Sam,
I'll try and answer your question as best I can.
AC or DC shouldn't matter when conducting insulation resistance testing
(IRT) because the conductors shouldn't be connected to an AC or DC power
source. You definitely can't conduct insulation resistance testing when the
conductor is connected
Jeff,
I don't know how much pricing has changed lately but the Kohler 12RES was
going for around $5,000 with a two-wire start built-in. That's only $500
more than the smaller generator with a lot more capacity. I don't think
they make it in gasoline so you'd have to use propane.
Thanks,
Will
On
I've got a PV array attached to my standing seam metal roof directly above
my bed about 24" from my head when I'm sleeping and although we do hear
some expansion/contraction noises it's not a problem. Every once in a while
we'll hear a loud noise but I think that's more from my timber frame
shiftin
Milbank makes a kit that will add a second set of lugs to their meter
sockets. Not sure if it's approved by your utility, you should check with
them and see what they allow.
On Sun, Sep 19, 2021 at 9:50 AM Al Frishman wrote:
> Hey Wrenchers,
> I have a client that is installing a new electric se
Jerry,
I'm curious, how did they prove over torquing? When doing inspections it's
easy to find connectors that are under torqued but I haven't heard of a
reliable way to check for over torque.
Thanks,
Will
On Mon, Sep 6, 2021 at 1:34 AM Jerry Shafer
wrote:
> 1/4" x 20 is no more the 10 ftlbs (
ches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.c
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives fo
nuals and white papers of the inverter
manufacturers to determine if they can do this. I believe both SolarEdge
and Enphase can do it. I'd assume others can as well.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Ce
Jason,
You should dig into the PVWatts help documentation. They get into pretty
good detail on how their calculations work. You might find the answer
you're looking for there.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272
t was torn, so the clips that hold
> the metal to the roof held, at least long enough for the metal to tear. It
> is completely plausible that the point load was too high from too few
> clamps.
>
>
>
> On Mon, Oct 19, 2020 at 8:16 AM Will White wrote:
>
>> It
anks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34
Do you envision a world powered by renewable energy? Be the change
<http://solarenergy.org/donate>.
On Sun, Oct 18, 2020
amp; settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update parti
org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponso
tteries is relatively flat.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34
Do you envision a world powered by renewable energy? Be the change
<http://solarenergy.org/donate&g
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
*Will White*
Curriculum Developer
e: w...@solarenergy
the tests and
all. So. unless you can get the actual letter with the UL numbers, I
wouldn't necessarily put much faith in that. This is coming more from the
radio side of Chinese equipment, but I suspect it could apply to the solar
side as well."
Thanks,
Will
--
*Will White*
The 25 W would be used to size the batteries, 49 VA would be used to size
the inverter.
Good luck,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34
*FACT: If we covered 0.33
etail/?product_key=6362
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34
*FACT: If we covered 0.33% of the earth with solar panels, we could power
the world with rene
semble. It
looks more like the LG RESU but it's AC and has multiple microinverters in
it.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Professional
# 093006-34
*FACT: If we covered 0.3
the system. For example, if you have a 48
V system you need a 48 V battery, you can't (usually) use two 24 V
batteries in series with lithium-ion.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installati
Why not use a couple of micro inverters? You'd have to check the specs to
see if they're compatible but that may work.
Thanks,
Will White
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Installation Pr
they are no known arc/ground fault
> backfeed approved rated breakers?
>
> Jay
>
>
>
> On Apr 25, 2019, at 11:45 AM, Will White wrote:
>
> Jay,
>
> You're triggering some serious PTSD with this question. When 2017 NEC came
> out Mass was the first state t
& settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update
;> www.members.re-wrenches.org
>>
>> _______
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/r
lling to
> avoid the issues Will discussed. A little common sense goes a long way to
> avoid stripped screws. Just my 2 cents worth.
>
>
>
> *From:* RE-wrenches *On
> Behalf Of *Will White
> *Sent:* Wednesday, March 27, 2019 11:04 AM
> *To:* RE-wrenches
> *Subject:* Re:
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
NABCEP Certified PV Instal
//www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
>
>
ep 13, 2018 at 11:07 AM jay wrote:
> HI Will,
>
> I found this unit from Japan. Hioki CM4372
>
> jay
>
> peltz power
>
>
>
> On Sep 13, 2018, at 5:28 AM, Will White wrote:
>
> Hello Wrenches,
>
> I've started doing some work on 1,000 VDC systems so
installers what's your go to refrigerator recommendation?
> I'm going to go through the energy star website but I thought I'd consult
> with the experts too. I'd like to find something that has a form factor
> similar to the Sunfrost although I know that's going to be
gt;
> -
> From: "jay"
> To: "RE-wrenches"
> Cc:
> Sent: Thursday September 13 2018 10:07:17AM
> Subject: Re: [RE-wrenches] Multi-meters
>
> HI Will,
>
> I found this unit from Japan. Hioki CM4372
>
> ja
on't have that much money in the
budget.
Is it worth getting a 1,500 VDC meter or is 1,000 VDC enough? What are you
techs in the field using?
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
PV Installation Professional
# 09
ood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
ion?
I'm going to go through the energy star website but I thought I'd consult
with the experts too. I'd like to find something that has a form factor
similar to the Sunfrost although I know that's going to be hard to find.
Thanks,
Will White
--
*Will White*
Curricul
-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
&g
tserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
&g
gt;> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
> ___
> Li
e-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.member
PO.
https://www.youtube.com/watch?v=TWfXAvfRyIM
Thanks,
Will
--
*Will White*
Curriculum Developer
[image: Inline image 3]
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
PV Installation Professional
# 093006-34
On Thu, Aug 31, 2017 at 2:00 AM, William Miller
wrote:
> Fr
gt;>
>>
>>
>> www.cometsolar.com <http://www.cometenergysystems.com>
>>
>> 264.235.5670 <(264)%20235-5670>
>>
>> 869.662.5670 <(869)%20662-5670>
>>
>> Skype: netconcepts
>>
>> __
hes.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/
org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
--
*Will White*
Curriculum Developer
[image: Inline image 3]
e: w...@solarenergy.org
w: www.solarenergy
ver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re
Hey Wrenches,
I'm doing an upgrade to an Outback VFX series off-grid system with the
flexware boxes. What type/brand of ring connectors and crimpers do you all
use for the DC breakers with the post terminals?
Thanks,
Will
___
List sponsored by Redwood
Mike,
Have you read the Enphase white paper on module to inverter size? It goes
into good detail on why they do it.
http://www2.enphase.com/global/files/Enphase_White_Paper_Module_Rightsizing.pdf
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w
s.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
ck-boots transformer at the home to
> get us back to 240 volts? This would need to be service entrance sized.
>
>
>
> *Howard ?Scot? Arey*
>
> Owner, Solar CenTex
>
> 254-300-1228
>
> scot.a...@solarcentex.com
>
>
>
>
>
> _
Does anyone know where I can get two SunTech STP-175 black modules? Please
contact me off list.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
PV Installation Professional
# 093006-34
.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-3092
PV Installation Professional
# 093006-34
On Fri, Aug 5, 2016 at 1:41 PM, wrote:
> Since I am having such a tough time even getting a call back, never mind
> reimbursments,
t 3' wide and have a rubber back. I get them cut in about 10' sections
and lay them out to make a path from point A to point B. Customers really
appreciate that.
Thanks,
Will
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-309
PV Install
e-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.mem
nches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-309
PV I
a system on one building with
it's own meter to connect to a meter on a different building.
I'd suggest you ask the utility what their policy is.
Good Luck,
Will White
--
*Will White*
Curriculum Developer
e: w...@solarenergy.org
w: www.solarenergy.org
p: 802-272-309
PV Installation
Has anyone found a viable alternative?
The real issue I see is that we have to use something accepted by incentive and
finance organizations and so far the only thing they accept (for the most part)
is SunEye and Pathfinder.
Thanks,
Will
Will White
Director of Construction – East Coast
RGS
We use the RA-35 on the link you had below. They work really well because they
only take a few screws.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Benn Kilburn
Sent: Wednesday, January 06, 2016 4:20 PM
To: RE-wrenches
Subject: [RE-wrenches] Temporary Roof
issues, it just
doesn’t clean clothes as well as standard front or top load design.
I’m curious what others use for strategies when firing up or turning off the
generator?
Thanks,
Rich
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Will White
Sent: Wednesday, D
I had a problem with one of the control boards on my front load dryer on my off
grid Outback system. Seems that some type of surge fried the board. It was
replaced and I added a whole house AC surge protector. I don’t know if the
surge protector worked but I haven’t had any problems since.
F
We’ve also used the ECO-65 which works great but the problem with your roof
will be flashing. The roofs we installed on were asphalt so we could use the
flashing. It’s going to be hard to seal a ECO-65 plate on a metal roof.
Will White
Director of Construction – East Coast
RGS Energy
64
Talk to your tax advisor (or have the customer talk to theirs). Don't ever
give out tax advise (unless you're licensed to) as it opens you to liability
should you give them the wrong advise and they get audited by the IRS.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
I’ve seen photos from one of the leasing companies of arrays right next to a
golf course that got multiple ball strikes. They were having to constantly
replace modules which lead to a rule of no arrays within some number of feet
from a course. I think it was 300’.
From: RE-wrenches [mailto:r
I second the last paragraph. Even though we’ve had issues with DP&W I still
like their product.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of William Miller
Sent: Thursday, October 08, 2015 3:14 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DPW Rack Problems
a
plastic tube instead of the paper one so that helps prevent them from blowing
out when they get a little damp.
Thanks,
Will
Will White
Director of Construction – East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com
area.
Thanks,
Will
Will White
Director of Construction – East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsenergy.com/> |
william.wh...@rgsenergy.com<mailto:william.wh...@rgse
This is what I did at my house. There's large conductors going to the house
for the generator output and small conductors coming back from the main load
center to power the charger and electronics. I live off the grid and the load
isn't noticeable.
Thanks,
Will
Will White
D
kind of a pain and
I could see how a less savvy customer could mess this up pretty easily.
Thanks,
Will
Will White
Director of Construction - East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com | william.wh...@rgs
too expensive.
I wouldn’t install the mounts in house because slate is so difficult to work
with. You also can’t walk on it or it cracks.
Good Luck,
Will
Will White
Director of Construction – East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax
We've found the M250 to be just as stable as the M215. Usually when we have an
issue it's right out of the box.
Thanks,
Will
Will White
Director of Construction - East Coast
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGS
We’ve used Ecofasten ECO-65 successfully on both SIP roofs and membrane roofs.
They’re expensive and a bit labor intensive but it’s a good solution. They
have metal flashing for asphalt roofs and you can also use membrane patches on
pretty much any type of membrane or rolled asphalt roof.
htt
DP&W makes an off price list option that is some type of mechanical adjustment.
It has to be ordered beforehand and can’t be retrofit.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Mick Abraham
Sent: Monday, September 08, 2014 10:11 AM
To: RE-wrenches
Subject
d shutdown.
Thanks
On Wed, Aug 27, 2014 at 7:47 AM, Will White
mailto:william.wh...@rgsenergy.com>> wrote:
Our experience in MA with rapid shutdown unfortunately varies with AHJ. Some
are letting us put an Eaton NEMA 4 disconnect on the roof next to the array.
Some are letting us put a
switch which is
expensive.
Rapid shutdown doesn’t apply to pole or ground mounts.
Hope this helps.
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsenergy.
or otherwise.
Thanks,
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsenergy.com/> |
william.wh...@rgsenergy.com<mailto:william.wh...@rgse
It's still a good best practice to bond both ends in case of a fire if the
conduit becomes separated in the middle it will still be bonded.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of William Miller
Sent: Tuesday, July 15, 2014 1:47 AM
To: 'RE-wrenches'
Subj
We’ve used tons of them. Pretty standard Tier 1 Chinese panel. They’re you’re
average PV panel, nothing exceptional but nothing bad either in my experience.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Kristopher Schmid
Sent: Friday, July 11, 2014 2:53 PM
T
Have you checked out Eco Fastens ECO-65? It's a large plate with 8 screws and
it's got flashing for both asphalt and membrane roofs.
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of will...@millersolar.com
Sent: Tuesday, June 03, 2014 12:09 PM
To: RE-wrenches
Su
ake a standard breaker panel, install a Arc fault and run the wiring from the
enphase like it is the grid: ie into the main lugs.
Then this will go out through the breaker in the correct fashion, and onto the
main panel.
jay
peltz power
PS as to the code, they want it this way
On May 20, 2014,
commissioning, ships disabled.
Phil Forest
South Mountain Company
On May 20, 2014, at 10:59 AM, Will White
mailto:william.wh...@rgsenergy.com>> wrote:
Wrenches,
Is anyone else having problems with inspectors and the 2014 NEC? In Mass we’re
having all kinds of issues with inspectors requiring/al
o run the trunk cable in a raceway.
It's getting very difficult to install in Mass.
Thanks,
Will
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsene
We use Locus in MA. It’ autoreports.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of James Gustafson
Sent: Thursday, May 08, 2014 1:13 PM
To: RE-wrenches
Subject: [RE-wrenches] Data acquisition system for Mass-CEC
Hello Hard Workin
We had a new competitor take a video of one of our installs (with owner's
permission) and post it on the front of their web page. I believe it's still
there almost two years later.
It's a shady thing to do but I don't think there was anything we could legally
do to stop them.
From: re-wrenche
I've had a similar experience as August.
We're using Ecofasten Green Flashing plus all holes get a dab of Geocel
Proflex. We've also never had a problem with a properly flashed penetration.
Thanks,
Will
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenc
<mailto:william.wh...@rgsenergy.com>
Will White
Operations Manager - New England
RGS Energy
64 Main St. |Montpelier, VT 05602
tel 802.223.7804 | mobile 802.234.3167 | fax 802.223.8980
RGSEnergy.com<http://www.rgsenergy.com/> |
william.wh...@rgsenergy.com<mailto:william.wh..
's my $0.02
Thanks,
Will
______
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com<http://www.realgoodssolar.com/>
The All Earth Trackers will hold about 5 kW of modules:
http://www.allearthrenewables.com/
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Daum
Sent: Thursday, August 01, 2013 1:06 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] B
As far as I understand it doesn't matter which color you use for which
conductor as long as it isn't white, gray, or green.
We have different crews using different colors but I think black and either
blue or red is the most common.
Thanks,
Will
From: re-wrenches-boun...@lists.re-wrenches.org
We use PV Wire which is double insulated on the roof in free air and regular
THHN/TNWN for the run from the junction box back to the inverter (using no
white or gray wires of course).
Thanks,
Will
__
Will
anks,
Will
__
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wr
done?
Thanks,
Will
______
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com<http://www.realgoodssolar.com/>
___
List sponsored by
.
Thanks,
Will
__
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
-Original Message-
From: r
e box.
Thanks,
Will
______
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com<http://www.realgood
Viessmann also uses Wilo pumps (you should be able to get them locally from
Blodgett Supply). I believe Viessmann also uses Typhocor. I think they're a
European glycol manufacturer.
Thanks,
Will
__
I don't have any experience in large storage but I know Dynapower in Vermont is
working on a storage solution. You should check them out:
http://www.dynapowerenergy.com/
Thanks,
Will
__
Will
m day one. I've never had
a problem and with the Flexnet DC monitor there are all kinds of great settings
for when you want it to start and stop. It's worked flawlessly since I set it
up.
Thanks,
Will
k.
Thanks,
Will
__
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
-Origin
tached you won't have problems.
Snow is also another reason you don't see a lot of gutters in Vermont.
That's my .02
Thanks,
Will
______
Will White
Regional Field Operations Manager - New England
lso if you have an asphalt shingle roof you can create an unbalanced load with
snow sliding off the south side and sticking on the north side. Most engineers
take this into consideration too.
Thanks,
Will
__
out
the rivets.
__
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com<http://www.realgoodssolar.com/>
From: re-wrenches-boun...@
fasteners so it doesn't go through the
finished ceiling inside.
Thanks,
Will
______
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-
We never answer tax questions. We always refer the customer to a tax
professional. You can get in some pretty big trouble giving tax advice and
open yourself up to some serious liability.
__
Will White
d the problem.
__
Will White
Regional Field Operations Manager - New England
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
-Ori
We use the LA302R for AC and LA602DC for the DC side. I don't think I've ever
had one of them struck so I can't say how well they actually work.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Keith Cronin
Sent: Friday, August 17,