Does anyone make a 1000vdc single phase inverter?
Would reduce wire costs dramatically 

Jay
Peltz power. 

> On Sep 18, 2018, at 11:36 AM, Lorenzo Ortiz <lore...@cal-solar.com> wrote:
> 
> Thanks for all the input guys.  After looking at the 3 phase with transformer 
> options with some transformer manufacturers, that has been pretty much ruled 
> out due to complexity/cost. 
> With single phase step-up and step-down transformers, even at 600VAC, it 
> still requires some monster wire.
> The best solution seems to be placing the inverters next to the POI and just 
> running long strings from the array back to the inverters and accepting up to 
> 4%-5% voltage drop. And that's with #8 instead of the usual #10 AND 
> accounting for worst-case production.
> 
> Man, sometimes this solar stuff is just crazy...
> 
>> On Tue, Sep 18, 2018 at 10:15 AM, Blake Gleason <bl...@sunlightandpower.com> 
>> wrote:
>> Good advice already on this thread.  A couple of points to consider:
>> 
>> 1. Re: step-up/step-down option (probably what I'd do): definitely pay 
>> attention to transformer spec to minimize both magnetization and operating 
>> losses.  Newer DOE 2016-compliant transformers are MUCH better than before, 
>> and that's just the minimum standard.  If you really want to minimize 
>> magnetization losses, you can always design a relay/timer to disconnect the 
>> transformers at night (from the interconnection side), although I've found 
>> that this setup is either very expensive or too unreliable (nuisance 
>> tripping upon re-connect, timer gets "off" cycle somehow, etc).
>> 
>> 2. I think someone mentioned a 480V single-phase inverter.  I'm not aware of 
>> a high-quality product meeting that description.  Is there one?  All of the 
>> "480V" single-phase inverters I'm aware of are 277V (line to neutral), which 
>> is hardly worth the transformer effort (versus 240V).
>> 
>> 3. Definitely use aluminum wire for the long run.  If wire size is still too 
>> large, even with step up/down tranformers, consider allowing slightly 
>> increased voltage drop at full power (say, 5%), and, depending on typical 
>> grid voltage at the site, change taps on one of the transformers to err on 
>> the low side (from inverters' point-of-view), to keep the inverters from 
>> tripping at upper voltage limit at full power (max voltage drop/rise).
>> 
>> 
>> Blake
>> 
>>> On Tue, Sep 18, 2018 at 9:57 AM, Jerry Shafer <jerrysgarag...@gmail.com> 
>>> wrote:
>>> Lorenzo
>>> You might want to look at relocating the inverter(s) closer to the meter 
>>> instead of the array, one reason is even if there is some line loss at full 
>>> power its less as the voltage goes up and the inverter does not see the 
>>> line resistance that can cause high voltage issues at the inverter. Some 
>>> engineers use more side of peak performance than full power, this keeps 
>>> wite size down and does not effect output
>>> Jerry
>>> 
>>> On Sep 17, 2018 9:42 AM, "Lorenzo Ortiz" <lore...@cal-solar.com> wrote:
>>> Wrenches,
>>> 
>>> We have a PV array situated about 900' from the POI (240V 1PH). We 
>>> initially spec'd (5) 11.4kW inverters and the combined output would be 
>>> 238A. The wire size required for this current over that distance is cost 
>>> prohibitive.
>>> 
>>> A solution was to use a single 50kW 3 phase inverter at the array and then 
>>> convert it to 240V... somehow? Is anyone familiar with how to go about 
>>> doing this? My thought was to have a step down transformer at the POI and 
>>> pull off two legs to get 240V. Is this even a thing?
>>> 
>>> The other, more expensive option is to use a step up transformer at the 
>>> array and a step down at the POI to get us a smaller wire size.
>>> 
>>> Thanks for any input.
>>> 
>>> 
>>> -- 
>>> Loren Ortiz   Commercial PV Designer
>>> 
>>>     lo...@cal-solar.com  (530) 274-3671
>>>   
>>> 
>>> 
>>> 
>>> Showroom located at: 149 E Main St. Grass Valley, CA 95945
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>> 
>> 
>> 
>> -- 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>>                                              
>>                                              
>>                                      
>>                                              
>>                                              
>>                                              
>>                                      
>> Blake Gleason - PE, LEED AP
>> Director of Innovation & Technical Excellence
>> 
>> P: 510.845.2997 x128 
>> E: bl...@sunlightandpower.com 
>> W: sunlightandpower.com
>> 
>> See how universities are using business as a force for good with solar!
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> 
> 
> -- 
> Loren Ortiz   Commercial PV Designer
> 
>     lo...@cal-solar.com  (530) 274-3671
>   
> 
> 
> 
> Showroom located at: 149 E Main St. Grass Valley, CA 95945
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to