Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-08 Thread James Jarvis via RE-wrenches
Why was ACLD discontinued? -James Jefferson Jarvis APRS World, LLC +1-507-454-2727 (Sent from my phone. My apologies for spelling errors and brevity.) On Sat, Oct 8, 2022, 12:35 PM Bradley Bassett via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > The ACLD was long ago discontinued.

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-08 Thread Bradley Bassett via RE-wrenches
The ACLD was long ago discontinued. The Morningstar relay driver would work fine. I think Magnum limited the size of the grid tie inverter to 90% of the Magnum inverter max power. So 3960W for a MS4448PAE. Brad On Sat, Oct 8, 2022 at 8:47 AM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-08 Thread Jay via RE-wrenches
Hi Drake I remembered that they make this product or they did. https://www.magnum-dimensions.com/sites/default/files/MagDocs/64-00062%20Rev%20A%20%28ACLD-40%29_web.pdf ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-w

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-07 Thread Dave Tedeyan via RE-wrenches
Hi Drake, Just to make sure I understand you correctly, I could tie in a new grid tie inverter on the load side of the Magnum inverter. Then when the grid is up, the power will be able to backfeed through the MMP175-30D panel to the AC input (which will get rewired to the grid). And when the grid i

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-07 Thread Drake Chamberlin via RE-wrenches
The grid tie inverter can sell through the Magnum relay. When the grid goes down, it will feed the batteries. Drake Chamberlin Athens Electric LLC Ohio Electrical Contractor's License 44810 CO Master Electrician's License 4526 NABCEP Certified PV Installation Professional --- On 2022-

[RE-wrenches] AC coupled grid tie only inverter

2022-10-07 Thread Dave Tedeyan via RE-wrenches
Hi All, I've got someone who wants to tie their off-grid system with a Magnum inverter (which I think is a 4024 PAE inverter) to the grid. Since the Magnum inverter cannot be grid tied, I was wondering if there is some kind of simple grid tie inverter that can be the grid interface, while keeping

Re: [RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread Chris Sparadeo via RE-wrenches
Hi William, Each Powerwall can accept 5 kW of continuous charge and 7 kW peak for 10 seconds. These values increase respectively with additional units (i.e. 10kW continuous for 2 units, 15kW for 3 etc). It’s my understanding that each unit can accept 7.6 kW of AC coupled PV. If PV is generating mo

Re: [RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread Marco Mangelsdorf via RE-wrenches
Max rating of the Gateway2 is 200A. Regarding a generator input, you're correct, there's no means that I'm aware of to integrate a backup generator with the Tesla equipment that would interact with the solar and storage. marco On Thu, Apr 28, 2022 at 5:45 PM William Miller via RE-wrenches < re-wr

[RE-wrenches] AC Coupled Tesla system

2022-04-28 Thread William Miller via RE-wrenches
Friends: I have two questions about AC coupling Tesla systems: 1. Are there limits on how much power can be AC coupled through a Tesla gateway? Does it depend on the quantity of power-walls connected? 2. I understand a Tesla system does not have a separate generator input so if a genera

Re: [RE-wrenches] AC-coupled storage

2018-05-24 Thread Dave Angelini Offgrid Solar
Blue Ion ? made in Hawaii ! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 > Aloha, > > > > Other than the Tesla Powerwall, does anyone know of any other AC-coupled > residential storage products curr

Re: [RE-wrenches] AC-coupled storage

2018-05-23 Thread Peter Giroux
- From: Marco Mangelsdorf To: 'RE-wrenches' Sent: Wednesday, May 23, 2018 5:54 PM Subject: [RE-wrenches] AC-coupled storage Aloha, Other than the Tesla Powerwall, does anyone know of any other AC-coupled residential storage products currently on the market? Thanks

Re: [RE-wrenches] AC-coupled storage

2018-05-23 Thread Glenn Burt
Sonnen eco series. GlennSent from my 'smart' phone so please excuse spelling and typographical errors. -- Original message--From: Marco MangelsdorfDate: Wed, May 23, 2018 6:28 PMTo: 'RE-wrenches';Cc: Subject:[RE-wrenches] AC-coupled storage Aloha,   Other than

[RE-wrenches] AC-coupled storage

2018-05-23 Thread Marco Mangelsdorf
Aloha, Other than the Tesla Powerwall, does anyone know of any other AC-coupled residential storage products currently on the market? Thanks, marco --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus ___

Re: [RE-wrenches] AC-coupled battery back-up

2017-12-17 Thread Dan Fink
Hi Marco; more below. Dan Fink Professor of Solar Energy Technology, Ecotech Institute IREC Certified Instructor™ for: ~ PV Installation Professional ~ Small Wind Installer Executive Director, Buckville Energy NABCEP Registered Continuing Education Providers™ 970.672.4342 On Sun, Dec 17, 2017 a

[RE-wrenches] AC-coupled battery back-up

2017-12-17 Thread Marco Mangelsdorf
Aloha all, Here in the State of Aloha we’re leading the way as far as being the first PV peeps to add AC-coupled storage to existing grid-tie NEM systems with the benefit to the homeowner being having back-up power if/when the grid goes down. During a grid outage the AC-coupled battery storage

Re: [RE-wrenches] AC Coupled Enphase

2017-08-30 Thread b...@midnitesolar.com
On 8/30/2017 5:54 AM, Drake wrote: Hi boB, Would there be any issues with delayed control of the microinverters? We do  plan to  use disconnects for maintenance. Thanks, Drake I highly doubt there would be enough delay to worry about anything regarding battery damage Even with Rul

Re: [RE-wrenches] AC Coupled Enphase

2017-08-30 Thread Drake
Hi boB, Would there be any issues with delayed control of the microinverters? We do plan to use disconnects for maintenance. Thanks, Drake At 06:27 PM 8/29/2017, you wrote: Content-Type: multipart/alternative; boundary="155C815B9802686293824DDD" Content-Language: en-US SSRs

Re: [RE-wrenches] AC Coupled Enphase

2017-08-29 Thread b...@midnitesolar.com
SSRs, especially AC SSRs made from thyrisotrs (scrs and/or triacs)  are "leaky" in general so when turned OFF, can cause a shock  Maybe not enough to kill you but maybe enough to make you fall off the roof ! I'm not sure why the disconnects aren't good enough which should already be i

Re: [RE-wrenches] AC Coupled Enphase

2017-08-29 Thread Dave Angelini Offgrid Solar
Probably a good idea to test that HBCO is set right, actually does shut down the inverter, and stays programmed correctly in a LBCO or complete drain of battery. Dave DrakeDave > The plan is to use N/C relays. As this is in a > backup system, N/O relays would need to spend > most of their lives e

Re: [RE-wrenches] AC Coupled Enphase

2017-08-29 Thread Drake
The plan is to use N/C relays. As this is in a backup system, N/O relays would need to spend most of their lives energized. The relays will not be able to receive any control power while the grid is up. If all else fails and the relays stay closed and overcharge the batteries, the high voltag

Re: [RE-wrenches] AC Coupled Enphase

2017-08-29 Thread Jason Szumlanski
My vote would still be to use two single pole relays as suggested previously to kill each leg. That way you build in redundancy and dropping either leg will do the trick. In fact, it sounds like this would be even better than a two pole relay for the redundancy reason. The other factor is whether

Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Nick Soleil
The one-pole relay will work for de-energizing any of the Enphase microinverters. Nick Soleil Field Application Engineer Enphase Energy Cell: 707-321-2937 On Aug 28, 2017, at 6:03 PM, Drake mailto:drake.chamber...@redwoodalliance.org>> wrote: Hi Nick, I should mention that the inverters bein

Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake
Hi Nick, I should mention that the inverters being AC coupled are M-250s, not the new IQ series. Would that make any difference? Thanks, Drake At 03:12 PM 8/28/2017, Drake wrote: Hi Nick, At 11:20 AM 8/28/2017, you wrote: Content-Language: en-US Content-Type: multipart/alternative;

Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake
Hi Nick, That is very good news. I just hit the wall trying to find 2 pole solid state N/C relays. I was trying to decide whether to go back to mechanical or buy double the amount of single pole relays. Thanks, Drake At 11:20 AM 8/28/2017, you wrote: Content-Language: en-US Content-Type:

Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Nick Soleil
You can use a one-pole relay. We show one-pole switching in our zero-export, self-consumption doc for PEL applications. Nick Soleil Field Application Engineer Enphase Energy Cell: 707-321-2937 On Aug 28, 2017, at 6:44 AM, Drake mailto:drake.chamber...@redwoodalliance.org>> wrote: Hello Wrenc

Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread James Jefferson Jarvis
On 8/28/2017 8:44 AM, Drake wrote: Alternatively, does anyone know of reasonably priced, 2 pole solid state relays? Just use two single pole SSRs. One for each leg. There are two pole SSR, but the price is not going to be bargain basement. -James Jefferson Jarvis APRS World, LLC +1-507-454-2

[RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake
Hello Wrenches, I am going to AC couple some Enphase inverters and found some really nice solid state, single pole relays to control them with. Enphase says I must use 2 pole relays for the control current even though the disconnects will turn off all power for maintenance. Enphase claims th

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread Ray Walters
Just reading up on Magnum's new AC load diversion controller. It looks like the best option at this point, it provides AC load diversion so you can use AC loads not DC resistors, and it communicates with the inverter, so the system has both 3 stage temp compensated battery charging, and has 2

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread Ray Walters
Hi Larry; I'm actually looking at the secondary DC array strategy you mentioned as well. It's all about those lower charge rates in the absorption and float stages. The DC array could be sized for a charge rate as low as C50 and probably have enough current to get the job done. Meanwhile En

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread jay
HI Drake, What sort of multi stage relay control are you using? jay peltz power > On Aug 21, 2015, at 5:27 AM, Drake > wrote: > > I'm considering an AC coupled system with Enphase that would shed inverters a > group at a time, ending up with one still charging until the set point is > reac

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread jay
A question about turning the AC on/off as means of primary on/off control for this AC coupling question. Some time ago I was told that most (all?) inverters don’t like having the AC switched on/off as a means of disconnect. If I understand correctly this causes the DC internal relay to have to

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread Drake
I'm considering an AC coupled system with Enphase that would shed inverters a group at a time, ending up with one still charging until the set point is reached. At 12:56 AM 8/21/2015, you wrote: Hi Folks; I've done more research on the whole AC coupled issue, and one flaw I found with both t

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread Starlight Solar Power Systems
Ray, I’m curious about what you mean by not doing a 3 stage charge. While PV charging in coupled mode (off grid), the battery will reach your absorption set point. Is this triggering the GT inverters to shut off or does the battery inverter absorb timer run at all? I would think the absorb time

Re: [RE-wrenches] AC Coupled with Generator

2015-08-21 Thread jerrysgarage01
;T 4G LTE smartphone Original message From: Ray Walters Date:08/20/2015 6:56 PM (GMT-10:00) To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled with Generator Hi Folks; I've done more research on the whole AC coupled issue, and one flaw I found with both the Sunny

Re: [RE-wrenches] AC Coupled with Generator

2015-08-20 Thread Ray Walters
Hi Folks; I've done more research on the whole AC coupled issue, and one flaw I found with both the Sunny Island and the Radian is that they can't really do a full 3 stage charge for the batteries in off grid mode. They detect that the batteries are full and disconnect the AC coupled GT invert

Re: [RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Jerry Shafer
Ray The Outback does not dump load it drops inverter string (s) instead Jerry On Mon, Aug 17, 2015 at 5:26 PM, Ray Walters wrote: > Yes, we're definitely planning a battery based inverter. The real trouble > is when the generator is charging, its AC power passes through to the loads > and hence

Re: [RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Mac Lewis
Hi Ray, With that size grid-tied system, you would want to use a battery based inverter(s) near the (6.7/0.8) 8000W range. The frequency shift of the Sunny Islands will work with kicking out the enphase inverters but you wouldn't get the same output ramping that it would offer if it was a Sunny B

Re: [RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Ray Walters
Yes, we're definitely planning a battery based inverter. The real trouble is when the generator is charging, its AC power passes through to the loads and hence to the Enphase inverters. Also I agree with the other poster about Outback being more cost effective. I just took a look at their Remo

Re: [RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Jerry Shafer
I cant see this working well without some battery based inverter Jerry On Aug 17, 2015 10:10 AM, "Ray Walters" wrote: > HI Esteemed Wrenches: > > I am consulting on a system I have never seen, that consists of a 6.7Kw > Enphase roof mounted system, and 2 backup generators. Each generator has > a

Re: [RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Peter Giroux
ASAE - Original Message - From: "Ray Walters" To: "RE-wrenches" Sent: Monday, August 17, 2015 4:10 PM Subject: [RE-wrenches] AC Coupled with Generator HI Esteemed Wrenches: I am consulting on a system I have never seen, that consists of a 6.7Kw Enphase roof m

[RE-wrenches] AC Coupled with Generator

2015-08-17 Thread Ray Walters
HI Esteemed Wrenches: I am consulting on a system I have never seen, that consists of a 6.7Kw Enphase roof mounted system, and 2 backup generators. Each generator has an automatic 200 amp transfer switch to back up its own 200 amp panel. Both 200 amp panels are fed by a 400 amp service from

Re: [RE-wrenches] AC Coupled + CC Grid Feed Input

2014-05-29 Thread toddcory
here is the direct link: http://enphase.com/global/files/Enphase_Application-Note_AC-Coupled-Battery-Based-Systems.pdf On Thursday, May 29, 2014 10:21am, "Nick Soleil" said: Hi Drake, I'm happy to discuss the ins-and-outs of this with you by phone. My cell phone is listed bel

Re: [RE-wrenches] AC Coupled + CC Grid Feed Input

2014-05-29 Thread Nick Soleil
Hi Drake, I'm happy to discuss the ins-and-outs of this with you by phone. My cell phone is listed below. I have installed AC Coupled systems using Outback GVFX inverters and a 120-240 transformer. My experience is that this works fine. We have published a basic document on this, which is prim

Re: [RE-wrenches] AC Coupled + CC Grid Feed Input

2014-05-28 Thread jay peltz
Hi Drake, I have done this, or I think what you are asking. I have AC coupled 2 enphase 190s through a transformer to a VFX-3525 in an offgrid situation. It worked fine. However I did notice when there were very little loads I got what I think is an AC ripple. I would see some lights having I

[RE-wrenches] AC Coupled + CC Grid Feed Input

2014-05-28 Thread Drake
Hello Wrenches, We put a system in a year ago with an Outback GVFX 3524 with 2205 W of PV and a Midnite Solar Classic CC. The system owner would now like to expand the system by another 6 modules. Our tentative plan is to AC couple 6 Enphase M-215s powered by 6 REC 255 W modules to the Outb

Re: [RE-wrenches] AC coupled ProSine

2013-05-13 Thread Kent Osterberg
May 13, 2013 3:16 PM To: RE-wrenches Subject: [RE-wrenches] AC coupled ProSine Has any put together an ac-coupled system using the Xantrex ProSine inverter? I've got a customer that wants to try this and I don't even know if it is possible to do with the ProSine. I'd rather not be t

Re: [RE-wrenches] AC coupled ProSine

2013-05-13 Thread David Katz
.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg Sent: Monday, May 13, 2013 3:16 PM To: RE-wrenches Subject: [RE-wrenches] AC coupled ProSine Has any put together an ac-coupled system using the Xantrex ProSine inverter? I've got a customer that wants to try

[RE-wrenches] AC coupled ProSine

2013-05-13 Thread Kent Osterberg
Has any put together an ac-coupled system using the Xantrex ProSine inverter? I've got a customer that wants to try this and I don't even know if it is possible to do with the ProSine. I'd rather not be the first to give it a try. -- Kent Osterberg Blue Mountain Solar, Inc. www.bluemountainsol

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-08 Thread Ryan
-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake Sent: Friday, March 08, 2013 9:40 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Magnum Issue Thank you to all who responded to this post. Larry, that sounds like a great potential

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-08 Thread Drake
Thank you to all who responded to this post. Larry, that sounds like a great potential solution. That will put the frequency shift in line with where the battery cutoff voltage needs to be. The frequency shift happens 2 volts above the absorption charge set point. My only issue with the soluti

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Brian Faley
Solar Power Systems Sent: Thursday, March 07, 2013 3:36 PM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Magnum Issue ANDyou are still working on that stand-alone, programable, temperature compensated battery chargerright??? Thank you, Larry Crutcher Starlight Solar Power

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Larry Crutcher, Starlight Solar Power Systems
ANDyou are still working on that stand-alone, programable, temperature compensated battery chargerright??? Thank you, Larry Crutcher Starlight Solar Power Systems On Mar 7, 2013, at 4:07 PM, Brian Faley wrote: Hi Allan, In answer to your question: Yes, we’re developing an AC side 4k

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Brian Faley
y Inc. 2211 West Casino Rd Everett, WA 98204 Ph 425-353-8833 www.magnumenergy.com From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar Sent: Thursday, March 07, 2013 2:41 PM To: RE-wrenches Cc: Support Subject: Re: [RE-wre

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Allan Sindelar
OK, a bit more: The line diagram I was referencing was dated 5/1/2010. A later diagram from a Powerpoint given at last year's NABCEP CE conference shows a "MagNet" AC diversion controller. It allows AC diversion loads and three-stage charging. No mention of temp c

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Larry Crutcher, Starlight Solar Power Systems
Meant to say, "You should tweak #3 & #4 above..." Drake, Charging an AGM battery does not have to occur at the maximum charge voltage allowable; you can charge at a lower voltage for longer periods of time and still achieve 100% SoC. Since you have grid power to work with, slow down the charg

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Allan Sindelar
Drake, Magnum's approach does not use disconnecting the AC output from the GT inverter as a fail-safe method of preventing battery overcharge. Rather, the Magnum documents I have use a DC diversion controller and diversion load for this purpose. Their method

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Larry Crutcher, Starlight Solar Power Systems
Drake, Charging an AGM battery does not have to occur at the maximum charge voltage allowable; you can charge at a lower voltage for longer periods of time and still achieve 100% SoC. Since you have grid power to work with, slow down the charge cycle. Assuming you have a late model ME-RC and v

[RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Drake
Hello Wrenches, I had an unexpected glitch in AC coupling a Magnum 4024 PAE inverter. The system utilizes AGM batteries, which (according to Concorde tech support) have a very strict upper voltage limit. The relay used to stop the current input from the direct grid tie inverter, when batter

Re: [RE-wrenches] AC Coupled

2012-02-18 Thread Darryl Thayer
PM Subject: Re: [RE-wrenches] AC Coupled Larry, I have run into similar situations. The simplest thing is to wire the Sunny Boy 6000 into a breaker in a small dedicated box on the *grid side* of the transfer switch. Grid present: feeds back normally Grid absent: interacts with Sunny

Re: [RE-wrenches] AC Coupled

2012-02-18 Thread Hilton Dier III
Larry, I have run into similar situations. The simplest thing is to wire the Sunny Boy 6000 into a breaker in a small dedicated box on the *grid side* of the transfer switch. Grid present: feeds back normally Grid absent: interacts with Sunny Islands Grid absent, genset on: Sunny Boy cut off

Re: [RE-wrenches] AC coupled GT Sunny Island w Enphase; string optimizers

2011-02-01 Thread Kelly Keilwitz, Whidbey Sun & Wind
Wrenches, Here's an update on this configuration (20kW Enphase, AC coupled to Sunny Islands) you should know about: Enphase will not support and warranty the use of their micro inverters in an AC-coupled installation with battery-based inverters. Enphase approved this verbally with us in d

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread Kelly Keilwitz, Whidbey Sun & Wind
s? Best, August -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kelly Keilwitz, Whidbey Sun & Wind Sent: Friday, January 14, 2011 9:35 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC coupled, grid-tie

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread August Goers
wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kelly Keilwitz, Whidbey Sun & Wind Sent: Friday, January 14, 2011 9:35 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass Hi August, To make sure

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread Kelly Keilwitz, Whidbey Sun & Wind
sage- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kelly Keilwitz, Whidbey Sun & Wind Sent: Thursday, January 13, 2011 7:33 PM To: RE Wrenches listserve Subject: [RE-wrenches] AC coupled, grid-tied Sunny Island - contact

Re: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-14 Thread August Goers
: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kelly Keilwitz, Whidbey Sun & Wind Sent: Thursday, January 13, 2011 7:33 PM To: RE Wrenches listserve Subject: [RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass Wre

[RE-wrenches] AC coupled, grid-tied Sunny Island - contactor & bypass

2011-01-13 Thread Kelly Keilwitz, Whidbey Sun & Wind
Wrenches, We are including 2 Sunny Island inverters into a previously battery- less grid tied design utilizing 20 kW of PV on Enphase micro inverters and 2 SMA Windy Boy 6000 inverters (10 kW XZERES 442 turbine). Our customer wishes to run his fuel generator as little as possible when the g

Re: [RE-wrenches] AC Coupled Issues

2010-04-19 Thread Dave Click
Jeff- The Sunny Boys can be reprogrammed into "off grid" mode so they can work between 56-64 Hz, but I believe you need both a service cable and a call to SMA tech support to make that happen. They then note in their system that that inverter's been adjusted to no longer meet UL 1741. Jeff Yag

Re: [RE-wrenches] AC Coupled Issues

2010-04-17 Thread Andrew Truitt
Jeff - We have a number of systems with exactly that configuration and we haven't had any issues. However, we have not installed the XW/SB combination since Xantrex (Schneider?) rolled out the firmware that incorporates the high battery frequency shift to shut down the solar inverter(s). We switc

Re: [RE-wrenches] AC Coupled Issues

2010-04-17 Thread Jeff Yago
As mentioned before, many of our clients want battery backup with their solar, but are not off-grid. They also want a generator so battery banks can be down-sized. For many of these applications we use a SunnyBoy at the array when the aray is located hundreds of feet from house, and usually a

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-23 Thread Nick Soleil
ma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax:707-769-9037 From: Jeff Yago To: RE-wrenches Sent: Wed, October 21, 2009 7:53:11 PM Subject: Re: [RE-wrenches] AC Coupled Re-visited There have been some good advice related to battery bank sizin

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-23 Thread toddcory
and the > battery bank is 48 volts 3500 AH > > --- On Tue, 10/20/09, Glenn Burt wrote: > > > From: Glenn Burt > > Subject: Re: [RE-wrenches] AC Coupled Re-visited > > To: "'RE-wrenches'" > > Date: Tuesday, October 20, 2009, 2:13 PM >

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-22 Thread Phil Undercuffler
w Phil sent you ;-) I think there is a lot of opportunity to add power reliability and stability to traditional grid tie systems -- what we need is a way to do it easily and effectively. Here's to looking for a way! Phil Undercuffler Conergy > -- Forwarded message -- >

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread boB Gudgel
Jeff Yago wrote: There have been some good advice related to battery bank sizing and a better description of how Sunny Islands work with SunnyBoys, but I am afraid we are getting away from my original post that started this and that was: Since a battery based inverter has a battery charging se

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread Jeff Yago
There have been some good advice related to battery bank sizing and a better description of how Sunny Islands work with SunnyBoys, but I am afraid we are getting away from my original post that started this and that was: Since a battery based inverter has a battery charging section and all kinds

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread Darryl Thayer
urt > Subject: Re: [RE-wrenches] AC Coupled Re-visited > To: "'RE-wrenches'" > Date: Tuesday, October 20, 2009, 2:13 PM > > > > > > > > > > > > > > > > > SMA recently told me that the > recomme

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Allan Sindelar
Phil, Good advice. Assuming 48V and a large system, what would you use as a diversion load and controller in this application? As I understand it, this would be a DC diversion load, such as a wind gennie air heater, that would be gradual, resistive, and noncritical for occasional use in this rare

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Phil Undercuffler
t; > > -- Forwarded message -- > From: "Walt Ratterman" > To: , "'RE-wrenches'" < > re-wrenches@lists.re-wrenches.org> > Date: Tue, 20 Oct 2009 12:37:04 -0700 > Subject: Re: [RE-wrenches] AC Coupled Re-visited > > Glenn

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Walt Ratterman
2:14 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] AC Coupled Re-visited SMA recently told me that the recommended Ah of the battery bank is related to the amount of PV and connected inverters. They recommended a 500Ah bank with a 5kW PV SB, and a 600Ah bank with a 6kW PV SB. 100Ah to 1

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Glenn Burt
f Of Mark Frye Sent: Tuesday, October 20, 2009 2:42 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] AC Coupled Re-visited Thanks Kent. And so I understand more clearly, in the case of 2 SIs as you describe, each SI has it's own battery bank, and the solar would be split between

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Michael Welch
Behalf Of Jeff Yago Sent: Tuesday, October 20, 2009 9:52 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Re-visited it is my understanding that the Sunny Island coupled with Sunny Boys is able to taper charge in an AC coupled system as the 2 inverters are able to communicate with each other

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Mark Frye
hes.org] On Behalf Of Kent Osterberg Sent: Tuesday, October 20, 2009 11:10 AM To: glenn.b...@glbcc.com; RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Re-visited In off-grid mode the Sunny Island uses frequency shift power control to reduce the output of the Sunny Boy inverters and thereby regulat

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Kent Osterberg
: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa Sent: Tuesday, October 20, 2009 12:05 PM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Re-visited   Greetings..it is my understanding that the Sunny Island coupl

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Glenn Burt
ts.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa Sent: Tuesday, October 20, 2009 12:05 PM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Re-visited Greetings..it is my understanding that the Sunny Island coupled with Sunny Boys is able to tap

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Mark Frye
ar.com _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago Sent: Tuesday, October 20, 2009 9:52 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC Coupled Re-visited it is my understanding that the Sunny Island couple

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Jeff Yago
it is my understanding that the Sunny Island coupled with Sunny Boys is able to taper charge in an AC coupled system as the 2 inverters are able to communicate with each other and the Sunny Island alters the frequency input of the Sunny Boys and lowers the total output of the Sunny Boys to match th

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Kirpal Khalsa
Greetings..it is my understanding that the Sunny Island coupled with Sunny Boys is able to taper charge in an AC coupled system as the 2 inverters are able to communicate with each other and the Sunny Island alters the frequency input of the Sunny Boys and lowers the total output of the Sunny B

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Mick Abraham
Hi, All~ On an AC coupled system as Jeff describes, the "battery charge circuitry" on the battery based inverter is not even participating. A straight pure sine inverter...with no charger function built in...would also "charge" the battery if AC coupled to a SunnyBoy with no grid available. The "

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-20 Thread Jeff Yago
We have completed several totally different AC coupled systems using different inverters, due to large ground mounted arrays that had to be located a great distance from inverter-battery-generator-grid BAS, which are working just fine even with the mis-match of inverter brands.  The SunnyBoy seems

Re: [RE-wrenches] AC coupled with grid and backup generator

2009-07-28 Thread Darryl Thayer
I have experienced the same thing with Outback and PVPowered. DT --- On Tue, 7/28/09, Mark Dickson wrote: > From: Mark Dickson > Subject: Re: [RE-wrenches] AC coupled with grid and backup generator > To: jry...@netscape.com, "'RE-wrenches'" > Date:

Re: [RE-wrenches] AC coupled with grid and backup generator

2009-07-28 Thread Mark Dickson
-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago Sent: Tuesday, July 28, 2009 6:55 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC coupled with grid and backup generator We are completing a residential 4 kW solar system that is on the

Re: [RE-wrenches] AC coupled with grid and backup generator

2009-07-28 Thread Jeff Yago
We are completing a residential 4 kW solar system that is on the grid, but has backup battery-powered Xantrex 6 kW inverter, AC coupled Sunny-Boy inverter, and a 17 kW Kohler generator.  The larger generator is to allow operation of a ground-source heat pump during winter which is not supplied from

Re: [RE-wrenches] AC coupled relay

2009-06-05 Thread Richard L Ratico
Hi Drake, Up to now, like you, we've been using the SMA DATA SHEETS (the glitzy ones with the color graphics) to size our wiring and breakers. But, those sheets make no mention of a MAXIMUM OUTPUT FAULT CURRENT. MAXIMUM OUTPUT FAULT CURRENT is specified only in the very last pages of the inst

Re: [RE-wrenches] AC coupled relay

2009-06-05 Thread Drake Chamberlin
Hi Dick, Thanks for the suggestion. I will run the concept by the SMA tech people. I did use the SMA spec sheets in sizing the wiring, but maybe opening the relays creates fault current at a voltage that will jump the gap. Drake At 10:50 PM 6/4/2009, you wrote: Hi Drake, I'm sending you

Re: [RE-wrenches] AC coupled relay

2009-06-04 Thread Richard L Ratico
Hi Drake, I'm sending you some attachments off list as well. They are Sunny Boy Specs from the SMA Installation Manuals, which are more complete than those on the SMA data sheets. Note, the Maximum Output Fault Current for the 3000 & 4000 is 30 amps, while Maximum Overcurrent Protection is 30 A

Re: [RE-wrenches] AC coupled relay

2009-06-04 Thread Drake Chamberlin
Hi Dick, There are three inverters, all Sunny Boys, a 3000, 4000 and a 7000. The breakers are QO. The AC conductor sizes are #8 for the 7000, #10 for the 4000 and #12 for the 3000. The breakers are set for the NEC ratings of the wire (40 A, 30 A and 20 A.). I sent some information to you

Re: [RE-wrenches] AC coupled relay

2009-06-04 Thread Richard L Ratico
Hi Drake, Could you please provide more information, array size, inverter make / model, conductor size, breaker rating, breaker brand? Dick Solarwind Electric Bradford, VT --- You wrote: If I'm following this thread correctly, the relay is to break the flow of AC current to the battery ba

Re: [RE-wrenches] AC coupled relay

2009-06-03 Thread Jeff Yago
Thanks to Christopher Freitas and Kirk who answered my question.   Its great to have this resource for a quick answer to problems others have already resolved.   By the way, we have found a great new way to install ground mounted racks.  Maybe I am the last to know, but sign companies who do work f

Re: [RE-wrenches] AC coupled relay

2009-06-03 Thread Drake Chamberlin
e 03, 2009 11:05 AM To: jry...@netscape.com; 'RE-wrenches' Subject: Re: [RE-wrenches] AC coupled relay I have done it with a SQD 60a, 240 vac contactor. The coil is 120 vac. It is driven by a secondary 12vdc relay sending 120 ac to the coil. The coil of the dc relay is driven by the

Re: [RE-wrenches] AC coupled relay

2009-06-03 Thread Christopher Freitas
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago Sent: Wednesday, June 03, 2009 9:35 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC coupled relay What specific supplier, model number, and brand relay have you foun

Re: [RE-wrenches] AC coupled relay

2009-06-03 Thread Kirk Herander, VSE
...@lists.re-wrenches.org] On Behalf Of Jeff Yago Sent: Wednesday, June 03, 2009 9:35 AM To: RE-wrenches Subject: Re: [RE-wrenches] AC coupled relay What specific supplier, model number, and brand relay have you found to be perfect to isolate the inverter AC output to the sub-panel of a battery-based

  1   2   >