Currently up in the air as to whether 2020 will allow that on 1- and 2- family 
houses. If so then yes...currently don’t know of any. 

Brian

> On Sep 18, 2018, at 2:45 PM, Jay <jay.pe...@gmail.com> wrote:
> 
> Does anyone make a 1000vdc single phase inverter?
> Would reduce wire costs dramatically 
> 
> Jay
> Peltz power. 
> 
>> On Sep 18, 2018, at 11:36 AM, Lorenzo Ortiz <lore...@cal-solar.com> wrote:
>> 
>> Thanks for all the input guys.  After looking at the 3 phase with 
>> transformer options with some transformer manufacturers, that has been 
>> pretty much ruled out due to complexity/cost. 
>> With single phase step-up and step-down transformers, even at 600VAC, it 
>> still requires some monster wire.
>> The best solution seems to be placing the inverters next to the POI and just 
>> running long strings from the array back to the inverters and accepting up 
>> to 4%-5% voltage drop. And that's with #8 instead of the usual #10 AND 
>> accounting for worst-case production.
>> 
>> Man, sometimes this solar stuff is just crazy...
>> 
>>> On Tue, Sep 18, 2018 at 10:15 AM, Blake Gleason 
>>> <bl...@sunlightandpower.com> wrote:
>>> Good advice already on this thread.  A couple of points to consider:
>>> 
>>> 1. Re: step-up/step-down option (probably what I'd do): definitely pay 
>>> attention to transformer spec to minimize both magnetization and operating 
>>> losses.  Newer DOE 2016-compliant transformers are MUCH better than before, 
>>> and that's just the minimum standard.  If you really want to minimize 
>>> magnetization losses, you can always design a relay/timer to disconnect the 
>>> transformers at night (from the interconnection side), although I've found 
>>> that this setup is either very expensive or too unreliable (nuisance 
>>> tripping upon re-connect, timer gets "off" cycle somehow, etc).
>>> 
>>> 2. I think someone mentioned a 480V single-phase inverter.  I'm not aware 
>>> of a high-quality product meeting that description.  Is there one?  All of 
>>> the "480V" single-phase inverters I'm aware of are 277V (line to neutral), 
>>> which is hardly worth the transformer effort (versus 240V).
>>> 
>>> 3. Definitely use aluminum wire for the long run.  If wire size is still 
>>> too large, even with step up/down tranformers, consider allowing slightly 
>>> increased voltage drop at full power (say, 5%), and, depending on typical 
>>> grid voltage at the site, change taps on one of the transformers to err on 
>>> the low side (from inverters' point-of-view), to keep the inverters from 
>>> tripping at upper voltage limit at full power (max voltage drop/rise).
>>> 
>>> 
>>> Blake
>>> 
>>>> On Tue, Sep 18, 2018 at 9:57 AM, Jerry Shafer <jerrysgarag...@gmail.com> 
>>>> wrote:
>>>> Lorenzo
>>>> You might want to look at relocating the inverter(s) closer to the meter 
>>>> instead of the array, one reason is even if there is some line loss at 
>>>> full power its less as the voltage goes up and the inverter does not see 
>>>> the line resistance that can cause high voltage issues at the inverter. 
>>>> Some engineers use more side of peak performance than full power, this 
>>>> keeps wite size down and does not effect output
>>>> Jerry
>>>> 
>>>> On Sep 17, 2018 9:42 AM, "Lorenzo Ortiz" <lore...@cal-solar.com> wrote:
>>>> Wrenches,
>>>> 
>>>> We have a PV array situated about 900' from the POI (240V 1PH). We 
>>>> initially spec'd (5) 11.4kW inverters and the combined output would be 
>>>> 238A. The wire size required for this current over that distance is cost 
>>>> prohibitive.
>>>> 
>>>> A solution was to use a single 50kW 3 phase inverter at the array and then 
>>>> convert it to 240V... somehow? Is anyone familiar with how to go about 
>>>> doing this? My thought was to have a step down transformer at the POI and 
>>>> pull off two legs to get 240V. Is this even a thing?
>>>> 
>>>> The other, more expensive option is to use a step up transformer at the 
>>>> array and a step down at the POI to get us a smaller wire size.
>>>> 
>>>> Thanks for any input.
>>>> 
>>>> 
>>>> -- 
>>>> Loren Ortiz   Commercial PV Designer
>>>> 
>>>>     lo...@cal-solar.com  (530) 274-3671
>>>>   
>>>> 
>>>> 
>>>> 
>>>> Showroom located at: 149 E Main St. Grass Valley, CA 95945
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> 
>>>> 
>>> 
>>> 
>>> 
>>> -- 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>>                                             
>>>                                             
>>>                                             
>>>                                             
>>>                                             
>>>                                             
>>>                                      
>>> Blake Gleason - PE, LEED AP
>>> Director of Innovation & Technical Excellence
>>> 
>>> P: 510.845.2997 x128 
>>> E: bl...@sunlightandpower.com 
>>> W: sunlightandpower.com
>>> 
>>> See how universities are using business as a force for good with solar!
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>> 
>> 
>> 
>> -- 
>> Loren Ortiz   Commercial PV Designer
>> 
>>     lo...@cal-solar.com  (530) 274-3671
>>   
>> 
>> 
>> 
>> Showroom located at: 149 E Main St. Grass Valley, CA 95945
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to