
months.
Rebecca, have you already installed this s
with detection since replacing PV arrays and other products may
be far more costly than installing an AFCI detector.
Bill.
*From:* re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *August Goers
*Sent:* Sunday, October 14, 2012 9:11
ple, is it okay to install our inverter breaker on either the
bottom or the top? If not, then our only resort is to either upgrade the
service or downsize the main breaker which isn't always possible to do.
Thanks for your thoughts in advance.
Best,
August
August Goers
to these either.
Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
On 10/15/2012 9:32 AM, August Goers wrote:
Hi Wrenches,
Here is yet another 120% rule question as it relates to center fed main
panels. 2011 NEC 705.12 deals with inverter point of connection and
705.12(D)(7