If you want to bring it up to 2017, you would need RS. It would be very expensive to retrofit this project to shut down within the 2017 boundary limits of one foot or less depending upon technology being used. If you are not changing anything on the roof, you won't be 2017 compliant.  I am pretty sure that you always had to have the dc conductors in metallic conduit within the structure. I also think you had to have an dc disconnect at the nearest accessible entry point within the building.  To make the system reasonably safe and not 2017 compliant, I would add metallic conduit to the inside, and add a dc disconnect, external or internal, add a directory citing where the ac and dc disconnects are.  This is definitely not going to make you 2017 compliant, but as was pointed out, this system is most likely grandfathered. Chris

On 6/12/2019 5:34 PM, Kirk Herander wrote:

I am not required to meet 2017 code. In Florida, they are only up to the 2011 code. I want to bring it up to NEC2017 regardless. So for my questions,  assume the 2017 code is relevant. And it is a flat carport roof, the rack is mounted at a fixed tilt of about 20 degrees. Understood?

*From:*RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On Behalf Of *Ray
*Sent:* Wednesday, June 12, 2019 4:24 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] need for outdoor DC disconnect

Are you required to meet the latest code?  In many retrofit/ replacement situations, you are only required to meet the code requirements of the date the original system was installed. Metal vs PVC is dependent on the code version you are meeting.  Was metal a NEC 2008 requirement? I don't have my old code versions here.   When metal is required, its only from the point of entry into the building to the inverter, so if you mount the inverter outdoors, it doesn't have to change either.  I've got lots of legacy systems that have PVC  on the inside, and never had an issue.  Seems like more trouble to change out than its worth, but if the AHJ requires it, then yes.

Also, you didn't mention if the array was roof or ground mounted, which would effect the 690.12 interpretation.

Ray Walters
Remote Solar
303 505-8760

On 6/12/19 12:49 PM, Kirk Herander wrote:

    All,

    I am retrofitting an existing PV system with Storedge / LG Chem /
    optimizers and updating some code issues. I am replacing the PVC
    conduit carrying the array conductors into the building with
    metallic raceway to the point of DC disconnect(i.e. the inverter).
     The array is presently connected to an Outback inverter / FM60
    controller / AGM batteries (grid tied with backup). If I am
    interpreting NEC 690.12 etc. correctly, a DC disconnect outdoors
    is generally not required because of new rapid shutdown
    capability, amongst other reasons. Would this be the case
    regardless of metal or plastic conduit penetrating the building?
    The system at present has no outdoor DC disco, and to me that’s a
    violation in addition to lack of metallic raceway entering the
    building. Thanks.

    *Kirk Herander*

    *Owner|Principal, VT Solar, LLC *

    */Celebrating our 28^th Anniversary 1991-2019/*

    *www.vermontsolarnow.com
    
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>*

    dba Vermont Solar Engineering

    NABCEP^TM 2003 Inaugural Certificant

    VT RE Incentive Program Partner

    802.863.1202



    _______________________________________________

    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:

    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:

    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:

    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to