stions!
>
> Bruce Fiero-RMI
>
>
>
> *Willpower Electric LLC*
>
>
> Original Message
> Subject: Re: [RE-wrenches] Charging a HUP
> From:
> Date: Sun, February 09, 2014 12:04 pm
> To: "RE-wrenches"
>
> Yes Chris. I've got about 42 on one
capacitor bank to correct some of the power factor issues of the inverter/chargers so I can get more useable kw out of the genset.Thanks for your suggestions!Bruce Fiero-RMIWillpower Electric LLC
Original Message
Subject: Re: [RE-wrenches] Charging a HUP
From: <
Yes Chris. I've got about 42 on one leg and 35-37 on the other. The transformer keeps the legs balanced to within about 5 amps.Bruce
Original Message
Subject: Re: [RE-wrenches] Charging a HUP
From: Chris Mason <cometenergysyst...@gmail.com>
Date: Sun, February 09, 20
ker trips!
>
> Bruce
>
> Original Message ----
> Subject: Re: [RE-wrenches] Charging a HUP
> From: "Kevin Pegg"
> Date: Sun, February 09, 2014 9:39 am
> To: "RE-wrenches"
>
> "Has anybody scoped ac line to VFX's under full charg
e gen when I replace the breaker to avoid overheating when breaker trips!Bruce
Original Message
Subject: Re: [RE-wrenches] Charging a HUP
From: "Kevin Pegg" <kp...@energyalternatives.ca>
Date: Sun, February 09, 2014 9:39 am
To: "RE-wrenches" <
A 12KW generator can produce 250A at 48V, and the breaker should be 12KW
*125% or 62.5 amps.
You may have an unbalanced load, you probably can only put 6KW per leg of
the 240V feed.
On Sat, Feb 8, 2014 at 2:46 AM, wrote:
> Hi All,
>
> 3 VFX 3648
> 2 FM 80
> 6.5 kw solar
> 12 kw generator
> PSX
.
>
> Kevin
>
> -Original Message-
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of *
> br...@willpowerelect.com
> *Sent:* February 9, 2014 9:28 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches]
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of
br...@willpowerelect.com
Sent: February 9, 2014 9:28 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP
Roger the 136-272 charge amps, and the theoretical
the breaker, and a 5-6 kw charging load tripping the breaker...Bruce
Original Message ----
Subject: Re: [RE-wrenches] Charging a HUP
From: "RE Ellison" <reelli...@gmail.com>
Date: Sun, February 09, 2014 8:07 am
To: "'RE-wrenches'" <re-wrench
Hi Bob,
While I did see on this list earlier about batteries preferring to charge
slowly, some manufactures feel very differently.
In my experience the industrial type require a C10ish minimum charge rate, some
higher even.
The info was on the HUP website
jay
peltz power
On Feb 9, 2014, at
-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Sunday, February 09, 2014 9:38 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP
Hi guys,
The HUP manual specifies minimum charge rate of 136 amps, max at 272,
jay
peltz power
On Feb
akes sense in the morning
> when I reread it….
>
> Later,
> Bob
>
>
>
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
> br...@willpowerelect.com
> Sent: Sunday, February 09, 2014 1:29 AM
> T
To: RE-wrenches
Subject: Re: [RE-wrenches] Charging a HUP
Hi Larry,
I have an FNDC in the system. Manufacturer wanted 2 hour EQ before adding water
to the new battery. We got that and had SG between 1.260 and 1.275 on all 24
cells. Cells were very thirsty (shipped with electrolyte almost to
, and nervous about barely c/20 and a 12kw genset only giving me about 5.Bruce
Original Message
Subject: Re: [RE-wrenches] Charging a HUP
From: "Larry Crutcher, Starlight Solar Power Systems"
<la...@starlightsolar.com>
Date: Sat, February 08, 2014 11:50 a
Hi Bruce,
Please explain "feeding it properly". Charging any lead acid battery slowly
actually preserves battery life. As long as you are achieving the recommended
charge voltage (temperature compensated) for long enough time, and reaching
100% SoC regularly, you are caring for the battery.
At
Hi All,3 VFX 36482 FM 806.5 kw solar12 kw generatorPSX 240 on generator output and VFX stackingMate 3HUP 1690 ahSystem design considering 45 amp charge current from each VFX totaling 135 amps. (135 x ~55v = 7.42kw) Potential charge current from 2 arrays and FM 80's, 90 - 100 amps. On a good day, r
16 matches