[RE-wrenches] Imax disturbance Error

2022-01-09 Thread Mac Lewis
Hello Wrenches,

I've got a customer that has an issue with their ~10 yr old SB8000US
connected to a quad stack of Sunny Island system that's off-grid.

It looks like it's on and off, trying to make power but seems to think
there is a problem on the AC side.  Do you have any advice as to what may
be going on?  Anything that I can do that may not require replacement?
Very tough communicating to SMA while on site and of course, this always
happens on Friday night.

Thanks!

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Marco Mangelsdorf
Hey Mac,

It’s been my experience over the years that the Imax failure is fatal.

marco

On Sunday, January 9, 2022, Mac Lewis  wrote:

> Hello Wrenches,
>
> I've got a customer that has an issue with their ~10 yr old SB8000US
> connected to a quad stack of Sunny Island system that's off-grid.
>
> It looks like it's on and off, trying to make power but seems to think
> there is a problem on the AC side.  Do you have any advice as to what may
> be going on?  Anything that I can do that may not require replacement?
> Very tough communicating to SMA while on site and of course, this always
> happens on Friday night.
>
> Thanks!
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Jeremy Rodriguez


Hello
we have a lot of PAE series magnum inverters out there.
One client lately has been experiencing voltage drop and failure of PCBs in two 
of his household appliances.  I know it’s common to have some dimming of the 
lights when a well pump or other large load kicks on, but has anyone ran across 
a solution to alleviate the problem or boost up the voltage / condition it, in 
any way ?
I’m not sure if this just happens with low battery voltage, or always
The inverter is located ~ 300 ft from the main electrical panel with #2/2/2/4 
URD feeders to an outdoor disco, then 8 AWG copper to the mains panel.
4448 PAE with one string of 6CS21P Batteries.


Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado


Sent by Jeremy's iPhone. Sorry for typos and shorthand!
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Garrison
I was troubleshooting a site on Friday with the same Imax error on the same 
SB8000 inverter. Took the cover off and found a cracked capacitor. 

Inverter was manufactured 12/2021 and SMA is telling me it’s out of warranty 
(by a week). I’m
trying to appeal to their humanity. 

Good luck!

Garrison Riegel
Celestar Solar

> On Jan 9, 2022, at 11:55 AM, Marco Mangelsdorf  wrote:
> 
> Hey Mac,
> 
> It’s been my experience over the years that the Imax failure is fatal.
> 
> marco 
> 
>> On Sunday, January 9, 2022, Mac Lewis  wrote:
>> Hello Wrenches,
>> 
>> I've got a customer that has an issue with their ~10 yr old SB8000US 
>> connected to a quad stack of Sunny Island system that's off-grid.
>> 
>> It looks like it's on and off, trying to make power but seems to think there 
>> is a problem on the AC side.  Do you have any advice as to what may be going 
>> on?  Anything that I can do that may not require replacement?  Very tough 
>> communicating to SMA while on site and of course, this always happens on 
>> Friday night.
>> 
>> Thanks!
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Carl Adams
Mac,

SMA tech support told me this usually indicates a failing transformer so as
Marco suggests, the patient does not have long to live.  I've seen a couple
of these at 10+ years of service on the inverter.

Was kind of regards
Carl Adams
SunRock Solar

On Sun, Jan 9, 2022, 12:50 PM Mac Lewis  wrote:

> Hello Wrenches,
>
> I've got a customer that has an issue with their ~10 yr old SB8000US
> connected to a quad stack of Sunny Island system that's off-grid.
>
> It looks like it's on and off, trying to make power but seems to think
> there is a problem on the AC side.  Do you have any advice as to what may
> be going on?  Anything that I can do that may not require replacement?
> Very tough communicating to SMA while on site and of course, this always
> happens on Friday night.
>
> Thanks!
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Jerry Shafer
I would look at connections first, lug that is not as tight as it ne we do
to be, a breaker failing, outlets that are either push in wires or have
loose connections. Eliminate what you can before looking at the inverters

On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez 
wrote:

>
>
> Hello
> we have a lot of PAE series magnum inverters out there.
> One client lately has been experiencing voltage drop and failure of PCBs
> in two of his household appliances.  I know it’s common to have some
> dimming of the lights when a well pump or other large load kicks on, but
> has anyone ran across a solution to alleviate the problem or boost up the
> voltage / condition it, in any way ?
> I’m not sure if this just happens with low battery voltage, or always
> The inverter is located ~ 300 ft from the main electrical panel with
> #2/2/2/4 URD feeders to an outdoor disco, then 8 AWG copper to the mains
> panel.
> 4448 PAE with one string of 6CS21P Batteries.
>
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado
>
>
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand!
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Imax disturbance Error

2022-01-09 Thread Ray

AC coupled off grid?  Sounds like a good time to go DC coupled.

Ray Walters
Remote Solar
303 505-8760

On 1/9/22 3:31 PM, Carl Adams wrote:

Mac,

SMA tech support told me this usually indicates a failing transformer 
so as Marco suggests, the patient does not have long to live.  I've 
seen a couple of these at 10+ years of service on the inverter.


Was kind of regards
Carl Adams
SunRock Solar

On Sun, Jan 9, 2022, 12:50 PM Mac Lewis  wrote:

Hello Wrenches,

I've got a customer that has an issue with their ~10 yr old
SB8000US connected to a quad stack of Sunny Island system
that's off-grid.

It looks like it's on and off, trying to make power but seems to
think there is a problem on the AC side. Do you have any advice as
to what may be going on? Anything that I can do that may not
require replacement?  Very tough communicating to SMA while on
site and of course, this always happens on Friday night.

Thanks!

-- 




Mac Lewis

*

"Yo solo sé que no sé nada." -Sócrates

*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] PAE series surge capacity/ power factor ?

2022-01-09 Thread Ray
Long runs of URD direct buried?  Just a nick into the metal can corrode 
the cable all the way through over time.  We use conduit for almost 
everything anymore.  The savings with URD doesn't pan out, when you have 
to abandon the line after 10 years.


Ray Walters
Remote Solar
303 505-8760

On 1/9/22 5:10 PM, Jerry Shafer wrote:
I would look at connections first, lug that is not as tight as it ne 
we do to be, a breaker failing, outlets that are either push in wires 
or have loose connections. Eliminate what you can before looking at 
the inverters


On Sun, Jan 9, 2022, 11:36 AM Jeremy Rodriguez 
 wrote:





Hello
we have a lot of PAE series magnum inverters out there.
One client lately has been experiencing voltage drop and failure
of PCBs in two of his household appliances.  I know it’s common
to have some dimming of the lights when a well pump or other
large load kicks on, but has anyone ran across a solution to
alleviate the problem or boost up the voltage / condition it, in
any way ?
I’m not sure if this just happens with low battery voltage, or
always
The inverter is located ~ 300 ft from the main electrical panel
with #2/2/2/4 URD feeders to an outdoor disco, then 8 AWG copper
to the mains panel.
4448 PAE with one string of 6CS21P Batteries.



Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado



Sent by Jeremy's iPhone. Sorry for typos and shorthand!

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org