This is excellent – thank you. I offered back to the inspector that this 
language is much more precise than the open-end IRC language. Will advise all 
what is returned.

 

Scot

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Vincent Jolissaint via RE-wrenches
Sent: Tuesday, March 29, 2022 12:31 PM
To: re-wrenches@lists.re-wrenches.org
Cc: Vincent Jolissaint <vince...@cobaltpower.com>
Subject: [RE-wrenches] ​IRC 328 and ESS...approved barriers and "subject to" 
damage

 

2021 International Fire Code
Revise as follows:
1207.11.7 Protection from impact. Stationary storage battery systems  ESS 
installed in a location 
subject to vehicle damage in accordance with shall  Section 1207.11.7.1 or 
1207.11.7.2 shall be 
provided with impact protection in accordance with Section 1207.11.7.3. be 
protected by approved 
barriers. Appliances in garages shall also be installed in accordance with 
Section 304.3 of the 
International Mechanical Code.
Add new text as follows:
1207.11.7.1 Garages.
Where an ESS is installed in the normal driving path of vehicle travel within a 
garage, impact 
protection complying with Section 1207.11.3 shall be installed. The normal 
driving path is a line 
perpendicular to the garage vehicle opening to the back wall, extending 3 ft. 
(914 mm) to either 
side along the back wall and to a height of 48 in. (1219 mm), (See Figure 
1207.11.7.1)  





Exception: Where the clear height of the vehicle garage opening is 7 ft 6 in, 
(2286 mm) or less, 
ESS installed not less than 36 inches (914 mm) above finished floor are not 
subject to vehicle 
impact protection requirements.








1207.11.7.2 Other locations subject to vehicle impact.
Where an ESS is installed in a location other than as defined in Section 
1207.11.7.1, and  is 
subject to vehicle damage, impact protection shall be provided in accordance 
with Section 
1207.11.7.3.











1207.11.7.3 Impact Protection Options.
Where ESS is required to be protected from impact in accordance with Section 
1207.11.7.1 or 
1207.11.7.2 such protection shall comply with one of the following:















1.  Bollards constructed in accordance with one of the following:
1.1  48 inches (1219 mm) in  length by 3 inches (76mm) in diameter schedule. 80 
steel pipe embedded 
in a concrete pier 12 inches (304 mm) deep and 6 inches (152 mm) in diameter, 
with 36 inches (914 
mm) of pipe exposed, filled with concrete, and spaced at a maximum interval of 
5 feet (1524 mm). 
Each bollard shall be located not less than 6 inches (152 mm) from an ESS.
1.2  36 inches (914 mm) in height by 3 inches (76 mm) in diameter schedule 80 
steel pipe fully 
welded to an 8 inches (203 mm) by 8 inches (203 mm) by  ¼ inch (6.4 mm) thick 
steel plate and 
bolted to a concrete floor by means of 4 - ½ inch (13 mm) concrete anchors with 
3 inch (76 mm) 
minimum embedment.  Spacing shall be not greater than 60 inches. (1524 mm), and 
each bollard shall 
be located not less than 6 inches (152 mm) from the ESS.
1.3  Pre-manufactured steel pipe bollards shall be filled with concrete and 
anchored in accordance 
with the manufacturer's installation instructions, with spacing not greater 
than a 60 inches. (1524 
mm). Located not less than 6 inches (152mm) from the ESS.
















Hi Wrenches,

 

The 2023 IRC has been modified with some code that I helped create.

 

Here is a link that has a pretty recent draft of this code. This code (with 
slight edits) has been adopted by the ICC and will become code January 1 2023.  
See page 486.

 

https://www.iccsafe.org/wp-content/uploads/IFC-2021-Group-A-2021-Group-A-Aug-13.pdf

 

 

 

With Regard,

Vince Jolissaint

Cobalt Power Systems Inc. | Director of CAD Services
2557 Wyandotte St.  | Mountain View CA  94043
Office:  <tel:650.938.9574> 650.938.9574 | E-Mail  
<mailto:vince...@cobaltpower.com> vince...@cobaltpower.com

 

 


Message: 1
Date: Tue, 29 Mar 2022 09:15:23 -0500
From: <scot.a...@solarcentex.com <mailto:scot.a...@solarcentex.com> >
To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org 
<mailto:re-wrenches@lists.re-wrenches.org> >
Subject: [RE-wrenches] IRC 328 and ESS...approved barriers and
        "subject to" damage
Message-ID: <04e301d84377$6e935c30$4bba1490$@solarcentex.com 
<http://solarcentex.com> >
Content-Type: text/plain; charset="us-ascii"

Good morning, Wrenches.



We all discuss the NEC when it comes to ESS but the section in International
Residential Code (IRC) R328 is something to look at carefully. 



Easy to miss is the requirement to extend fire alarm systems to garage
spaces where we quite often install the ESS.

But the section in R328.8 Protection from impact is what worries me as it is
so open ended. Here is what I wrote to a city inspector:

"I'd like to review this open-ended section of R328 and how you interpret
it, please.



We intend to mount the ESS within an attached garage but we position so as
to prevent damage from vehicles coming into their normal parking space.
Having said that, a vehicle that moved five further feet forward might in
fact run into an ESS. So do you read "subject to" as in normal, due course
or do you consider the very worst scenario / accident?

And what approved barriers have you seen that comply to your satisfaction in
xxxxx."



What do you all do for R328?




_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to