Also using Drakes solution, you bypass the issue with the inverter “voltage 
drop” causing it to go out of spec in high production times (a 5% voltage drop 
would really mean that the inverter would see the grid as being 5% higher than 
it really is when producing at full power, potentially causing a high grid 
voltage fault). You can then allow for more than 1% voltage drop over that 
distance without risking the system shutting down. You change an operational 
requirement constraint into a pure power production vs cost of wire issue. It 
might be that going with smaller wire is less expensive that the extra energy 
you would generate from that 1% better voltage drop.

 

Also you said 11.4kW inverter with 240V 1ph, which makes me think SolarEdge. If 
that’s true then your situation just got a even better. I believe they will 
communicate to optimizers up to 1000’ (I don’t like operating at the edge of a 
systems spec, but might be the best option here). But they operate at the same, 
higher voltage under power producing conditions. That only helps your power 
loss issues. You can run the numbers, but you usually lose about 1/2ish total 
annual energy compared to the calculated %voltage drop on the DC lines. So if 
you have the wire run designed for 5% drop at peak power, you’d really only 
lose roughly 2-3% total energy per year.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
drake.chamber...@redwoodalliance.org
Sent: Monday, September 17, 2018 1:50 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Step-up/Step-down Transformer question

 

Another option would be to locate the inverters near the grid and run the DC at 
as high a voltage as possible. Have a separate run of wire for each of the 5 
inverters. If you ran the DC at 500 V, an 11.4 kW inverter would only draw 
22.8. A. Use 2/0 AL for a little over 1% VD at full power. 




----- Original Message -----

From:

"RE-wrenches" <re-wrenches@lists.re-wrenches.org 
<mailto:re-wrenches@lists.re-wrenches.org> >

 

To:

"RE-wrenches" <RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> >

Cc:

 

Sent:

Mon, 17 Sep 2018 09:42:01 -0700

Subject:

[RE-wrenches] Step-up/Step-down Transformer question



Wrenches,

 

We have a PV array situated about 900' from the POI (240V 1PH). We initially 
spec'd (5) 11.4kW inverters and the combined output would be 238A. The wire 
size required for this current over that distance is cost prohibitive.

 

A solution was to use a single 50kW 3 phase inverter at the array and then 
convert it to 240V... somehow? Is anyone familiar with how to go about doing 
this? My thought was to have a step down transformer at the POI and pull off 
two legs to get 240V. Is this even a thing?

 

The other, more expensive option is to use a step up transformer at the array 
and a step down at the POI to get us a smaller wire size.

 

Thanks for any input.




 

-- 

Loren Ortiz   Commercial PV Designer

 

    lo...@cal-solar.com <mailto:lore...@cal-solar.com>   (530) 274-3671

  

 

 

Showroom located at: 149 E Main St. Grass Valley, CA 95945

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to