What a swap over...we have a muni project where the higher voltage optimizers on the 480v inverter allowed us to minimize conductor sizing. New central inverter would need to support strings that use that size. And then the labor to remove all those optimizers! But we're replacing one of those inve
: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org> ] On Behalf Of Scot Arey via
RE-wrenches
Sent: Wednesday, May 29, 2024 3:16 PM
To: 'RE-wrenches'
Cc: scot.a...@solarcentex.com <mailto:scot.a...@solarcentex.com>
Subj
Offgrid Solar
"we go where powerlines don't"
<http://members.sti.net/offgridsolar/><https://offgridsolar1.com/>
https://offgridsolar1.com/ <http://members.sti.net/offgridsolar/>
e-mail <mailto:offgridso...@sti.net> offgridso...@sti.net
text 209 8
inverter to match with the existing
optimizers. They will not work with Sol-Ark and vice versa.
Tom McCalmont
CEO, Paired Power
pairedpower.com <http://pairedpower.com> | LinkedIn
<https://www.linkedin.com/company/paired-power/>
(650) 701-7247
On May 22, 2024, at 6
I understand this. Whereas I can set absorb times and charged return ampsnfor an FM80, my SolArk appears to give generic times based on size of battery bank. Maybe it's a minimal issue but fact that Rolls has identified a concern is noteworthy to me.Thanks.Howard "Scot" AreyOwner, Solar CenTex254-3
Wow, are we in the golden age of inverter/chargers? If it had 200-a.p pass thru it would be near perfect.Begs the question: are stand alone charge controllers becoming a historical artifact?Howard "Scot" AreyOwner, Solar CenTex254-300-1228
___
List sponso
Fronius Primo are great and up to 15kw 240v version.
From: RE-wrenches On Behalf Of
William Miller via RE-wrenches
Sent: Thursday, February 22, 2024 5:51 PM
To: RE-wrenches
Cc: William Miller
Subject: [RE-wrenches] Non-battery string inverter options?
Friends:
Now that RSS is requir
Wireless smoke alarms that interconnect to the home system. UL listed.
Gamechanger for applications like this.
From: RE-wrenches On Behalf Of
William Miller via RE-wrenches
Sent: Friday, November 17, 2023 12:08 AM
To: RE-wrenches
Cc: William Miller
Subject: [RE-wrenches] ESS in attached ga
Just attended the NABCEP conference last week and took in CEU classes from
Rolls and Midnite on battery charging and design. Just awesome classes and I
walked away thinking the FLA were kind of like my old 7.3 Powerstroke
diesel.I could work on them and could see when issues were developing. The
li
Hate to ask but are these long lead like SMA and Fronius have become? If
shortage, is this some sign that charge controllers are being overtaken by
hybrid inverters with integrated chargers (like Sol-Ark?).
-Original Message-
From: RE-wrenches On Behalf Of
jay via RE-wrenches
Sent: Tuesda
I have found many of the utilities, especially the cooperatives will undersize transformers relative to main service capacity.Wel always try to check and very infrequently is the transformer smaller than proposed system design.We have had to upgrade some transformers. Tough pill but hard to argue
on for a single
module.
Was surprised by one manufacturer who advised us to read that bypass diodes
were not an warranty defect even though the module was making half power.
Good luck, look forward to hearing how your case goes.
Scot Arey
Solar CenTex
From: RE-wrenches On Behalf Of
D
I agree. I also had a Bolt battery recall and we joked that GM probably got
better priority than Solar CenTex for limited battery stock.
Glad you added that important context.
Scot
-Original Message-
From: RE-wrenches On Behalf Of
Hilton Dier via RE-wrenches
Sent: Monday, November 14,
That's interesting if it is the max CT input current. The 15kw comes with the 320amp cts so if I use two 150-amp cts in parallel seems I stay below that current.Howard "Scot" AreyOwner, Solar CenTex254-300-1228
___
List sponsored by Redwood Alliance
Pay
I think you're overstating this a bit. The generator integration feature wasn't the make or break selling point. It was simply a response to customer question of whether this would be possible. Of course the answer was that SE said a solution was forthcoming.I hardly believe that is some illegality
No hijack at all. Good and necessary dialogue. Thanks. ScotHoward "Scot" AreyOwner, Solar CenTex254-300-1228
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Ch
he installers, to their benefit (consider the long
queue for tech support and their response, "ok you have to be onsite for us
to do something before we RMA it." Which would be fine if we were not forced
to wait hour-plus for tech support.
Woul
it’s pretty nominal price after the
system controller, load controller(s?), and the essential loads panel.
My thoughts,
Scot Arey
Owner, Solar CenTex
From: RE-wrenches On Behalf Of AE
Solar via RE-wrenches
Sent: Monday, May 23, 2022 7:56 PM
To: RE-wrenches
Cc: AE Solar
Subject: [RE
Watching this thread. Same issues here in Texas. I can see the 5" hail strikes but what did the 2" hits do.Howard "Scot" AreyOwner, Solar CenTex254-300-1228
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
Li
??? How can
this be asked here?
Ron, are you NABCEP PV Installation Pro certified?
Scot Arey
Owner, Solar CenTex
From: RE-wrenches On Behalf Of
Jerry Shafer via RE-wrenches
Sent: Tuesday, April 12, 2022 10:27 PM
To: RE-wrenches
Cc: Jerry Shafer
Subject: Re: [RE-wrenches] Sol-Ark
This is excellent – thank you. I offered back to the inspector that this
language is much more precise than the open-end IRC language. Will advise all
what is returned.
Scot
From: RE-wrenches On Behalf Of
Vincent Jolissaint via RE-wrenches
Sent: Tuesday, March 29, 2022 12:31 PM
To: re-w
Good morning, Wrenches.
We all discuss the NEC when it comes to ESS but the section in International
Residential Code (IRC) R328 is something to look at carefully.
Easy to miss is the requirement to extend fire alarm systems to garage
spaces where we quite often install the ESS.
But the s
My head is exploding at thought of the Radian being AC coupled to the Sol-Ark. Howard "Scot" Areyowner, Solar CenTex254 300 1228
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists
Yes we use IQ combiners on all new projects. I will try to get my hands on this
filter.
Many thanks for all responses.
Howard "Scot" Arey
owner, Solar CenTex
254 300 1228
On Fri, Oct 16, 2020 at 11:30 AM -0500, "Nick Soleil"
wrote:
Th
ads/2018-IRC-UPDATE-Handout-9-1-17.pdf&ved=2ahUKEwiGv-zC_cHrAhVIeawKHcMWDqsQFjAMegQIARAC&usg=AOvVaw36RmseBH_BsTWca5GZc6jd
Howard "Scot" Arey
owner, Solar CenTex
254 300 1228
On Sat, Aug 29, 2020 at 6:07 PM -0500, "Jerry Shafer"
wrote:
I have
Egauge
Howard "Scot" Arey
owner, Solar CenTex
254 300 1228
On Mon, Dec 9, 2019 at 9:28 AM -0600, wrote:
Good morning fellow wrenchers. Looking for recommendations on an aftermarket
monitoring system. Commercial site, 208 and customer is putting back 3 times a
Yes I had also heard from Outback that AC Coupling not supported.
Too bad because the AC coupling load center was slick setup and integration.
Scot
Get Outlook for Android
On Wed, Jul 25, 2018 at 10:29 AM -0600, "Kelly Keilwitz, Whidbey Sun & Wind"
wrote:
Larry,I rec
Fronius has been wonderful and as you say, they are prompt.
More importantly, they have a tech team one can reach quite quickly.
Strongly recommend the company and its product line.
Howard "Scot" Arey
Solar CenTex
254-300-1228
Sent from Outlook Mobile
On Wed, Jun 15, 20
uctor back to the
Fronius 10.0 where we used the distribution plate to spead the amperage
across the six string input channels.
I'm stuck - any thoughts on other potential arc-fault causes?
Howard "Scot" Arey
254-300-1228
scot.a...@sola
er switch where both
the grid and the backup position are open (still allows PV grid-tied
operations to sell back to grid and partially offset loads during normal
grid ops) but closes the grid connection during grid failures so that the
battery backup provides power (with 2 Radians only).
Howard
indicated above?
- If the 4th wire is a neutral (I certainly hope it is), where
might I find the ground electrode conductor (the building is relatively new,
less than 10 years I believe.). FYI, the building is metal.
I look forward to your comments
Howard "Scot" Arey