I dealt with this on my "last" GTBB system.  I say last, because I only do backup systems now in places like Puerto Rico that actually need backup.  The FXRs will NOT connect to even an inverter generator (Yamaha EF3000), unless they are programmed to GEN.  Our solution was to save two different system profiles on the Mate, and the customer, after actuating the transfer switch was to switch to the other profile on the Mate.  Power reliability before GTBB:  99.9%,  Power Reliability after GTBB was installed: 80%.

The FXRs had firmware problems that caused one inverter (and half the backup loads) to shut off when trying to sell back. Outback Tech support blamed me for the problems, and only after several months of shut downs, did they acknowledge that their firmware was actually the issue.  Customer spent $30k+ for less reliability.

Magnum going away?  Probably a good thing too, since I had my first out of the box failure this Spring, after an almost perfect record over the past 15 years.  Customer was on generator power for over 2 months waiting for the replacement.  My whole career has been marked with great companies being sold, only to see them later drown in a cesspool of mediocre products and poor tech support.

Ray Walters
Remote Solar

On 10/24/2024 5:55 PM, Bradley Bassett via RE-wrenches wrote:
As I remember the FXR inverters will rarely connect to any generators beside very well controlled or inverter type generators. I agree that I don't think there is any automatic transfer from grid tie to generator input.

Brad Bassett

On Thu, Oct 24, 2024 at 3:42 PM Wayne Irwin via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    It is my understanding that the FXR will not "automatically"
    switch from Grid Input to Gen.
    To my knowledge this is a manual option only.
    I do not recall any way to make this happen automatically. That
    would have been great.

    You can however still call for the generator at a low V setting
    and have the generator power an external charger to boost the
    batteries.
    I think the brand we used to use was IOTA however, I have also
    seen golf cart chargers used.


    Wayne Irwin
    President
    License #CVC56695
    State Licensed Solar Contractor
    Pure Energy Solar International Inc.
    wa...@pureenergysolar.com
    PureEnergySolar.com <http://pureenergysolar.com/>
    SolarChargingStation.com <http://solarchargingstation.com/>
    352 377-6527 Office
    352 336-3299 Fax


    The Sun Is Always Shining!

    The content of this message is Pure Energy Solar Confidential. If
    you are not the intended recipient and have received this message
    in error, any use or distribution is prohibited. Please notify me
    immediately by reply e-mail and delete this message from your
    computer system. Thank you.

    ------------------------------------------------------------------------
    *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on
    behalf of Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org>
    *Sent:* Thursday, October 24, 2024 5:57 PM
    *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
    *Cc:* Jay <jay.pe...@gmail.com>
    *Subject:* Re: [RE-wrenches] New Outback FXR Series as GTGBB on
    existing Off Grid Home
    Hi Jeremy

    There are two issues I think.

    1 is that the inverter won’t connect.
    And I don’t have an answer why the inverter won’t in sell mode but
    will in gen mode. Maybe the generator is slightly out of the more
    narrow window for grid. I presume you’ve checked hz and volts and
    they are in spec for grid?  I know sometimes the frequency control
    can be slightly variable without a load. I’ve had success in the
    past getting inverters to connect to a generator with putting some
    dumb loads on it. Like incandescent lights or small heater.

    2. Maybe it’s a good thing it won’t because if it did connect
    wouldn’t it be possible for the inverter to try to sell to the
    generator?  If you didn’t have to change grid to Gen?

    Jay

    On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches
    <re-wrenches@lists.re-wrenches.org> wrote:

    
    Wrenches,
    We have a client that has brought utility power in and we now
    have the system hooked up to the utility.
    In setting the system up, I've experienced that the inverter will
    sell and function fine with all the settings set up as* Grid
    Tied* mode, but it does not play nice when the grid is gone , and
    the Generator is brought in as the AC source.
    We have installed an external transfer switch to switch the
    inverters' AC input, from either the utility or the existing
    backup generator ( if the grid fails), automatically.

    The manual states that the inverter's two input selections can be
    programmed for seperate input modes, via the* Input* *Type* menu.
    Ive not been able to get this accomplished.

    When simulating a grid outage, thus changing the AC input to the
    inverter being from the Generator, the inverter will not synch to
    the AC power to charge the batteries.
    The only way that I can get the inverter to synch, is to switch
    the input mode to *GEN* from *GRID.*
    This is not ideal since the client would need to be present to
    make the button push, even though the generator will be started
    automatically if the grid were to go down (hopefully) , just as
    it did before.
    With no way to contact Outback , can someone advise how to
    properly program the inverter/ MATE3S for this project?
    Equipment onsite:
    Single VFXR3648 inverter
    Two FM60 CCs
    Hub4
    MATE3S
    ATS with Dual Relays 50A
    L.A. Battery bank

    Here's how we would like it to work:
    Utility power ON:
    Sell excess power once the batteries have gone through the Absorb
    cycle. Batteries remain full in case of a utility failure.
    Utility Outage:
    ATS now feeds Inv AC input via Generator if needed.
    Inverter runs the home as it did , off grid.
    If the battery voltage drops and the AGS is engaged, the inverter
    will use that input to charge the batteries as usual.  If the
    grid comes back on and the gen is running, the generator can
    still run, with no connection to the inverter. With the grid now
    charging the battery bank, and the AGS will enventually shut off
    the Gen. Based on voltage.
    Contact me off list if necessary


    Jeremy Rodriguez
    All Solar Inc.
    Penrose, CO
    719-276-4954



    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to