Wrenches - I've got an Eaton HFD3090 90A breaker protecting a Solectria
50TL that's tripped twice in the past 5 days, after having no issues during
the first 8 months of system production (including throughout the summer).
Monitoring (inverter-direct and RG CTs) shows nothing unusual (all 3 phases
<57A) and nothing to indicate a brief edge-of-cloud effect.  I'm heading
out today to IR the AC connections and expect to see a some color, but
being as the site is somewhat remote wanted to check with the group on any
other recommendations before leaving.  I don't have a logging current meter
but might pick up a spare breaker to swap in if all connections check out.
Any other suggestions?  Anyone ever had nuisance tripping issues with Eaton
Series C breakers?


Regards,


Andrew Truitt

www.dr.ventures
d: 202.486.7507

NABCEP Certified PV Installation Professional ID: 032407-66
Colorado Journeyman Electrician License No.: 600132

[image: Logo]



The content of this email is confidential and intended for the recipient
specified in message only. It is strictly forbidden to share any part of
this message with any third party, without a written consent of the sender.
If you received this message by mistake, please reply to this message and
follow with its deletion, so that we can ensure such a mistake does not
occur in the future.
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to