What gen set are you using
Fun times

On Wed, Oct 23, 2024, 7:47 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Wrenches,
> We have a client that has brought utility power in and we now have the
> system hooked up to the utility.
> In setting the system up, I've experienced that the inverter will sell and
> function fine with all the settings set up as* Grid Tied* mode, but it
> does not play nice when the grid is gone , and the Generator is brought in
> as the AC source.
> We have installed an external transfer switch to switch the inverters' AC
> input, from either the utility or the existing backup generator ( if the
> grid fails), automatically.
>
> The manual states that the inverter's two input selections can be
> programmed for seperate input modes, via the* Input* *Type* menu. Ive not
> been able to get this accomplished.
>
> When simulating a grid outage, thus changing the AC input to the inverter
> being from the Generator, the inverter will not synch to the AC power to
> charge the batteries.
> The only way that I can get the inverter to synch, is to switch the input
> mode to *GEN* from *GRID.*
> This is not ideal since the client would need to be present to make the
> button push, even though the generator will be started automatically if the
> grid were to go down (hopefully) , just as it did before.
>
> With no way to contact Outback , can someone advise how to properly
> program the inverter/ MATE3S for this project?
> Equipment onsite:
> Single VFXR3648 inverter
> Two FM60 CCs
> Hub4
> MATE3S
> ATS with Dual Relays 50A
> L.A. Battery bank
>
> Here's how we would like it to work:
> Utility power ON:
> Sell excess power once the batteries have gone through the Absorb cycle.
> Batteries remain full in case of a utility failure.
> Utility Outage:
> ATS now feeds Inv AC input via Generator if needed.
> Inverter runs the home as it did , off grid.
> If the battery voltage drops and the AGS is engaged, the inverter will use
> that input to charge the batteries as usual.  If the grid comes back on and
> the gen is running, the generator can still run, with no connection to the
> inverter.  With the grid now charging the battery bank, and the AGS will
> enventually shut off the Gen. Based on voltage.
> Contact me off list if necessary
>
>
> Jeremy Rodriguez
> All Solar Inc.
> Penrose, CO
> 719-276-4954
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to