Today I installed 3 of the MN
POWERFLO 5 batteries with an OBVFX3648
Per the battery label I was able to set the inverter LBCO to 46 vdc.
I see that the battery BMS range
Is 44.8-58 vdc
We should be good to go.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose
Wrenches
Signature Solar has no absorb time recommendation for their rack mount EG4s !
I’m setting up a system with a 1200 ah battery stack. Six in parallel.
What would be a good absorption time? No battery comms to CCs
5925 wPV
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc
They did call me back from a message left a week prior.
Also emailed me with a case # and response.
I’m waiting for a response back.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On
We Installed the automatic transfer switch so the inverter AC input could be
either grid or generator.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Oct 24, 2024, at 10:41 AM, Wi
Generac Eco Gen
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Oct 23, 2024, at 9:06 PM, Jerry Shafer via RE-wrenches
wrote:
What gen set are you using
Fun times
On Wed, O
ff list if necessary
Jeremy Rodriguez
All Solar Inc.
Penrose, CO
719-276-4954
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email addr
If anyone knows of a source for the DC negative and positive bus bars for an
8048A with GSLC, please advise.
TGIF!
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Tech support picked up the phone within 2 minutes today.
The tech I spoke with has been with OB for ten years , as I recall
He said they are building up “ the team”
Seems like tech support will be there , but I’m not sure about the product lines
Jeremy Rodriguez
Solar Installation / Design
All
ISO a refurbished inverter for a Bergey Excel Inverter, or a source for a
different manufacturer of an inverter that would work.
Contact me off list if needed.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorr
Greetings,
Whose using the new Discover
Rack mounted batteries?
They look like the EG4 line up
Pros and Cons ?
Thanks
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
We installed 5 or 6 in Colorado.
I know of 3 still operating
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On May 29, 2024, at 6:45 PM, John Blittersdorf via RE-wrenches
wrote:
T
Looking for an SB3.8-1SP-US-41 if anyone has one please contact me off list
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsor
Has anyone had issues with Tigo TS4AF rapid shut down devices along with their
transmitter, causing arc fault codes with a Fronius Primo inverter?
Fronius tells me I need to use AP smart devices. Hmmm.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado
With news that PLP has dropped the TPM line, what are you all recommending for
a good mount for up to 8 modules , 400 w range.
I looked in the archives, but no luck.
I thought there was someone formerly at DPW that was making them.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc
, inverter shuts OFF, no PV to re
charge back to LBCI, no generator backup to recharge batteries.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
What are you wrenches that used to install the SB-41 units sourcing now?
Looks like there is a new model on their website
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Has anyone experienced a grid tie inverter back feed a whole house backup
generator after a utility outage?
What can happen ?
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Wrenches
Has anyone confirmed which AFCI, combo GF/ CAFI , or GF only circuit breaker
brand names work with the PAE series inverter?
The leviton combos seems to freak out!
Regards ,
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by
The manufacturer from china.
Terravolt does offer tech support for the product.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Aug 30, 2023, at 13:38, Dave Angelini Offgrid Solar v
I’m working with the manufacturer to get a replacement, as these are two year
old batteries.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Aug 29, 2023, at 21:14, Jerry Shafer
Leaking from somewhere mid way in the battery case I’m guessing.
The liquid followed a cable down to the BMS board and corroded it badly.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand
If anyone has had issues with the Iron Edison lithiums leaking, please contact
me off list
But , feel free to comment here if needed.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Is it correct to size an PV array to provide .5C for a Lithium Iron bank?
130Ah x .5 = 65
65A = ~ 3.5kw PV DC
Seems overkill for one battery.
Any advice is appreciated.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy
I’ve got a customer with a Pika still
running, maybe three customers, actually… 😎
The one client made his own brush holder !
If that’s what you need, I can get you in contact with him.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by
group had
me make up a cable to hook up a computer to the battery to re - set the BMS I
believe.
I’m scheduled with a new tech support channel for Iron Edison to take this on.
Has anyone done this before , and is it really going to do any good ?
Jeremy Rodriguez
Solar Installation
Oops.
I will not post on the forum about this any longer.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On May 1, 2023, at 3:17 PM, Jeremy Rodriguez wrote:
Okay.
I’d be interested
Okay.
I’d be interested in at least 2 qty.
What’s a price on them? Model # ?
We’d need them shipped to us in Colorado.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On May 1, 2023,
If anyone has a model # NE170-U1 Or similar size / wattage 72 cell
modules laying around in good condition please contact me off the list
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
hello does anyone know of a source for service rated line side piercing
connectors? 200A rated
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Thermal Wrenches,
can someone recommend a supplier for pre-coiled stainless or copper tube heat
exchangers?
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Can someone possibly send me a few pictures of installs on a tile roof with
tiles removed where the mods would go, and asphalt shingles or similar
installed under the mods?
We have a client that is wanting to see how this could look
Please email me off list, if so
Jeremy Rodriguez
Solar
for maintenance by qualified persons.
Non-load-break bolted or plug-in disconnects shall be permitted.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Jan 28, 2023, at 7:28 AM, Christ
I believe midnite still has the remote trip DC PNL mount breakers, but of
course, no birdhouse to make it work.
Not sure what the trip trigger needs either as far as voltage.
-MNEDC250RT
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by
Now that there has been some time since the non WLAN units came out, does
anyone have recommendations for a good WiFi extender to utilize?
Is it OK to use the onboard USB port to power one. I’ve seen the white paper
on this set up but have yet to try it.
Jeremy Rodriguez
Solar
Is the Lynx II gateway required for battery to battery comms?
Model 42-48-6650
We will be installing with an inverter that cannot communicate.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typo
input
Sell disabled
Grid Support disabled
There is no TOU metering.
Regards,
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsor
The PIKA turbines are long gone and there are likely no parts available
anywhere.
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> On Dec 6, 2022, at 3:02 PM, Rich Nicol via RE-
Can anyone recommend the best Wi-Fi repeater to use with the new Sunny boys’
that do not have Wi-Fi capability?
Mr. Mahon?
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St.
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Can anyone recommend a reliable AGS module that works well with the EVO series
inverters?
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
We’ve ordered one to try since we cannot get the PAEs.
I hope Magnum can resume shipping orders in the 38 weeks I was told!
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On J
Does anyone have a source these days for Magnum Energy Inverters?
Contact me off list if needed.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
I’d look at the Simpliphi brand
We’ve had good luck, however they were smaller in size at 3.8KW
Perhaps they make a larger battery for your needs.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typo
Hello
Does anyone have a solution for adding a second inverter to an single flex
power pre wired panel, to achieve 120/240V ?
I know it wouldn’t be on the same panel, but looking for an option here.
Regards,
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose
Hello
Does anyone have a good used 250A CB for the old DC250 by Xantrex? I believe
they are a GJ250?
Or does any of the new equipment work. Kind of looks like the Magnum Energy
breakers in a MMP.
Contact me off list If necessary.
Regards,
[cid:01CF3FE4-AB99-4225-AEC0-0BE703F2658B]
Jeremy
Does anyone have a solution for operating a remote trip MN battery breaker
since the BDM is gone?
We do have a birdhouse, so maybe someone has a BDM, but otherwise,
what to do?
Batteries in a dwelling
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose
Michael
If we can find new old stock of a roof top comm kit, would it work with the
Inverter?
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Mar 18, 2022, at 12:11 PM,
interface board.
Can someone clarify if the CCA + Gateway are needed, or can I use the GIB to
get the gateway communication established.
Thanks in advance !
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typo
Just a rated disco at the ground mount? Labeled as the rapid shutdown switch?
That’s too simple!
In
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Feb 1, 2022, at 6:49 PM,
What about the PV circuits that leave the combiner and are ran on or in a
building to the CC
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Feb 1, 2022, at 4:07 PM, Brian Me
So the issue ended up being , as far as we can tell at this point , a loose
neutral connection at the first load distribution panel feeding all loads after
the inverter.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's i
the mains panel.
4448 PAE with one string of 6CS21P Batteries.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
___
List sponsored by Redwood All
If anyone has any leftover stock of the midnite MNPV4HV-DISCO3R-DLX-PSB
combiner, please contact me off list.
Regards,
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Iron Edison RE Volt 10.2
Battery Amp Hours - 600
Charged Voltage - 56 VDC
Charge return amps- 30A
Time- 6 minutes
Charge Factor- 99%
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand
. Happy holidays
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Redwood Alliance
Pay optional member dues here: http
nce.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wren
clear when I checked cells. 1.265- 1.275
No residue on the caps
I did note that all the positive Posts have “grown” and cause the case to start
cracking slightly around the post.
I’ve seen this a lot with Deka.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose
when I checked cells. 1.265- 1.275
No residue on the caps
I did note that all the positive Posts have “grown” and cause the case to start
cracking slightly around the post.
I’ve seen this a lot with Deka.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado
Steve,
Do you measure voltage of each battery with them disconnected or as is.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Jul 21, 2021, at 8:59 AM, Steve Higgins
Okay
Is there a quick way to run on just one string? Or should I say determine which
batteries would make a good string.
I’d normally say, find the best batteries based on specific gravity and use
them, but in this case all specific gravity‘s seem good.
Jeremy Rodriguez
Solar Installation
Deka 8L16
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Jul 21, 2021, at 8:24 AM, Jay wrote:
And what color is the electrolyte?
On Jul 21, 2021, at 8:02 AM, Jay wrote:
cell here.
What else can be checked , battery wise?
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Redwood Alliance
Wrenches
Anyone with experience in design of evac tube systems with atmospheric tanks,
can you please contact me off list? I need some advice / schematics for heat
dissipation strategies.
Regards,
Jeremy Rodriguez
Solar Installation / Design
All Solar, Inc.
1453 M St
Penrose Colorado 81240
pulling from a cistern and is a 115V unit. Not sure of the
pressure tank size or pump hp rating.
•ME 4448 PAE with one string of ~500 AH battery cap.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typo
Spaghetti walk pad.
https://www.bestmaterials.com/detail.aspx?ID=18959
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Mar 8, 2021, at 4:02 PM, Jeremy Coxon wrote:
We inst
We’ve had good luck with thread cutting screws. Found some 3/8“ diameter that
worked good with the LFeet and butyl tape. Need to pre drill the perlin.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for
Does anyone have any trick to adjusting the tilt angle of the TPM4 pole mounts?
These are the racks with the aluminum beam (strongback) with slots for the
bolts.
We have tried anti seize, and cutting the heads of the bolts square in attempts
to help with adjustment.
Help!
Jeremy Rodriguez
This is for a PIKA wind turbine.
We have since been in contact with that support group at Generac.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Sep 29, 2020, at 7:27 AM,
If anyone has any info on how to get a hold of The former PIKA ENERGY support
group, please contact me off list.
Or if anyone knows where one could get one of their inverters rebuilt/repaired
let me know.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose
Please contact me off list if you have 2 or 3 CS6P 200P mods.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Re
Hello
Does anyone know if the SMA ROOFTOP COMMUNICATION KIT
works with the new -41 inverters?
Regards ,
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Hello
Can you recommend a distributor for a Radian inverter bypass kit?
Our usual no longer sells.What?
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
The hotter it is the better. I like it as it softens up and I think it’s Safe
to 30 degrees.
We have only used it on asphalt.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On
Hello,
Has anyone been in touch with Xzeres Wind Power lately?
Their phone number seems to lead to a empty cubical.
I’ve got a client in So CO in need of help with his 10kw turbine/ SMA Windy Boy
inverter set up.
If anyone has experience with these, contact me off list.
TIA,
Jeremy Rodriguez
Pre cut the rails at ground level with your circular saw.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Jun 12, 2019, at 11:32 PM, frenergy
mailto:frene...@psln.com>>
You should check with your electrical supplier.
We have sourced some weebs and I recall they were burndy
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
On Apr 9, 2019, at 6:06 PM,
Is it ok to extend the battery temp sensor wire for a classic controller?
Length might be around 25 ft max. Original is 15ft.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
I have been reading Outbacks AC coupling note.
It refers to using only a single Radian Inverter.
Is it possible to duplicate the equipment if more PV is installed, and use two
Radians, with their outputs paralleled to the critical loads panel?
I see it recommends 6Kw of PV with an 8048 Radian
Jer
I’m in need of two Solar World SW275. BOB modules.
Please contact me off list if you have any.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
We’ve installed 5 of them. Good machine, and they were worth the extensive lead
times. Pika is not focused on their turbine any more, and I’ve been told they
will not produce any more, unless they have a large project to fulfill.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar
stage quickly, BTW.
Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lis
We’ve installed many Midnite BHs with the disconnecting combiners (and battery
disco modules pre 2017 NEC.)
Recently we set up a roof mounted array with the disconnecting HV combiner
along with the SOB for the PV Side of the CC. Worked well.
I’d be interested in the OB gear as well.
Jeremy
I’ve done a quick search of the archives, but does anyone know of the the
effects of an EMP PULSE on a module? We’ve got a potentially large project to
look forward to, and one developer is very concerned
Jeremy Rodriguez
Solar installation / Design Expert
All Solar, Inc.
1463 M St
Penrose
Wrenches,
We have a client with a string of sealed L16s and he believes he may have a
weak or failed cell.
What’s the best way to test or check these batteries, since there is no
electrolyte to draw out.
We don’t install many AGMs, in fact, steer the client away from them, usually.
Jeremy
Have you tried updating the inverter via an SD card.
SMA tech support emailed me a link.
We had a similar problem but don't think it had anything to do with the RSB,
though this one used the remote switch, so I'm not sure if it's the same RSB
you refer to.
Jeremy R
Does anyone have a contact at Photowatt (France)?
Looking for possible warranty coverage.
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Does anyone have a dealer only phone number to reach SolarEdge tech support?
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
___
Me too !
but DPW wants the horizontal hole to hole spacing as if the module is in
portrait mode.
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> On Aug 23, 2017, at
I have seen all the spec sheets. I need the horizontal, hole to hole
dimensions.
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> On Aug 21, 2017, at 8:01 PM, Exeltec
Hello
Does anyone happen to have access to a HIT210N module they could measure?
I'm in need of the mounting hole dims. See below.
[page1image480]
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for
If Anyone has some Suntech STP-200-220/18 modules (3)
Please contact me off list.
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Hello,
I have a potential client needed some help with an Apollo charge controller. If
anyone has a current phone number I'd appreciate it.
Jeremy Rodriguez
Solar Installation And
Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for
How about Midnite din mount 150vdc breakers. 1-63 amp range.
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
On May 24, 2017, at 11:59 AM, Drake
mailto:drake.ch
Opps. I mean Fronius !
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
> On Apr 11, 2017, at 7:37 PM, Jeremy Rodriguez wrote:
>
> Hello
> I'm reaching ou
Hello
I'm reaching out to an SMA rep on the list to contact me off list.
I have a client in need of a hard copy of the operators manual for his new
Galvo 3.1 inverter.
Missing in the box.
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado
Anyone have any Poly CSIs in the 250-260w range? Looking for three.
please contact me off list.
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
If anyone has a hub 4 wire cover, with no pieces cut out, please contact me off
list.
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
Do you if the wiring from the E panel will reach with the AC conduit box in
place on the FX?
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
On Aug 27, 2016, at 10:02 PM
This is for an existing system. They are wanting to install the outback product
on FXs installed with E panels
They currently have Midnite arrestors. I know!
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone.
the sides of the OB ACA vs. where
they originally land.
Any thoughts or experiences would be appreciated!
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shor
How about these?
https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typo