William,

What is your string configuration?  The SMA TL inverters have a very low 
operating voltage window, going down to 125 Vdc, but you still have the issue 
of the disconnect.
[cid:image001.png@01CFE248.3F9A1920]

Have you looked at ABB’s (PowerOne) TL inverters: 
http://www.abb.us/product/us/9AAC179447.aspx?country=US?  They can be 
programmed to operate down to 90 Vdc, and they give you the ability to combine 
upstream and have the 2 MPPT’s operate as one, allowing you to combine outside 
of the inverter and bring a single set of PV output conductors to the 
inverter’s DC disconnect:

Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Tuesday, October 07, 2014 12:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder

Friends:

If only an SMA would work here. But DC volts too low. We are using Solectria 
PVI5200TLS.

We do not use PV wire. We transition to THWN-2 in conduit immediately.

William

Miller Solar

On Oct 6, 2014, at 8:30 PM, Chris Mason 
<cometenergysyst...@gmail.com<mailto:cometenergysyst...@gmail.com>> wrote:
I presumed SMA TL series.

On Mon, Oct 6, 2014 at 10:02 PM, Jerry Shafer 
<jerrysgarag...@gmail.com<mailto:jerrysgarag...@gmail.com>> wrote:

As i read the thread you say TL which TL SMA, AE ect. They have defferent dc 
input designs
On Oct 6, 2014 12:21 PM, "jay peltz" <j...@asis.com<mailto:j...@asis.com>> 
wrote:
I do believe the outback and midnite combiners have a lock hole to prevent 
exactly your concern.
unauthorized access.

jay

peltz power
On Oct 6, 2014, at 11:40 AM, William Miller wrote:


Wrenches:

We are getting up to speed on using transformer-less inverters.  I have 
advocated long for the additional safety offered by these inverters but I am 
realizing the trade-offs with the new technology:  The implementation gets more 
complicated with the requirement for PV wire, OCPD and disconnecting means for 
plus and minus and plus providing  Arc Flash rated equipment.

I am currently designing a system that will locate the PV about 400 feet from 
the residence.  The system will utilize 2 Solectria 5200 watt inverters at the 
residence.  I would like to provide disconnecting means for the 4 strings at 
the array, in case of any needed service or excavating.  Preferably I’d like 
the disconnecting means to be deployable by a lay person (i.e. the gardener).

Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I could 
install an Outback 8 circuit combiner with 8 touch-safe fuse holders.  The new 
combiners have had dead-fronts for a while now.  The gardener needs only to 
have a Philips screw driver to open this cover.  Any better ideas out there?

Thanks,

William


<image002.jpg>
Lic 773985
millersolar.com<http://www.millersolar.com/>
805-438-5600<tel:805-438-5600>

_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com<http://www.cometenergysystems.com>
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to