Hi Jason

Any chance for some photos?

Jay

> On Nov 18, 2020, at 12:18 PM, Jason Szumlanski 
> <ja...@floridasolardesigngroup.com> wrote:
> 
> 
> The plot thickens on the fuse blowing issue. Again, we tore the Enphase IQ 
> system apart looking for any reason for the fuse to keep blowing. We 
> reconfirmed torque on all line side conductors to the service (supply side 
> interconnection using Polaris taps).
> 
> Low and behold, I get a second client with the exact same issue yesterday. 
> The circumstances are eerily alike. Both disconnects are located on the west 
> side of the house and have 36 IQ7+ microinverters on an IQ Combiner, 
> requiring 60A fuses on the 60A fusible disconnect. The combined inverter 
> output rating is 43.56A. The interconnections are identical with #6 THHN 90ºC 
> conductors and Polaris taps. Both disconnects have conductors on the 
> right-hand side line-side terminal that are discolored (the copper is 
> silvery, the insulation is not burned). The fuses blow at peak current around 
> 1:30 pm, only on bright and sunny days.
> 
> I'm starting to suspect a faulty fusible disconnect switch. Maybe the blades 
> are not making proper contact with the line side terminals.
> 
> For the client who is having regular/frequent fuses blowing I plan to replace 
> the disconnect with a heavy-duty version or possibly get a 100A disconnect 
> with fuse reducers. I'm not sure which option would yield a better test. I 
> might also switch brands.
> 
> Currently, we are using GE TG3222R. The fuses are Bussman FRN-R Time Delay. I 
> have to believe a heavy-duty switch would be less susceptible to this, but 
> maybe a higher rated one would be a better option. I'm not a fan of fuse 
> reducers, however. 
> 
> Jason Szumlanski
> Florida Solar Design Group
> 
> 
>> On Sun, Aug 30, 2020 at 5:54 PM Jason Szumlanski 
>> <ja...@floridasolardesigngroup.com> wrote:
>> The tripping breaker occurred at random times, even at night. No 
>> weather-related correlation.
>> 
>> I have more research to do to see when this fuse issue is happening, but 
>> previous visits showed no water ingress. I'm not sure about temperature.
>> 
>> 
>> 
>> 
>>> On Thu, Aug 27, 2020 at 8:51 PM Jay <jay.pe...@gmail.com> wrote:
>>> Hi Jason
>>> 
>>> One thought I have about the blowing fuse is to check it with a IR tool. 
>>> 
>>> I suspect a poor connection of the fuse to holder which during higher air 
>>> temp is causing it to fail.  
>>> I’m assuming that the correct amp size and slow blow fuse Is installed and 
>>> that the wire connections are done correctly. But again an IR tool during 
>>> peak heat would be  a good test. 
>>> 
>>> About the enphase fix, wow what a head scratcher. But given that it’s fixed 
>>> it means that it’s not a short, but enough amps going through over enough 
>>> time to trip it. I wonder if a magnetic hydraulic vs thermal breaker ( CBI  
>>> vs CH etc) would have worked?
>>> 
>>> Is that breaker box ever in the sun?  Is there any Correlation between  
>>> high ambient temperatures and tripping?  
>>> 
>>> It sure would keep me up at night too 
>>> 
>>> Jay
>>> 
>>> 
>>>>> On Aug 27, 2020, at 4:29 PM, Jason Szumlanski 
>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>> 
>>>> 
>>>> So the resolution to this is in... But I still have no idea what was 
>>>> wrong. 
>>>> 
>>>> The string of 10 offending microinverters was split into 5 and 5. We had a 
>>>> spare breaker in the IQ Combiner so it was relatively easy to run another 
>>>> branch circuit. It has been over two months with no recurrence. So the 
>>>> issue seems to be resolved, but again, no idea why.
>>>> 
>>>> So here we go again... On another system we have a similar problem now. In 
>>>> this case it is supply side interconnected with a fusible disconnect. The 
>>>> same fuse (same line) keeps blowing every few to several weeks. We can't 
>>>> find any home run wiring issues or issues with terminator caps. There are 
>>>> no apparent faults in the AC Combiner. We have no idea why this is 
>>>> happening. But in this system, just the fuse blows, not one of the 
>>>> individual branch circuit breakers. 
>>>> 
>>>> This is getting very frustrating. And this is way more serious because 
>>>> fuses and service calls are expensive and I can't isolate the issue to one 
>>>> branch circuit. I don't even know where to start. Leaving each circuit 
>>>> disconnected for several weeks to prove a negative is an untenable 
>>>> suggestion to make to a client. But I don't see any other good options. 
>>>> 
>>>> Jason Szumlanski 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>>> On Tue, Jun 9, 2020, 3:42 PM Jason Szumlanski 
>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>> Yes, we double-checked that. I have seen that happen before and it's one 
>>>>> of my early diagnostic steps for something like this.
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Tue, Jun 9, 2020 at 9:18 AM Mac Lewis <maclew...@gmail.com> wrote:
>>>>>> Hi Jason,
>>>>>> 
>>>>>> Are you certain that the branch circuits aren't crisscrossed somewhere, 
>>>>>> meaning that an L1 branch 1, isn't connected to an L2 branch 2?  That 
>>>>>> could explain two different breakers tripping.  
>>>>>> 
>>>>>> Good luck
>>>>>> 
>>>>>> 
>>>>>>> On Wed, Jun 3, 2020 at 1:07 PM Jason Szumlanski 
>>>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>>>> Undoubtedly, the termination caps are the second thing we check after 
>>>>>>> the rooftop junction box(es). These are prone to installation errors, 
>>>>>>> even when the right parts are used. And given the cost, I've thought 
>>>>>>> very long and hard about abandoning them altogether and terminating 
>>>>>>> strings in small j-boxes with watertight fittings. But in this case, 
>>>>>>> there was no evidence of improper installation (we replaced them) and 
>>>>>>> it was not correlated to rain events.
>>>>>>> 
>>>>>>> We are well equipped with bare Q-cable and field wireables that we 
>>>>>>> could use for troubleshooting to bypass certain sections, but the 
>>>>>>> intermittent nature of the problem and unpredictable timeframe between 
>>>>>>> faults is very frustrating. While this is a rare occurrence, it is 
>>>>>>> definitely a "con" to consider when comparing string vs. microinverters 
>>>>>>> that I had not strongly considered in the past. I'm intent on getting 
>>>>>>> to the bottom of this in order to learn what to look for in the future 
>>>>>>> and how to approach diagnoses of Enphase branch circuit faults.
>>>>>>> 
>>>>>>> Jason
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>>> On Wed, Jun 3, 2020 at 2:31 PM Amos Post 
>>>>>>>> <integrityenergy...@gmail.com> wrote:
>>>>>>>> I was just at a site last week where the Enphase branch circuit 
>>>>>>>> breaker, outside utility disconnect breaker, and feed breaker in the 
>>>>>>>> main panel all tripped simultaneously, and it happened about 1 hour 
>>>>>>>> before I showed up onsite.  The customer said it had happened 1 other 
>>>>>>>> time last fall but that time it was just the 1 branch circuit in the 
>>>>>>>> Enphase combiner panel.  Interestingly the customer mentioned that he 
>>>>>>>> had just washed off the panels, also about 1 hour before I got there.  
>>>>>>>> I went on the roof and found that the installing contractor had not 
>>>>>>>> put on the Enphase termination caps.  1 string was wire-nutted with 
>>>>>>>> regular wire nuts and sitting on the roof, and the roof was damp right 
>>>>>>>> there. This was a fairly flat roof.  The other micro trunk cable was 
>>>>>>>> just cut with no protection at all, tied to the rail…
>>>>>>>> 
>>>>>>>> 
>>>>>>>> <IE LOGO 150x78.jpg>
>>>>>>>> 
>>>>>>>> 
>>>>>>>>        Amos Post
>>>>>>>>    Integrity Energy
>>>>>>>>   W 802.763.7023
>>>>>>>>    C 802.291.2188
>>>>>>>>     ienergyVT.com
>>>>>>>>         Facebook
>>>>>>>> 
>>>>>>>>> On Jun 3, 2020, at 2:05 PM, Jason Szumlanski 
>>>>>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>> 
>>>>>>>>> The breaker in the main panel IS tripping simultaneously with one of 
>>>>>>>>> the branch circuit breakers each time.
>>>>>>>>> 
>>>>>>>>> 
>>>>>>>>> 
>>>>>>>>> 
>>>>>>>>> 
>>>>>>>>> 
>>>>>>>>>> On Wed, Jun 3, 2020 at 12:43 PM Jay <jay.pe...@gmail.com> wrote:
>>>>>>>>>> A question that keeps nagging me is why do these breakers trip and 
>>>>>>>>>> not the breaker in the main panel?  
>>>>>>>>>> Presuming there is a 40 amp in the main
>>>>>>>>>> 
>>>>>>>>>> I would have thought that given all the times the breakers have 
>>>>>>>>>> tripped at some point that one would have tripped and I can’t 
>>>>>>>>>> understand why not?  
>>>>>>>>>> 
>>>>>>>>>> Jay 
>>>>>>>>>> 
>>>>>>>>>>>> On Jun 3, 2020, at 8:27 AM, Jerry Shafer 
>>>>>>>>>>>> <jerrysgarag...@gmail.com> wrote:
>>>>>>>>>>>> 
>>>>>>>>>>> 
>>>>>>>>>>> Wrenches
>>>>>>>>>>> Looking g at the bigger breaker tripping at the same time is very 
>>>>>>>>>>> likely do to response time of the breaker nothing more. As l 
>>>>>>>>>>> suggested in a previous message. Use a non bridged breaker to see 
>>>>>>>>>>> if it is one or both legs that trip. Also an eguage will help to 
>>>>>>>>>>> see what if anything leads up to the failure and when. 
>>>>>>>>>>> Jerry
>>>>>>>>>>> Jerry
>>>>>>>>>>> 
>>>>>>>>>>>> On Wed, Jun 3, 2020, 7:58 AM Jason Szumlanski 
>>>>>>>>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>>>> I wonder about that. Of course, it could be the "inverter output 
>>>>>>>>>>>> circuit" having a fault in the wiring still (an intermittent issue 
>>>>>>>>>>>> somewhere within the IQ cable or home run wiring). But internal to 
>>>>>>>>>>>> the microinverter, is it possible that a fault could still occur 
>>>>>>>>>>>> at night? I had a suggestion from another wrench that there are 
>>>>>>>>>>>> film capacitors on the AC output side, but are these isolated when 
>>>>>>>>>>>> there is no DC input? It seems unlikely that this would be an 
>>>>>>>>>>>> issue, but I have seen microinverters reporting a couple of watts 
>>>>>>>>>>>> at night (in Enlighten). I'm not sure how real that is.
>>>>>>>>>>>> 
>>>>>>>>>>>> The overriding question I have is what kind of fault would cause 
>>>>>>>>>>>> BOTH a branch circuit and the main solar breaker to trip 
>>>>>>>>>>>> simultaneously? That seems odd to me. If any normal load branch 
>>>>>>>>>>>> circuit has a fault, you don't often see premises main breakers 
>>>>>>>>>>>> tripping, or even feeder circuit breakers.
>>>>>>>>>>>> 
>>>>>>>>>>>> I got to thinking that maybe there is some kind of issue between 
>>>>>>>>>>>> the BR220 and CH240 breakers not playing nicely together. But I 
>>>>>>>>>>>> would think this would be a well-known issue because I'm sure 
>>>>>>>>>>>> there are tons of CH feeder breakers in the wild with BR branch 
>>>>>>>>>>>> circuits downstream. 
>>>>>>>>>>>> 
>>>>>>>>>>>> 
>>>>>>>>>>>> 
>>>>>>>>>>>>> On Tue, Jun 2, 2020 at 9:25 AM 
>>>>>>>>>>>>> <drake.chamber...@redwoodalliance.org> wrote:
>>>>>>>>>>>>> If it trips at night, we know it is not the output from the 
>>>>>>>>>>>>> inverters causing the tripping. The current must be coming from 
>>>>>>>>>>>>> the grid.
>>>>>>>>>>>>> 
>>>>>>>>>>>>> ---
>>>>>>>>>>>>>  
>>>>>>>>>>>>> 
>>>>>>>>>>>>> 
>>>>>>>>>>>>>> On 2020-06-01 12:05, Jason Szumlanski wrote:
>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>  
>>>>>>>>>>>>>> It's not weather. It's at all times of the day and night, and I 
>>>>>>>>>>>>>> confirmed that there is no correlation to rain or high winds. 
>>>>>>>>>>>>>> That was my first suspicion.
>>>>>>>>>>>>>>  
>>>>>>>>>>>>>> 
>>>>>>>>>>>>>> On Mon, Jun 1, 2020 at 10:27 AM Ray <r...@solarray.com> wrote:
>>>>>>>>>>>>>> Is it at all weather related?  Rain, or high humidity?  High 
>>>>>>>>>>>>>> temperatures?  Do you have any indication what time of day it 
>>>>>>>>>>>>>> trips off at?
>>>>>>>>>>>>>> 
>>>>>>>>>>>>>> Ray Walters
>>>>>>>>>>>>>> Remote Solar
>>>>>>>>>>>>>> 303 505-8760
>>>>>>>>>>>>>> On 6/1/20 10:23 AM, Jason Szumlanski wrote:
>>>>>>>>>>>>>>> Well, that didn't resolve it. The main breaker and a branch 
>>>>>>>>>>>>>>> circuit breaker tripped again a few days ago. It was the same 
>>>>>>>>>>>>>>> branch this time. 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> As my next diagnostic step I swapped two circuits (on which 
>>>>>>>>>>>>>>> breaker they are landed). If history is a guide, it will work 
>>>>>>>>>>>>>>> for about two weeks and then trip again.
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> I'm dumbfounded. I really don't want to have to tear this whole 
>>>>>>>>>>>>>>> system apart. At this point, if I have to remove all the 
>>>>>>>>>>>>>>> modules, I feel that I need to replace all of the trunk cable 
>>>>>>>>>>>>>>> which is an expensive proposition. I really don't know what 
>>>>>>>>>>>>>>> else to do at this point.
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> Jason
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>> On Mon, May 25, 2020, 10:43 AM Jason Szumlanski 
>>>>>>>>>>>>>>> <ja...@floridasolardesigngroup.com> wrote:
>>>>>>>>>>>>>>> I strongly suspect the CH240 combined breaker was compromised 
>>>>>>>>>>>>>>> (we will see). Since it happened that two different strings 
>>>>>>>>>>>>>>> tripped, I doubt I have two microinverters with internal 
>>>>>>>>>>>>>>> faults. It has to be the combined breaker. I was just surprised 
>>>>>>>>>>>>>>> that branch circuit breakers were tripping simultaneously with 
>>>>>>>>>>>>>>> the combined output breaker.
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> Of all the supply side connected systems I have installed, I 
>>>>>>>>>>>>>>> have never seen a combined output fusible disconnect fuse blow, 
>>>>>>>>>>>>>>> but I have seen many combined output breakers tripped. I was 
>>>>>>>>>>>>>>> worried early on that I would be replacing fuses constantly, 
>>>>>>>>>>>>>>> but that has not been an issue whatsoever.
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>>          
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>> On Thu, May 21, 2020 at 11:15 AM <scot.a...@solarcentex.com> 
>>>>>>>>>>>>>>> wrote:
>>>>>>>>>>>>>>> Actually, we had a IQ7 string loaded up to its max panel size 
>>>>>>>>>>>>>>> and max string length and in the spring on cool, clear day, it 
>>>>>>>>>>>>>>> tripped the string's associated breaker in the Enphase combiner.
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> We reset but of course that breaker was impaired and it tripped 
>>>>>>>>>>>>>>> again. We replaced and never had an issue going forward. We 
>>>>>>>>>>>>>>> suspect the breaker was less than perfect from the start as 
>>>>>>>>>>>>>>> we've add equally nice days since.
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> This almost reminds me of loading up Outback FM80. It says 
>>>>>>>>>>>>>>> 4,000 watts but in reality, 3,600 is the max when amps spike. I 
>>>>>>>>>>>>>>> will be extra careful going forward on IQ7 string length when 
>>>>>>>>>>>>>>> going to the max published...
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> My story.
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> Scot
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> 
>>>>>>>>>>>>>>> On Behalf Of Jason Szumlanski
>>>>>>>>>>>>>>> Sent: Thursday, May 21, 2020 8:57 AM
>>>>>>>>>>>>>>> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
>>>>>>>>>>>>>>> Subject: [RE-wrenches] Enphase intermittent breaker trippjng
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> I'm trying to resolve an intermittent frustrating problem with 
>>>>>>>>>>>>>>> and Enphase IQ system. There are three AC Branch circuits of 9 
>>>>>>>>>>>>>>> microinverters each coming into an Enphase AC combiner. 
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> What has been happening is one of the BR220 branch circuit 
>>>>>>>>>>>>>>> breakers and the combine CH240 breaker in the main backfed load 
>>>>>>>>>>>>>>> center have been tripping simultaneously. It has happened about 
>>>>>>>>>>>>>>> four times in the last 6 months. It was always the same branch 
>>>>>>>>>>>>>>> circuit breaker, so we kept investigating that string, checking 
>>>>>>>>>>>>>>> the junction box, trunk cable, and cap, etc. Finally we swapped 
>>>>>>>>>>>>>>> out the BR220 breaker. 
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> Fast forward 4 weeks, and we got another call. This time a 
>>>>>>>>>>>>>>> different branch circuit breaker and the main breaker tripped 
>>>>>>>>>>>>>>> simultaneously. We checked that branch circuit and could not 
>>>>>>>>>>>>>>> find any fault. It seems unlikely that two branch circuit 
>>>>>>>>>>>>>>> breakers would be faulty, so we have now switched out the CH240 
>>>>>>>>>>>>>>> main breaker in hopes that it is the culprit.  
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> I'm not totally confident in this resolution and I have my 
>>>>>>>>>>>>>>> fingers crossed. If that doesn't work, does anyone have any 
>>>>>>>>>>>>>>> suggestions on another diagnostic step? These intermittent 
>>>>>>>>>>>>>>> problems are a major hassle. One thought I had was to switch to 
>>>>>>>>>>>>>>> a supply side interconnection with a fusible disconnect. Maybe 
>>>>>>>>>>>>>>> the intermittent fault would blow one of the two line fuses so 
>>>>>>>>>>>>>>> at least I could narrow it down to which line the fault is on 
>>>>>>>>>>>>>>> if there is in fact a fault.
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> I have experienced two other tripping breaker issues with 
>>>>>>>>>>>>>>> Enphase systems in the past. Neither of them were systems I 
>>>>>>>>>>>>>>> installed. One turned out to be branch circuits that were not 
>>>>>>>>>>>>>>> properly paired up and landed on different breakers. Another 
>>>>>>>>>>>>>>> time we had an inverter with an internal fault which 
>>>>>>>>>>>>>>> eventually"blew up" with a loud popping noise and smoke 
>>>>>>>>>>>>>>> billowing out of it. That happened after resetting a trip 
>>>>>>>>>>>>>>> breaker multiple times. This case seems to be unrelated to 
>>>>>>>>>>>>>>> those issues. I'm perplexed. 
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> Jason Szumlanski
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>> Florida Solar Design Group
>>>>>>>>>>>>>>> 
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>>  
>>>>>>>>>>>>>>> _______________________________________________
>>>>>> 
>>>> 
>>>> <IE LOGO 150x78.jpg>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to