Hi All, I've been asked to review a GT-BBUS that was installed with a DC to AC ratio of 2.14. The system owner is frustrated b/c his 9.2-kW of PV is bottlenecked by an 80A MPPT (~4,300W). The inverter is a XW-5548 so there is a second bottleneck to overcome even if an additional CC were added.
My inclination is to install a GT inverter for half the array and make a separate point of connection. I have considered adding a transfer switch on the PV conductors to allow the owner to toggle between this new GT inverter and the existing CC. I thought that having the option would be of benefit during extended outages with little sun. I'd be curious to know if anyone has had to solve a problem similar to this one and if they were able to find a suitable switch. To-date, I have not located a good transfer switch or breaker assembly with handle-tie etc... Any thoughts are greatly appreciated. -- Matt Sherald PIMBY Energy, LLC NABCEP Certified Solar PV Installer® 304-704-5943 www.getpimby.blogspot.com www.getpimby.com
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org