August:

I have been told I can't combine upstream of the inverter. 

William

Miller Solar

> On Oct 7, 2014, at 8:03 AM, August Goers <aug...@luminalt.com> wrote:
> 
> William,
>  
> We have bumped into similar dilemmas when needing remote DC disconnects with 
> TL inverters. I believe the Solectria you are using has two MPPTs? Ideally, 
> you would keep each string separate to benefit from the dual trackers – this 
> would mean four DC disconnects if you went with a standard product like a 
> Square D HU361RB. If you combine each of the two strings out at the array(s) 
> then you could get away with two disconnects, one for each inverter. Neither 
> option is ideal.
>  
> Best,
>  
> August
>  
> Luminalt
>  
> 