Hey Matt,

See Morningstar's

TS-MPPT-60-600V-48-DB-TR

https://www.morningstarcorp.com/products/tristar-mppt-600v/

Hope that helps!

Jeff

~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~

Matt Sherald wrote on 10/22/19 9:07 AM:

Hi All,

I've been asked to review a GT-BBUS that was installed with a DC to AC ratio of 2.14. The system owner is frustrated b/c his 9.2-kW of PV  is bottlenecked by an 80A MPPT (~4,300W).  The inverter is a XW-5548 so there is a second bottleneck to overcome even if an additional CC were added.

My inclination is to install a GT inverter for half the array and make a separate point of connection.  I have considered adding a transfer switch on the PV conductors to allow the owner to toggle between this new GT inverter and the existing CC.  I thought that having the option would be of benefit during extended outages with little sun.

I'd be curious to know if anyone has had to solve a problem similar to this one and if they were able to find a suitable switch.  To-date, I have not located a good transfer switch or breaker assembly with handle-tie etc...  Any thoughts are greatly appreciated.

--
Matt Sherald
PIMBY Energy, LLC
NABCEP Certified Solar PV Installer®
304-704-5943

www.getpimby.blogspot.com <http://www.getpimby.blogspot.com>
www.getpimby.com <http://www.getpimby.com>



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to