Lorenzo
You might want to look at relocating the inverter(s) closer to the meter
instead of the array, one reason is even if there is some line loss at full
power its less as the voltage goes up and the inverter does not see the
line resistance that can cause high voltage issues at the inverter. Some
engineers use more side of peak performance than full power, this keeps
wite size down and does not effect output
Jerry

On Sep 17, 2018 9:42 AM, "Lorenzo Ortiz" <lore...@cal-solar.com> wrote:

Wrenches,

We have a PV array situated about 900' from the POI (240V 1PH). We
initially spec'd (5) 11.4kW inverters and the combined output would be
238A. The wire size required for this current over that distance is cost
prohibitive.

A solution was to use a single 50kW 3 phase inverter at the array and then
convert it to 240V... somehow? Is anyone familiar with how to go about
doing this? My thought was to have a step down transformer at the POI and
pull off two legs to get 240V. Is this even a thing?

The other, more expensive option is to use a step up transformer at the
array and a step down at the POI to get us a smaller wire size.

Thanks for any input.


-- 
*Loren Ortiz   Commercial PV Designer*

    lo...@cal-solar.com <lore...@cal-solar.com>*  (530) 274-3671*



<http://californiasolarco.com/referral-program/>
*Showroom located at: 149 E Main St. Grass Valley, CA 95945*
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to