William,
There is this DLTL disco with 8 poles. I understand that the "street
price" is very possible less than the $579 4-pole you cited earli
s-boun...@lists.re-wrenches.org] On
Behalf Of b...@midnitesolar.com
Sent: Wednesday, October 08, 2014 11:46 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
William,
There is this DLTL disco with 8 poles. I understand that the "street price"
is very possible le
tp://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> ] *On Behalf Of *All Solar,
> Inc.
> *Sent:* Tuesday, October 07, 2014 4:28 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] TL inverter wi
Most DC rated disconnects are expensive and bulky, but I've had good
experiences with these ones from IMO:
http://www.imopc.com/products/1170081
A 4-pole (2 string) 800VDC 16A IP65 PV manual disconnect for about a
hundred bucks, that's pretty hard to beat.
_
Darren Anders
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *All Solar, Inc.
*Sent:* Tuesday, October 07, 2014 4:28 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
U
Re just completed a project for a group and they required a remote
disconnect on the roof, it is a combiner box with a contactor disconnect
that is roof mounted and 100 feet away, next to the inverters we have the
push button, I will get the brand and get it to you.
Jerry
On Mon, Oct 6, 2014 at 8:
re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
William,
Just to pile on here, if you're running 4 pairs of low-voltage dc for 400'
you may be better off just sticking the inverters right there at the array
and making the long run as 240Vac. #
sts.re-wrenches.org] On Behalf
Of All Solar, Inc.
Sent: Tuesday, October 07, 2014 4:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
Use the Midnite SOB series.
They have a 4 pole
Jeremy Rodriguez,
President
__
-3476 | Cell 443-277-6286
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *William Miller
*Sent:* Tuesday, October 07, 2014 12:01 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
Friends:
If only an SMA would work here. But DC vo
wrenches.org] On
>> Behalf Of William Miller
>> Sent: Tuesday, October 07, 2014 8:28 AM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
>>
>> August:
>>
>> I have been told I can't combine upstream of the inver
:
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of William Miller
Sent: Tuesday, October 07, 2014 12:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with
Ryan:
Thanks but the maximum is 3 circuits and we have 4.
william
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Ryan Mayfield
Sent: Tuesday, October 7, 2014 11:40 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
ectria inverters so I don’t know
> much about them.
>
> Best,
>
> August
> Luminalt
>
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of William Miller
> Sent: Tuesday, October 07, 2014 8:28 AM
> To: RE-wrenches
-wrenches.org] On Behalf
Of August Goers
Sent: Tuesday, October 07, 2014 11:30 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
William,
I see now from the separate post from Michael Kelly of Solectria that indeed
you cannot combine your two strings with this inverter. I
-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
August:
I have been told I can't combine upstream of the inverter.
William
Miller Solar
On Oct 7, 2014, at 8:03 AM, August Goers wrote:
William,
We have bumped into similar dilemmas when needing remote DC discon
if it still is.
Wm
[Gradient Cap_mini]
Lic 773985
millersolar.com<http://www.millersolar.com/>
805-438-5600
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Michael Kelly
Sent: Monday, October 06, 2014 3:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inv
August:
I have been told I can't combine upstream of the inverter.
William
Miller Solar
> On Oct 7, 2014, at 8:03 AM, August Goers wrote:
>
> William,
>
> We have bumped into similar dilemmas when needing remote DC disconnects with
> TL inverters. I believe the Solectria you are using has
Behalf Of *William Miller
*Sent:* Monday, October 06, 2014 9:01 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder
Friends:
If only an SMA would work here. But DC volts too low. We are using
Solectria PVI5200TLS.
We do not use PV wire. We transition to THWN-2 in
Friends:
If only an SMA would work here. But DC volts too low. We are using Solectria
PVI5200TLS.
We do not use PV wire. We transition to THWN-2 in conduit immediately.
William
Miller Solar
> On Oct 6, 2014, at 8:30 PM, Chris Mason wrote:
>
> I presumed SMA TL series.
>
>> On Mon, Oct 6
nly.
Bill
- Original Message -
From: William Miller
To: RE-wrenches
Sent: Monday, October 06, 2014 11:40 AM
Subject: [RE-wrenches] TL inverter with long DC Feeder
Wrenches:
We are getting up to speed on using transformer-less inverters. I have
advocated long for the
I presumed SMA TL series.
On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer
wrote:
> As i read the thread you say TL which TL SMA, AE ect. They have defferent
> dc input designs
> On Oct 6, 2014 12:21 PM, "jay peltz" wrote:
>
>> I do believe the outback and midnite combiners have a lock hole to
>>
As i read the thread you say TL which TL SMA, AE ect. They have defferent
dc input designs
On Oct 6, 2014 12:21 PM, "jay peltz" wrote:
> I do believe the outback and midnite combiners have a lock hole to prevent
> exactly your concern.
> unauthorized access.
>
> jay
>
> peltz power
> On Oct 6, 20
I don't understand the reference to Arc-Flash. Arc-flash ratings are
dependent on high current potential, typically above 700 amp short circuit
current. I don't think you can get an arc flash from a solar system as
solar is inherently current limited.
On Mon, Oct 6, 2014 at 2:40 PM, William Miller
lar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Michael Kelly
> *Sent:* Monday, October 06, 2014 3:10 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] TL inverte
com/> millersolar.com
805-438-5600
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Michael Kelly
Sent: Monday, October 06, 2014 3:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
Hi William,
I wanted to let you kno
I do believe the outback and midnite combiners have a lock hole to prevent
exactly your concern.
unauthorized access.
jay
peltz power
On Oct 6, 2014, at 11:40 AM, William Miller wrote:
> Wrenches:
>
> We are getting up to speed on using transformer-less inverters. I have
> advocated long fo
Any time we do a ground array, at the array location we combine the strings
and have a disconnect and it has come in handy to
On Oct 6, 2014 10:41 AM, "Mark Westbrock"
wrote:
> If you don't want to combine strings at the array, then I would use a
> Square D HU361 for each string. It is a lot of
renches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of William Miller
Sent: Monday, October 6, 2014 14:40
To: RE-wrenches
Subject: [RE-wrenches] TL inverter with long DC Feeder
Wrenches:
We are getting up to speed on using transformer-less inverters. I have
advocated long for the
If you don't want to combine strings at the array, then I would use a
Square D HU361 for each string. It is a lot of hardware, but not too
expensive and very straightforward for a lay person to shut off without
risk.
Cheers,
Mark
*Mark Westbrock*
Field Manager & Employee-Owner
NM EE98J Jou
How about the Midnite Solar four pole disconnect?
Can't remember the model number but recently installed one on a two string TL
input circuit. They are made for disconnecting both positive and negative.
Jeremy Rodriguez,
President
All Solar, Inc.
1463 M
Penrose Colorado 81240
719-372-3808 offi
William,
No suggestions for what might work, but how would you be sure that the
gardener (or other) would not attempt to open the fuseholders under load?
Perhaps the box could have a padlock on it and the key could be located at
the inverters where they could be shutdown prior to opening the
fuseho
Wrenches:
We are getting up to speed on using transformer-less inverters. I have
advocated long for the additional safety offered by these inverters but I am
realizing the trade-offs with the new technology: The implementation gets
more complicated with the requirement for PV wire, OCPD and d