I have been designing a off-grid system that can fit in an outside-accessible compartment with an approximate 24" square footprint and space above about 18" - 24".

I am using two Battle Born LiFePO4 batteries rated at 24 V / 50 Ah, a Cotek pure sine wave inverter with an output power of 4,000 VA , a MorningStar TS-MPPT-60 charge controller, a Victron BMV-712 "coulomb counter" and a Battle Born surge limiter CL500.

The current limiter limits the current to 120 continuous, and 200 A for 30 sec.

I have been able to fit everything in and I am designing the cabling, and here is my problem.

I have one vendor that recommends Ancor brand Tinned Marine Grade Battery Cable. It is "resistant to salt water, battery acid, oil, gasoline, heat, abrasion and ultra-violet radiation. Exceeds UL 1426, ABYC and US Coast Guard Charter boat (CFR Title 46) standards. Highest quality ultra-flexible (Type 3) tinned copper stranding. Vinyl insulation. -50 deg-C to 105 deg-C." 2 AWG is composed of 665 ea 30 AWG stands.

The same vendor has "welding cable" with an EPDM insulation rated at 600 V, water/chemical/grease/abrasion resistant, -50 deg-C to 105 deg-C, "marine grade". Not UL listed. 624 ea 30 AWG strands.

Roughly comparable pricing.

They claim both 2 AWG cables are rated at 210 A. Not sure if this is continuous duty or whether I should derate this for what will be continuous duty.

This is new territory for me, and any help would be appreciated.

Peter T. Parrish, Ph.D.
President, California Solar Engineering


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to