HI Drake,
Yes the issue with rebulk setting effects both AGS and manual.
Raise it way up and they won’t have any issues with it not charging
jay
> On Jan 9, 2021, at 8:02 AM, drake.chamber...@redwoodalliance.org wrote:
>
> Jay,
>
> The generator is manual start.
>
> Drake
>
> ---
>
>
Jay,
The generator is manual start.
Drake
---
On 2021-01-08 15:39, Jay wrote:
Is it ags start and is it starting on volts or %, or load?
On Jan 8, 2021, at 1:10 PM, Dave Angelini Offgrid Solar
wrote:
You said both, it will go into absorb for an hour only and it will
net go
into abso
Sent: Friday, January 8, 2021 10:34 AM
To: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Radian Charges 1 hour per calendar day
Hello Wrenches,
An off grid, Radian / Mate 3 system we set up some years back has worked
flawlessly. The cli
I don't know if this will help, but there is a setting under the AGS menus
called DC Generator.
There is DC Absrob timer and DC Absrob Votlage.
It's imperative that this is left alone if you are using an AC source, I
find many systems that are doing this the customer or installer freaked out
beca
RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
> <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of
> drake.chamber...@redwoodalliance.org
> <mailto:drake.chamber...@redwoodalliance.org>
> Sent: Friday, January 8, 2021 10:34 AM
> To: RE-wrench
t;> William
>>
>> PS: I would not assume a recently purchased system has the latest firmware.
>>
>> Wm
>>
>> Miller Solar
>> 17395 Oak Road, Atascadero, CA 93422
>> 805-438-5600
>> www.millersolar.com <http://www.millersolar.com/>
>&
[mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of
*Mick Abraham
*Sent:* Friday, January 8, 2021 12:46 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Radian Charges 1 hour per calendar day
Happy Friday, Mechanix~
Drake Chamberli
...@redwoodalliance.org
Sent: Friday, January 8, 2021 10:34 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Radian Charges 1 hour per calendar day
Hello Wrenches,
An off grid, Radian / Mate 3 system we set up some years back has worked
flawlessly. The client is now reporting that his system
Is it ags start and is it starting on volts or %, or load?
> On Jan 8, 2021, at 1:10 PM, Dave Angelini Offgrid Solar
> wrote:
>
> You said both, it will go into absorb for an hour only and it will net go
> into absorb. Which one please?
>
> Is there an AGS?
>
>
> Dave Angelini Offgrid Sola
Charges 1 hour per calendar day
Happy Friday, Mechanix~
Drake Chamberlin wrote about the Radian inverter that began running a "too
short" absorption interval after several years of normal operations. Drake
said the possible culprit is inverter firmware per Outback; I wish to add a
It will initially go into absorb, but only stay there for 1 hour. He has
tried to get it back in absorb by shutting the generator off.
He turns the generator back on, and it doesn't trigger an absorb charge.
The system will only take a charge from the generator for 1 hour each
calendar day.
timer.
-Original Message-
From: RE-wrenches On Behalf Of
drake.chamber...@redwoodalliance.org
Sent: Friday, January 8, 2021 10:34 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Radian Charges 1 hour per calendar day
Hello Wrenches,
An off grid, Radian / Mate 3 system we
Same page with you Jay, as usual...
Does the battery system go to absorb with solar still even if it is
cloudy? Maybe a bad battery? Tis the season!
Can the user go thru the set-points and make sure nothing has changed? Gen
sets can do weird surges that can corrupt settings.
If he has to leave
Happy Friday, Mechanix~
Drake Chamberlin wrote about the Radian inverter that began running a "too
short" absorption interval after several years of normal operations. Drake
said the possible culprit is inverter firmware per Outback; I wish to add a
data point & follow up questions:
I sold an Out
You said both, it will go into absorb for an hour only and it will net go
into absorb. Which one please?
Is there an AGS?
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On Fri, 08 Jan 2021 13:33:56 -0
Hello Wrenches,
An off grid, Radian / Mate 3 system we set up some years back has worked
flawlessly. The client is now reporting that his system will only go
into absorption charge for 1 hour per calendar day. The setting was
previously to absorb for 2 hours.
He has tried shutting off the ge