Dave,
I agree with Jerry that they might not make it til spring. If I
remember right, they are fairly easy to change. I have a customer with
over 8000 hours on his Ecogen 6. I still have many customers still running
the 6 but
With Multiple brush replacements. His secret of longevity was to
David,
The brushes are a variable wear item but when they go the unit is down, I
have seen brushes worn down to the ribbon in under 2000 hrs and some go
twice that and are still OK, As they wear rotor scuff can be an issue plus
as they wear the tension gets weaker and its more prone to build up on
I have a Generac EcoGen 6kW LP gas genset in my neighborhood that I’m
maintaining. It’s been in service for over 12 years and it has 3,200 hours on
it.
I see that I missed the recommended 2,500 hour service for changing the
alternator rotor brushes.
My question is how critical is it that the br
Solar 1
314 631 1094
-From: palumbo1...@gmail.com
To: "RE-wrenches"
Cc:
Sent: 09-Jan-2018 21:19:00 +0000
Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
Thank you all for your help. Ray gets the gold star long distance
diagnostics award as it
Thank you all for your help. Ray gets the gold star long distance diagnostics
award as it was simply a thin layer of ice underneath the air cleaner. I
cleared that out and it started right up and ran in good shape.
Dave
Sent from my iPhone
> On Jan 9, 2018, at 3:35 PM, Chris Mason wrote:
>
>
If the unit is still under warranty, have any Generac dealer run through
the diagnostics. The testing flow suggests rotor or stator problems, and
there is a proscribed testing flow that needs to be performed. If it is
determined to be a warranty issue, it will be fixed for you at no cost.
If it is
Dave,
I had undervoltage on an eco-gen when the programming accidentally got
changed to 240V when it is a 120V unit.
John B.
On Tue, Jan 9, 2018 at 5:13 AM, Darryl Thayer wrote:
> Hello David, I have had that problem on other generators.
> I have had similar problems not with an Eco gen but
Hello David, I have had that problem on other generators.
I have had similar problems not with an Eco gen but with a couple of other
propane generator models. The problem occurs during cold weather. The
problem was poor gas supply pressure and the problem was I could not
convince anyone that was t
ays
the first to go'.. Good Luck.
db
Dan Brown
Foxfire Energy Corp.
Renewable Energy Systems
(802)-483-2564
[1]www.Foxfire-Energy.com
NABCEP #092907-44
Original Message
Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
From: Ray <[2
-wrenches] GENERAC EcoGen 6kw problem
Check to see if it’s programming matches its wired and expected voltage output
configuration.
Sent from my iPhone
On Jan 8, 2018, at 6:13 PM, David Palumbo wrote:
I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
starts quickly
:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] GENERAC EcoGen 6kw problem
Check to see if it’s programming matches its wired and expected voltage output
configuration.
Sent from my iPhone
> On Jan 8, 2018, at 6:13 PM, David Palumbo wrote:
>
> I am troubleshooting a 6kw EcoG
Check to see if it’s programming matches its wired and expected voltage output
configuration.
Sent from my iPhone
> On Jan 8, 2018, at 6:13 PM, David Palumbo wrote:
>
> I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
> starts quickly
> • but immediately shuts down
I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
starts quickly
• but immediately shuts down with an “Under Voltage” shutdown alarm
• I can clear shutdown alarm and restart with same result. I tried this a few
times with same result. One of the start attempts included a