August:

Or an Outback or Midnite combiner without the combs, and a plaque warning to 
not disconnect under load. 

William

Miller Solar

> On Oct 7, 2014, at 11:30 AM, August Goers <aug...@luminalt.com> wrote:
> 
> William,
>  
> I see now from the separate post from Michael Kelly of Solectria that indeed 
> you cannot combine your two strings with this inverter. I think that leaves 
> you stuck with four separate disconnect switches unless someone on this list 
> knows of a four pole DC rated disconnect switch. Or, you’ll have to switch 
> inverters. I have never installed these Solectria inverters so I don’t know 
> much about them.
>  
> Best,
>  
> August
> Luminalt
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of William Miller
> Sent: Tuesday, October 07, 2014 8:28 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] TL inverter with long DC Feeder
>  
> August:
>  
> I have been told I can't combine upstream of the inverter. 
>  
> William
> 
> Miller Solar
> 