Matt, 

quite a few issues and the GT inv. idea is where I would go
also. XW5548 can only sell 20A @240vac. I would just set up a manual A/B
switch on the grid inverter solar input to be able to switch this to the
mppt-80-600 for outages and bad solar days. 

I can dig up the one I used.
In this app we just added the second array for winter and let the mppt
current limit when it was cold to avoid stressing it offgrid. 
Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Tue, 22 Oct 2019 12:07:45 -0400, Matt Sherald 
wrote:   Hi All,   I've been asked to review a GT-BBUS that was installed
with a DC to AC ratio of 2.14. The system owner is frustrated b/c his
9.2-kW of PV is bottlenecked by an 80A MPPT (~4,300W). The inverter is a
XW-5548 so there is a second bottleneck to overcome even if an additional
CC were added.   My inclination is to install a GT inverter for half the
array and make a separate point of connection. I have considered adding a
transfer switch on the PV conductors to allow the owner to toggle between
this new GT inverter and the existing CC. I thought that having the option
would be of benefit during extended outages with little sun.   I'd be
curious to know if anyone has had to solve a problem similar to this one
and if they were able to find a suitable switch. To-date, I have not
located a good transfer switch or breaker assembly with handle-tie etc...
Any thoughts are greatly appreciated. 
-- 
     Matt Sherald PIMBY Energy,
LLC NABCEP Certified Solar PV Installer(R) 304-704-5943


www.getpimby.blogspot.com [3]
www.getpimby.com [4]      -- 




Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
[3] http://www.getpimby.blogspot.com
[4]
http://www.getpimby.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to