Hi guys,

The HUP manual specifies minimum charge rate of 136 amps, max at 272,

jay
peltz power
On Feb 9, 2014, at 1:38 AM, RE Ellison wrote:

> Sounds like there is a need for a bigger generator, my gut tells me there is 
> almost enough (but not quite), with 12kw to almost max the chargers and 
> nothing left to feed the other loads.
> I have found that “on paper” and reality do not always mix well.
> Getting max theoretical charging capacity from solar and the generator at the 
> same time is sometimes a tough nut to crack, although batteries seem to 
> “like” the varying charge better than a steady max charge. That battery can 
> probably absorb 420 amps as the charging max using the usual 3 stage charging 
> we have with inverters, you’re not getting anywhere near enough to max them 
> with that generator. Powering down all the chargers 30% or so (or 1 inverter 
> totally) would help stop the breaker trips but slow the charging off the 
> generator. Then you just need to pray for lots of sun.
> Is the solar alone enough to power the loads in the normal day to day usage 
> in a best case situation, or is this a case of the generator has to run to 
> keep up?
>  
> Up here we have seen 1 sunny day in 3 weeks, we know about generator usage…..
>  
> I can’t speak on the HUP’s. I have never used them, but might they be 
> somewhat hard to charge?
>  
> Just some thoughts, but it’s 3 am and I hope it makes sense in the morning 
> when I reread it….
>  
> Later,
> Bob
>  
>  
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
> br...@willpowerelect.com
> Sent: Sunday, February 09, 2014 1:29 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Charging a HUP
>  
> Hi Larry,
>  
> I have an FNDC in the system. Manufacturer wanted 2 hour EQ before adding 
> water to the new battery. We got that and had SG between 1.260 and 1.275 on 
> all 24 cells. Cells were very thirsty (shipped with electrolyte almost to the 
> plates) and took 8.5 gallons between all cells. We aren't having much trouble 
> getting voltage back up but SG is below 1.23 (within .01 on cells tested). 
> Strategy at this point is to give a daily bulk and absorb and EQ every 3 or 4 
> days for extended times and monitor SG. Discontinue hard charging when SG 
> plateaus. I generally shoot for c/10 charge current, and nervous about barely 
> c/20 and a 12kw genset only giving me about 5.
>  
> Bruce
> -------- Original Message --------
> Subject: Re: [RE-wrenches] Charging a HUP
> From: "Larry Crutcher, Starlight Solar Power Systems"
> <la...@starlightsolar.com>
> Date: Sat, February 08, 2014 11:50 am
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> 
> Hi Bruce,
>  
> Please explain "feeding it properly". Charging any lead acid battery slowly 
> actually preserves battery life. As long as you are achieving the recommended 
> charge voltage (temperature compensated) for long enough time, and reaching 
> 100% SoC regularly, you are caring for the battery.
>  
> At 82kWh battery capacity and 6.5kW PV, the customer may have a hard time 
> getting to 100%. You did not mention, but I HOPE you have a battery capacity 
> meter in the system. It's mandatory if they want to care for the battery. 
> Since the customer has a small generator, they need to realize the 
> limitations and reduce their loads during generator time so you can use the 
> full output.
>  
> Larry
> 
> On Feb 7, 2014, at 11:46 PM, br...@willpowerelect.com wrote:
>  
> Hi All,
>  
> 3 VFX 3648
> 2 FM 80
> 6.5 kw solar
> 12 kw generator
> PSX 240 on generator output and VFX stacking
> Mate 3
> HUP 1690 ah
>  
> System design considering 45 amp charge current from each VFX totaling 135 
> amps. (135 x ~55v = 7.42kw)  Potential charge current from 2 arrays and FM 
> 80's, 90 - 100 amps. On a good day, reasonable to expect 200+ amps?
> Have not been able to exceed 90 amps for more than 30 minutes, with the 
> generator putting out about 9 kw before it's 70 amp 2pole breaker trips. L1 
> 42 amps, L2 37 amps. 5 amps neutral. Load banked to 12.3 kw (51 amps @ 240v) 
> resistive without breaker trip.
> I have had to dial back the maximum charge current in the Mate 3 to 12 amps 
> each on two of the inverters (L1 and L2) and 8 on inverter 3 to keep the 
> generator from tripping out when customer turns on the microwave or coffee 
> pot. In effect, 42 amps charge @ 240 v = 7.6 kw. At the battery, I'm only 
> seeing 80 amps of charge current. Running loads are typically less than 1 kw 
> but there has been a of construction going on with chop saws and compressors 
> creating annoying spikes that are easily handled by the inverters when the 
> generator is off.
> I don't want to kill this new battery by not feeding it properly! I would 
> have put in a larger generator, but the owner bought the 12 kw before 
> deciding on the new battery. I thought the 12 would be merely adequate, but 
> not so....
> Any suggestions?
>  
> Thanks!
>  
> Bruce Fiero-RMI
> 
> 
> <sigimg0.jpeg>
> 
> s.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to