Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-12 Thread Ray
I should also add to my post and others' comments, that SAE rated and welding cables are not NEC legal for building wiring.  That used to be a common bust by the AHJ, and as others have pointed out:  Cobra Xflex, Arctic, etc are all UL listed building cable. Its got to have something listed on

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-12 Thread Ray
Also, welding and automotive cables use totally different rating systems like SAE, that are much more liberal than NEC.  For instance, golf carts are traditionally wired with #6 battery cables, and can see a continuous draw of 125 A and surges to 200. We would never do that by NEC, but the cabl

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-12 Thread Dave Angelini Offgrid Solar
ug 11, 2020, at 10:34 PM, Glenn Burt wrote: Okay I have to ask, why wouldn't you want to stick to code compliant battery cabling? FROM: RE-wrenches ON BEHALF OF peter...@pobox.com [5] SENT: Tuesday, August 11, 2020 6:18 PM TO: RE-wrenches@lists.re-wrenches.org [6] SUBJECT: [RE-wre

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-12 Thread Tump
lists.re-wrenches.org>> On Behalf Of > peter...@pobox.com <mailto:peter...@pobox.com> > Sent: Tuesday, August 11, 2020 6:18 PM > To: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > Subject: [RE-wrenches] Ampacity Ratings for Diffe

[RE-wrenches] Ampacity ratings for different conductors

2020-08-12 Thread Hilton Dier
Peter, I’d recommend 2-0 copper for this. Overkill? Perhaps, but the battery cables are probably the cheapest vital part of the system. Anything you can do to make life a bit better for the batteries will pay off. A few extra bucks for cable is a lot cheaper than one warrantee site visit. Cobr

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-11 Thread Glenn Burt
Okay I have to ask, why wouldn’t you want to stick to code compliant battery cabling? From: RE-wrenches On Behalf Of peter...@pobox.com Sent: Tuesday, August 11, 2020 6:18 PM To: RE-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Ampacity Ratings for Different Conductors I have

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-11 Thread Kent Osterberg
Peter, The 210-amp rating is probably for a 105°C insulation temperature in free air. For comparison, #2 THHN (90°C) copper in free air is rated for 190 amps. Not sure that it makes sense to use a free-air rating in a small closed box.  For outside use a temperature de-rating for ambient temp

Re: [RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-11 Thread Dave Angelini Offgrid Solar
I would and do use a 2/0 battery cable for a 4KW inverter. Anchor is an excellent marine cable, but not a #2. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Tue, 11 Aug 2020 15:18:22 -070

[RE-wrenches] Ampacity Ratings for Different Conductors

2020-08-11 Thread peter...@pobox.com
I have been designing a off-grid system that can fit in an outside-accessible compartment with an approximate 24" square footprint and space above about 18" - 24". I am using two Battle Born LiFePO4 batteries rated at 24 V / 50 Ah, a Cotek pure sine wave inverter with